5.8.2 RTD INPUTS
PATH: SETTINGS
ÖØ
TRANSDUCER I/O
ÖØ
RTD INPUTS
Ö
RTD INPUT H1(W8)
Hardware and software is provided to receive signals from external resistance temperature detectors and convert these
signals into a digital format for use as required. These channels are intended to be connected to any of the RTD types in
common use. Specific hardware details are contained in chapter 3.
RTD input channels are arranged in a manner similar to CT and VT channels. The user configures individual channels with
the settings shown here.
The channels are arranged in sub-modules of two channels, numbered from 1 through 8 from top to bottom. On power-up,
the relay will automatically generate configuration settings for every channel, based on the order code, in the same general
manner that is used for CTs and VTs. Each channel is assigned a slot letter followed by the row number, 1 through 8 inclu-
sive, which is used as the channel number. The relay generates an actual value for each available input channel.
Settings are automatically generated for every channel available in the specific relay as shown above for the first channel of
a type 5C transducer module installed in the first available slot.
The function of the channel may be either “Enabled” or “Disabled”. If “Disabled”, there will not be an actual value created for
the channel. An alphanumeric ID is assigned to the channel; this ID will be included in the channel actual values. It is also
used to reference the channel as the input parameter to features designed to measure this type of parameter. Selecting the
type of RTD connected to the channel configures the channel.
Actions based on RTD overtemperature, such as trips or alarms, are done in conjunction with the FlexElements™ feature.
In FlexElements™, the operate level is scaled to a base of 100°C. For example, a trip level of 150°C is achieved by setting
the operate level at 1.5 pu. FlexElement™ operands are available to FlexLogic™ for further interlocking or to operate an
output contact directly.
Refer to the following table for reference temperature values for each RTD type.
RTD INPUT H1
RTD INPUT H1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
RTD INPUT H1 ID:
RTD Ip 1
Range: Up to 20 alphanumeric characters
MESSAGE
RTD INPUT H1 TYPE:
100
Ω
Nickel
Range: 100
Ω
Nickel, 10
Ω
Copper, 100
Ω
Platinum,
120
Ω
Nickel
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...