C.3.1 BUFFERED/UNBUFFERED REPORTING
IEC 61850 buffered and unbuffered reporting is provided in the GGIO1 logical nodes (for binary status values) and MMXU1
to MMXU6 (for analog measured values). Report settings can be configured using the EnerVista UR Setup software, sub-
station configurator software, or via an IEC 61850 client. The following items can be configured:
•
TrgOps
: Trigger options. The following bits are supported by the F35:
–
Bit 1: data-change
–
Bit 4: integrity
–
Bit 5: general interrogation
•
OptFlds
: Option Fields. The following bits are supported by the F35:
–
Bit 1: sequence-number
–
Bit 2: report-time-stamp
–
Bit 3: reason-for-inclusion
–
Bit 4: data-set-name
–
Bit 5: data-reference
–
Bit 6: buffer-overflow (for buffered reports only)
–
Bit 7: entryID (for buffered reports only)
–
Bit 8: conf-revision
–
Bit 9: segmentation
•
IntgPd
: Integrity period.
•
BufTm
: Buffer time.
C.3.2 FILE TRANSFER
MMS file services are supported to allow transfer of oscillography, event record, or other files from a F35 relay.
C.3.3 TIMESTAMPS AND SCANNING
The timestamp values associated with all IEC 61850 data items represent the
time of the last change
of either the value or
quality flags of the data item. To accomplish this functionality, all IEC 61850 data items must be regularly scanned for data
changes, and the timestamp updated when a change is detected, regardless of the connection status of any IEC 61850 cli-
ents. For applications where there is no IEC 61850 client in use, the IEC 61850
SERVER SCANNING
setting can be pro-
grammed as “Disabled”. If a client is in use, this setting should be programmed as “Enabled” to ensure the proper
generation of IEC 61850 timestamps.
C.3.4 LOGICAL DEVICE NAME
The logical device name is used to identify the IEC 61850 logical device that exists within the F35. This name is composed
of two parts: the IED name setting and the logical device instance. The complete logical device name is the combination of
the two character strings programmed in the
IEDNAME
and
LD INST
settings. The default values for these strings are “IED-
Name” and “LDInst”. These values should be changed to reflect a logical naming convention for all IEC 61850 logical
devices in the system.
C.3.5 LOCATION
The LPHD1 logical node contains a data attribute called
location
(LPHD1.DC.PhyNam.location). This is a character string
meant to describe the physical location of the F35. This attribute is programmed through the
LOCATION
setting and its
default value is “Location”. This value should be changed to describe the actual physical location of the F35.
Содержание F35
Страница 2: ......
Страница 4: ......
Страница 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Страница 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Страница 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Страница 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Страница 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...
Страница 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...