5-188
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
SYSTEM SETUP
CHAPTER 5: SETTINGS
5
BREAKER1
Φ
A/3P OPND
— Selects an operand, usually a contact input, that is for a normally-closed 52/b status input that
creates a logic 1 when the breaker is open. If a separate 52/b contact input is not available, then the inverted 52/a status
signal or the inverted
BREAKER 1 CLOSED
status signal can be used.
BREAKER 1
Φ
B CLOSED
— If the mode is selected as three-pole, this setting has no function. If the mode is selected as single-
pole, this input is used to track the breaker phase B closed position as outlined for phase A.
BREAKER 1
Φ
B OPENED
— If the mode is selected as three-pole, this setting has no function. If the mode is selected as single-
pole, this input is used to track the breaker phase B opened position as outlined for phase A.
BREAKER 1
Φ
C CLOSED
— If the mode is selected as three-pole, this setting has no function. If the mode is selected as single-
pole, this input is used to track the breaker phase C closed position as outlined for phase A.
BREAKER 1
Φ
C OPENED
— If the mode is selected as three-pole, this setting has no function. If the mode is selected as single-
pole, this input is used to track the breaker phase C opened position as outlined for phase A.
BREAKER 1 TOPERATE
— This setting specifies the required interval to overcome transient disagreement between the 52/a
and 52/b auxiliary contacts during breaker operation. If transient disagreement still exists after this time has expired, the
BREAKER 1 BAD STATUS
FlexLogic operand is asserted for alarm or blocking purposes.
BREAKER 1 EXT ALARM
— This setting selects an operand, usually an external contact input connected to a breaker alarm
reporting contact. While the selected operand is active, the
BREAKER 1 TROUBLE
operand is activated.
BREAKER 1 ALARM DELAY
— This setting specifies the delay interval during which a disagreement of status among the three-
pole position tracking operands does not declare a pole disagreement. This allows for non-simultaneous operation of the
poles.
BREAKER 1 OPEN SEAL-IN
— This setting specifies the seal-in time of the three-pole open command initiated by either the
Trip Out element or a manual open command to the circuit breaker.
MANUAL CLOSE RECAL1 TIME
— This setting specifies the seal-in time of the close commands due to an operator-initiated
manual close command to the circuit breaker.
BREAKER 1 OUT OF SV
— Selects an operand indicating that breaker 1 is out-of-service.
BREAKER 1 RACKED-IN
— This setting selects a contact input to show whether the breaker is racked-in or racked-out. The
racked-in or racked-out status is used to indicate dynamically the status of breaker symbol, only applied in the single-line
diagram in the graphical front panel. If this setting is set to Off, the racked status is not considered.
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...