5-282
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CONTROL ELEMENTS
CHAPTER 5: SETTINGS
5
There is one breaker arcing current element available per CT bank, with a minimum of two elements. This element
calculates an estimate of the per-phase wear on the breaker contacts by measuring and integrating the current squared
passing through the breaker contacts as an arc. These per-phase values are added to accumulated totals for each phase
and compared to a programmed threshold value. When the threshold is exceeded in any phase, the relay can set an
output operand to “1.” The accumulated value for each phase can be displayed as an actual value.
The operation of the scheme is shown in the following logic diagram. The same output operand that is selected to operate
the output relay used to trip the breaker, indicating a tripping sequence has begun, is used to initiate this feature. A time
delay is introduced between initiation and the starting of integration to prevent integration of current flow through the
breaker before the contacts have parted. This interval includes the operating time of the output relay, any other auxiliary
relays, and the breaker mechanism. For maximum measurement accuracy, measure the interval between change-of-state
of the operand (from 0 to 1) and contact separation for the specific installation. Integration of the measured current
continues for 100 ms, which is expected to include the total arcing period.
The feature is programmed to perform fault duration calculations. Fault duration is defined as a time between operation of
the disturbance detector occurring before initiation of this feature, and reset of an internal low-set overcurrent function.
Correction is implemented to account for a non-zero reset time of the overcurrent function.
Breaker arcing currents and fault duration values are available under the
ACTUAL VALUES
RECORDS
MAINTENANCE
BREAKER 1(6)
menus.
BKR 1 ARC AMP INT-A(C)
— Select the same output operands that are configured to operate the output relays used to trip the
breaker. In three-pole tripping applications, configure the same operand to initiate arcing current calculations for poles A,
B, and C of the breaker. In single-pole tripping applications, configure per-pole tripping operands to initiate the calculations
for the poles that are actually tripped.
BKR 1 ARC AMP DELAY
— This setting is used to program the delay interval between the time the tripping sequence is
initiated and the time the breaker contacts are expected to part, starting the integration of the measured current.
BKR 1 ARC AMP LIMIT
— Selects the threshold value above which the output operand is set.
BKR 1 CLR ARC AMPS
— Selects a FLexLogic Operand to clear the accumulated I
2
t values (kA
2
-cycle), reset fault duration
items (breaker operating time), clear ARCING AMPS (kA
2
-cycle) and AMP MAX (kA) values of the last event.
BKR 1 INTERUPTION RATING
— This setting specifies the maximum symmetrical interruption rating of the circuit breaker.
BKR 1 INTERRUPTION
RATING: 31.5 kA
Range: 0.0 to 100.0 kA in steps of 0.1
BKR 1 CLR ARC AMPS:
Off
Range: FlexLogic operand
BKR 1 ARC AMP BLOCK:
Off
Range: FlexLogic operand
BKR 1 ARC AMP
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
BKR 1 ARC AMP
EVENTS: Disabled
Range: Disabled, Enabled
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...