GE Multilin
F35 Multiple Feeder Protection System
5-143
5 SETTINGS
5.6 CONTROL ELEMENTS
5
b) BREAKER ARCING CURRENT
PATH: SETTINGS
ÖØ
CONTROL ELEMENTS
ÖØ
MONITORING ELEMENTS
Ö
BREAKER 1(6) ARCING CURRENT
There is one breaker arcing current element available per CT bank, with a minimum of two elements. This element calcu-
lates an estimate of the per-phase wear on the breaker contacts by measuring and integrating the current squared passing
through the breaker contacts as an arc. These per-phase values are added to accumulated totals for each phase and com-
pared to a programmed threshold value. When the threshold is exceeded in any phase, the relay can set an output operand
to “1”. The accumulated value for each phase can be displayed as an actual value.
The operation of the scheme is shown in the following logic diagram. The same output operand that is selected to operate
the output relay used to trip the breaker, indicating a tripping sequence has begun, is used to initiate this feature. A time
delay is introduced between initiation and the starting of integration to prevent integration of current flow through the
breaker before the contacts have parted. This interval includes the operating time of the output relay, any other auxiliary
relays and the breaker mechanism. For maximum measurement accuracy, the interval between change-of-state of the
operand (from 0 to 1) and contact separation should be measured for the specific installation. Integration of the measured
current continues for 100 ms, which is expected to include the total arcing period.
The feature is programmed to perform fault duration calculations. Fault duration is defined as a time between operation of
the disturbance detector occurring before initiation of this feature, and reset of an internal low-set overcurrent function. Cor-
rection is implemented to account for a non-zero reset time of the overcurrent function.
Breaker arcing currents and fault duration values are available under the
ACTUAL VALUES
ÖØ
RECORDS
ÖØ
MAINTENANCE
Ö
BREAKER 1(6)
menus.
•
BKR 1 ARC AMP INT-A(C):
Select the same output operands that are configured to operate the output relays used to
trip the breaker. In three-pole tripping applications, the same operand should be configured to initiate arcing current
calculations for poles A, B and C of the breaker. In single-pole tripping applications, per-pole tripping operands should
be configured to initiate the calculations for the poles that are actually tripped.
•
BKR 1 ARC AMP DELAY:
This setting is used to program the delay interval between the time the tripping sequence is
initiated and the time the breaker contacts are expected to part, starting the integration of the measured current.
•
BKR 1 ARC AMP LIMIT:
Selects the threshold value above which the output operand is set.
BREAKER 1
ARCING CURRENT
BKR 1 ARC AMP
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
BKR 1 ARC AMP
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
MESSAGE
BKR 1 ARC AMP INT-A:
Off
Range: FlexLogic™ operand
MESSAGE
BKR 1 ARC AMP INT-B:
Off
Range: FlexLogic™ operand
MESSAGE
BKR 1 ARC AMP INT-C:
Off
Range: FlexLogic™ operand
MESSAGE
BKR 1 ARC AMP
DELAY: 0.000
s
Range: 0.000 to 65.535 s in steps of 0.001
MESSAGE
BKR 1 ARC AMP LIMIT:
1000 kA2-cyc
Range: 0 to 50000 kA
2
-cycle in steps of 1
MESSAGE
BKR 1 ARC AMP BLOCK:
Off
Range: FlexLogic™ operand
MESSAGE
BKR 1 ARC AMP
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
BKR 1 ARC AMP
EVENTS: Disabled
Range: Disabled, Enabled
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...