CHAPTER 5: SETTINGS
CONTROL ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-289
5
The flashover detection resets if the current drops back to zero, the breaker closes, or the selected FlexLogic operand for
supervision changes to high. Using supervision through the
BRK 1 FLSHOVR SPV A
,
BRK 1 FLSHOVR SPV B
, and
BRK 1 FLSHOVR
SPV c
settings is recommended by selecting a trip operand that does not allow the flashover element to pickup prior to the
trip.
The flashover detection can be used for external alarm, re-tripping the breaker, or energizing the lockout relay.
Consider the following configuration:
The source 1 (SRC1) phase currents are feeder CTs and phase voltages are bus VTs, and Contact Input 1 is set as Breaker
52a contact. The conditions prior to flashover detection are:
•
52a status = 0
•
VAg, VBg, or VCg is greater than the pickup setting
•
IA, IB, IC = 0; no current flows through the breaker
•
Δ
VA is greater than pickup (not applicable in this scheme)
The conditions at flashover detection are:
•
52a status = 0
•
IA, IB, or IC is greater than the pickup current flowing through the breaker
•
Δ
VA is greater than pickup (not applicable in this scheme)
Six VT breaker flashover application
The per-phase voltage difference approaches zero when the breaker is closed. This is well below any typical minimum
pickup voltage. Select the level of the
BRK 1 FLSHOVR DIFF V PKP
setting to be less than the voltage difference measured
across the breaker when the close or open breaker resistors are left in service. Prior to flashover, the voltage difference is
larger than
BRK 1 FLSHOVR DIFF V PKP
. This applies to either the difference between two live voltages per phase or when the
voltage from one side of the breaker has dropped to zero (line de-energized), at least one per-phase voltage is larger than
the
BRK 1 FLSHOVR V PKP
setting, and no current flows through the breaker poles. During breaker flashover, the per-phase
voltages from both sides of the breaker drops below the pickup value defined by the
BRK 1 FLSHOVR V PKP
setting, the
voltage difference drops below the pickup setting, and flashover current is detected. These flashover conditions initiate
FlexLogic pickup operands and start the
BRK 1 FLSHOVR PKP DELAY
timer.
This application does not require detection of breaker status via a 52a contact, as it uses a voltage difference larger than
the
BRK 1 FLSHOVR DIFF V PKP
setting. However, monitoring the breaker contact ensures scheme stability.
Voltages must be present prior to flashover conditions. If the three VTs are placed after the breaker on the line (or
feeder), and the downstream breaker is open, the measured voltage is zero and the flashover element is not
initiated.
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...