GE Multilin
F35 Multiple Feeder Protection System
5-17
5 SETTINGS
5.2 PRODUCT SETUP
5
The F35 supports the Distributed Network Protocol (DNP) version 3.0. The F35 can be used as a DNP slave device con-
nected to multiple DNP masters (usually an RTU or a SCADA master station). Since the F35 maintains two sets of DNP
data change buffers and connection information, two DNP masters can actively communicate with the F35 at one time.
The IEC 60870-5-104 and DNP protocols cannot be simultaneously. When the
IEC 60870-5-104 FUNCTION
set-
ting is set to “Enabled”, the DNP protocol will not be operational. When this setting is changed it will not
become active until power to the relay has been cycled (off-to-on).
The DNP Channels sub-menu is shown below.
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
DNP PROTOCOL
Ö
DNP CHANNELS
The
DNP CHANNEL 1 PORT
and
DNP CHANNEL 2 PORT
settings select the communications port assigned to the DNP protocol
for each channel. Once DNP is assigned to a serial port, the Modbus protocol is disabled on that port. Note that COM1 can
be used only in non-Ethernet UR relays. When this setting is set to “Network - TCP”, the DNP protocol can be used over
TCP/IP on channels 1 or 2. When this value is set to “Network - UDP”, the DNP protocol can be used over UDP/IP on chan-
nel 1 only. Refer to
Appendix E
for additional information on the DNP protocol.
Changes to the
DNP CHANNEL 1 PORT
and
DNP CHANNEL 2 PORT
settings will take effect only after power has
been cycled to the relay.
The
DNP NETWORK CLIENT ADDRESS
settings can force the F35 to respond to a maximum of five specific DNP masters. The
settings in this sub-menu are shown below.
MESSAGE
DNP MESSAGE FRAGMENT
SIZE: 240
Range: 30 to 2048 in steps of 1
MESSAGE
DNP OBJECT 1
DEFAULT VARIATION: 2
Range: 1, 2
MESSAGE
DNP OBJECT 2
DEFAULT VARIATION: 2
Range: 1, 2
MESSAGE
DNP OBJECT 20
DEFAULT VARIATION: 1
Range: 1, 2, 5, 6
MESSAGE
DNP OBJECT 21
DEFAULT VARIATION: 1
Range: 1, 2, 9, 10
MESSAGE
DNP OBJECT 22
DEFAULT VARIATION: 1
Range: 1, 2, 5, 6
MESSAGE
DNP OBJECT 23
DEFAULT VARIATION: 2
Range: 1, 2, 5, 6
MESSAGE
DNP OBJECT 30
DEFAULT VARIATION: 1
Range: 1, 2, 3, 4, 5
MESSAGE
DNP OBJECT 32
DEFAULT VARIATION: 1
Range: 1, 2, 3, 4, 5, 7
MESSAGE
DNP NUMBER OF PAIRED
CONTROL POINTS: 0
Range: 0 to 32 in steps of 1
MESSAGE
DNP TCP CONNECTION
TIMEOUT: 120 s
Range: 10 to 300 s in steps of 1
DNP CHANNELS
DNP CHANNEL 1 PORT:
NETWORK
Range: NONE, COM1 - RS485, COM2 - RS485,
FRONT PANEL - RS232, NETWORK - TCP,
NETWORK - UDP
MESSAGE
DNP CHANNEL 2 PORT:
COM2 - RS485
Range: NONE, COM1 - RS485, COM2 - RS485,
FRONT PANEL - RS232, NETWORK - TCP,
NETWORK - UDP
NOTE
NOTE
Содержание F35
Страница 2: ......
Страница 4: ......
Страница 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Страница 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Страница 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Страница 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Страница 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...
Страница 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...