CHAPTER 5: SETTINGS
PRODUCT SETUP
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-11
5
The following access supervision settings are available.
INVALID ATTEMPTS BEFORE LOCKOUT
— This setting specifies the number of times that an incorrect password can be entered
within a three-minute time span before lockout occurs. When lockout occurs, the
LOCAL ACCESS DENIED
or
REMOTE ACCESS
DENIED
FlexLogic operands are set to “On.” These operands are returned to the “Off” state upon expiration of the lockout.
PASSWORD LOCKOUT DURATION
— This setting specifies the time that the F35 locks out password access after the number
of invalid password entries specified by the
INVALID ATTEMPTS BEFORE LOCKOUT
setting has occurred.
The F35 provides a means to raise an alarm upon failed password entry. If password verification fails while accessing a
password-protected level of the relay (either settings or commands), the
UNAUTHORIZED ACCESS
FlexLogic operand is
asserted. The operand can be programmed to raise an alarm via contact outputs or communications. This feature can be
used to protect against both unauthorized and accidental access attempts.
The
UNAUTHORIZED ACCESS
operand is reset with the
COMMANDS
CLEAR RECORDS
RESET UNAUTHORIZED ALARMS
command. Therefore, to apply this feature with security, password-protect the Command level. The operand does not
generate events or targets.
If events or targets are required, the
UNAUTHORIZED ACCESS
operand can be assigned to a digital element programmed with
event logs or targets enabled.
The following table outlines access level timeout settings.
SETTINGS
PRODUCT SETUP
SECURITY
ACCESS SUPERVISION
ACCESS LEVEL TIMEOUTS
These settings allow the user to specify the length of inactivity required before returning to the Restricted access level.
Note that the access level is set to Restricted when control power is cycled.
COMMAND LEVEL ACCESS TIMEOUT
— This setting specifies the length of inactivity (no local or remote access) required to
return to Restricted access from the Command password level.
SETTING LEVEL ACCESS TIMEOUT
— This setting specifies the length of inactivity (no local or remote access) required to return
to Restricted access from the Command password level.
Dual-permission security access
SETTINGS
PRODUCT SETUP
SECURITY
DUAL PERMISSION SECURITY ACCESS
This feature provides a mechanism to prevent unauthorized or unintended upload of settings to a relay through the local
or remote interface.
The following settings are available through the local (front panel) interface only.
•
LOCAL SETTING AUTH
— This setting is used for local (front panel or RS232 interface) setting access supervision. Valid
values for the FlexLogic operands are either “On” (default) or any physical “Contact Input ~~ On” value.
INVALID ATTEMPTS
BEFORE LOCKOUT: 3
Range: 2 to 5 in steps of 1
PASSWORD LOCKOUT
DURATION: 5 min
Range: 5 to 60 minutes in steps of 1
ACCESS LEVEL
TIMEOUTS
COMMAND LEVEL ACCESS
TIMEOUT: 5 min
Range: 5 to 480 minutes in steps of 1
SETTING LEVEL ACCESS
TIMEOUT: 30 min
Range: 5 to 480 minutes in steps of 1
DUAL PERMISSION
SECURITY ACCESS
LOCAL SETTING AUTH:
On
Range: selected FlexLogic operands (see below)
REMOTE SETTING AUTH:
On
Range: FlexLogic operand
ACCESS AUTH
TIMEOUT: 30 min
Range: 5 to 480 minutes in steps of 1
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...