5-182
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
SYSTEM SETUP
CHAPTER 5: SETTINGS
5
Because energy parameters are accumulated, these values should be recorded and then reset immediately prior to
changing VT characteristics.
Three banks of phase/auxiliary VTs can be set, where voltage banks are denoted in the following format (X represents the
module slot position letter):
Xa, where X = {F, M, U} and a = {5}
See the Introduction to AC Sources section at the beginning of this chapter for details.
With VTs installed, the relay can perform voltage measurements as well as power calculations. Enter the
PHASE VT F5
CONNECTION
made to the system as “Wye” or “Delta.” An open-delta source VT connection is entered as “Delta.”
5.5.2 Power system
SETTINGS
SYSTEM SETUP
POWER SYSTEM
The power system
NOMINAL FREQUENCY
value is used as a default to set the digital sampling rate if the system frequency
cannot be measured from available signals. This can happen if the signals are not present or are heavily distorted. Before
reverting to the nominal frequency, the frequency tracking algorithm holds the last valid frequency measurement for a
safe period of time while waiting for the signals to reappear or for the distortions to decay.
PHASE VT F5
SECONDARY: 66.4 V
Range: 25.0 to 240.0 V in steps of 0.1
PHASE VT F5
RATIO: 1.00 :1
Range: 1.00 to 24000.00 in steps of 0.01
AUXILIARY VT F5
CONNECTION: Vag
Range: Vn, Vag, Vbg, Vcg, Vab, Vbc, Vca
AUXILIARY VT F5
SECONDARY: 66.4 V
Range: 25.0 to 240.0 V in steps of 0.1
AUXILIARY VT F5
RATIO: 1.00 :1
Range: 1.00 to 24000.00 in steps of 0.01
The nominal
PHASE VT F5 SECONDARY
voltage setting is the voltage across the relay input terminals when nominal
voltage is applied to the VT primary.
For example, on a system with a 13.8 kV nominal primary voltage and with a 14400:120 volt VT in a delta
connection, the secondary voltage is 115; that is, (13800 / 14400) × 120. For a wye connection, the voltage value
entered must be the phase to neutral voltage, which is 115
/
= 66.4.
On a 14.4 kV system with a delta connection and a VT primary to secondary turns ratio of 14400:120, the voltage
value entered is 120; that is, 14400 / 120.
If the
PHASE VT F5 CONNECTION
is set to “Delta”, the relay does not calculate voltage harmonics.
POWER SYSTEM
NOMINAL FREQUENCY:
60 Hz
Range: 25 to 60 Hz in steps of 1
PHASE ROTATION:
ABC
Range: ABC, ACB
FREQUENCY AND PHASE
REFERENCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
FREQUENCYTRACKING:
Enabled
Range: Disabled, Enabled
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...