CHAPTER 5: SETTINGS
GROUPED ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-231
5
IAC curves
The curves for the General Electric type IAC relay family are derived from the formulae:
Eq. 5-10
where
T = operate time (in seconds)
TDM = Multiplier setting
I = Input current
I
pkp
= Pickup Current setting
A to E = constants defined in the table
t
r
= characteristic constant defined in the table
T
RESET
= reset time in seconds (assuming energy capacity is 100% and RESET is “Timed”)
Table 5-31: GE type IAC inverse time curve constants
Table 5-32: GE type IAC curve trip times
0.10
6.400
2.667
1.000
0.533
0.333
0.229
0.167
0.127
0.100
0.081
0.20
12.800
5.333
2.000
1.067
0.667
0.457
0.333
0.254
0.200
0.162
0.40
25.600
10.667
4.000
2.133
1.333
0.914
0.667
0.508
0.400
0.323
0.60
38.400
16.000
6.000
3.200
2.000
1.371
1.000
0.762
0.600
0.485
0.80
51.200
21.333
8.000
4.267
2.667
1.829
1.333
1.016
0.800
0.646
1.00
64.000
26.667
10.000
5.333
3.333
2.286
1.667
1.270
1.000
0.808
IEC Short Inverse
0.05
0.153
0.089
0.056
0.044
0.038
0.034
0.031
0.029
0.027
0.026
0.10
0.306
0.178
0.111
0.088
0.075
0.067
0.062
0.058
0.054
0.052
0.20
0.612
0.356
0.223
0.175
0.150
0.135
0.124
0.115
0.109
0.104
0.40
1.223
0.711
0.445
0.351
0.301
0.269
0.247
0.231
0.218
0.207
0.60
1.835
1.067
0.668
0.526
0.451
0.404
0.371
0.346
0.327
0.311
0.80
2.446
1.423
0.890
0.702
0.602
0.538
0.494
0.461
0.435
0.415
1.00
3.058
1.778
1.113
0.877
0.752
0.673
0.618
0.576
0.544
0.518
IAC curve shape
A
B
C
D
E
t
r
IAC Extreme Inverse
0.0040
0.6379
0.6200
1.7872
0.2461
6.008
IAC Very Inverse
0.0900
0.7955
0.1000
–1.2885
7.9586
4.678
IAC Inverse
0.2078
0.8630
0.8000
–0.4180
0.1947
0.990
IAC Short Inverse
0.0428
0.0609
0.6200
–0.0010
0.0221
0.222
Multiplier
(TDM)
Current ( I / I
pickup
)
1.5
2.0
3.0
4.0
5.0
6.0
7.0
8.0
9.0
10.0
IAC Extremely Inverse
0.5
1.699
0.749
0.303
0.178
0.123
0.093
0.074
0.062
0.053
0.046
1.0
3.398
1.498
0.606
0.356
0.246
0.186
0.149
0.124
0.106
0.093
2.0
6.796
2.997
1.212
0.711
0.491
0.372
0.298
0.248
0.212
0.185
4.0
13.591
5.993
2.423
1.422
0.983
0.744
0.595
0.495
0.424
0.370
6.0
20.387
8.990
3.635
2.133
1.474
1.115
0.893
0.743
0.636
0.556
Multiplier
(TDM)
Current ( I / I
pickup
)
1.5
2.0
3.0
4.0
5.0
6.0
7.0
8.0
9.0
10.0
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...