5-70
F35 Multiple Feeder Protection System
GE Multilin
5.3 SYSTEM SETUP
5 SETTINGS
5
A description of the operation of the breaker control and status monitoring features is provided in chapter 4. Only informa-
tion concerning programming of the associated settings is covered here. These features are provided for two or more
breakers; a user may use only those portions of the design relevant to a single breaker, which must be breaker 1.
The number of breaker control elements is dependent on the number of CT/VT modules specified with the F35. The follow-
ing settings are available for each breaker control element.
•
BREAKER 1 FUNCTION:
This setting enables and disables the operation of the breaker control feature.
•
BREAKER1 PUSH BUTTON CONTROL:
Set to “Enable” to allow faceplate push button operations.
•
BREAKER 1 NAME:
Assign a user-defined name (up to six characters) to the breaker. This name will be used in flash
messages related to breaker 1.
•
BREAKER 1 MODE:
This setting selects “3-pole” mode, where all breaker poles are operated simultaneously, or “1-
pole” mode where all breaker poles are operated either independently or simultaneously.
•
BREAKER 1 OPEN:
This setting selects an operand that creates a programmable signal to operate an output relay to
open breaker 1.
•
BREAKER 1 BLK OPEN
: This setting selects an operand that prevents opening of the breaker. This setting can be
used for select-before-operate functionality or to block operation from a panel switch or from SCADA.
•
BREAKER 1 CLOSE:
This setting selects an operand that creates a programmable signal to operate an output relay
to close breaker 1.
•
BREAKER 1 BLK CLOSE
: This setting selects an operand that prevents closing of the breaker. This setting can be
used for select-before-operate functionality or to block operation from a panel switch or from SCADA.
•
BREAKER 1
Φ
A/3P CLOSED:
This setting selects an operand, usually a contact input connected to a breaker auxil-
iary position tracking mechanism. This input should be a normally-open 52/a status input to create a logic 1 when the
breaker is closed. If the
BREAKER 1 MODE
setting is selected as “3-Pole”, this setting selects a single input as the oper-
and used to track the breaker open or closed position. If the mode is selected as “1-Pole”, the input mentioned above
is used to track phase A and the
BREAKER 1
Φ
B
and
BREAKER 1
Φ
C
settings select operands to track phases B and C,
respectively.
•
BREAKER 1
Φ
A/3P OPND:
This setting selects an operand, usually a contact input, that should be a normally-closed
52/b status input to create a logic 1 when the breaker is open. If a separate 52/b contact input is not available, then the
inverted
BREAKER 1 CLOSED
status signal can be used.
•
BREAKER 1
Φ
B CLOSED:
If the mode is selected as three-pole, this setting has no function. If the mode is selected
as single-pole, this input is used to track the breaker phase B closed position as above for phase A.
•
BREAKER 1
Φ
B OPENED:
If the mode is selected as three-pole, this setting has no function. If the mode is selected
as single-pole, this input is used to track the breaker phase B opened position as above for phase A.
•
BREAKER 1
Φ
C CLOSED:
If the mode is selected as three-pole, this setting has no function. If the mode is selected
as single-pole, this input is used to track the breaker phase C closed position as above for phase A.
•
BREAKER 1
Φ
C OPENED:
If the mode is selected as three-pole, this setting has no function. If the mode is selected
as single-pole, this input is used to track the breaker phase C opened position as above for phase A.
•
BREAKER 1 Toperate
: This setting specifies the required interval to overcome transient disagreement between the
52/a and 52/b auxiliary contacts during breaker operation. If transient disagreement still exists after this time has
expired, the
BREAKER 1 BAD STATUS
FlexLogic™ operand is asserted from alarm or blocking purposes.
•
BREAKER 1 EXT ALARM:
This setting selects an operand, usually an external contact input, connected to a breaker
alarm reporting contact.
•
BREAKER 1 ALARM DELAY:
This setting specifies the delay interval during which a disagreement of status among
the three-pole position tracking operands will not declare a pole disagreement. This allows for non-simultaneous oper-
ation of the poles.
•
MANUAL CLOSE RECAL1 TIME:
This setting specifies the interval required to maintain setting changes in effect after
an operator has initiated a manual close command to operate a circuit breaker.
•
BREAKER 1 OUT OF SV:
Selects an operand indicating that breaker 1 is out-of-service.
Содержание F35
Страница 2: ......
Страница 4: ......
Страница 30: ...1 20 F35 Multiple Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 122: ...4 30 F35 Multiple Feeder Protection System GE Multilin 4 3 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Страница 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Страница 332: ...8 4 F35 Multiple Feeder Protection System GE Multilin 8 1 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Страница 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Страница 460: ...D 10 F35 Multiple Feeder Protection System GE Multilin D 1 IEC 60870 5 104 PROTOCOL APPENDIXD D ...
Страница 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...