![GE Multilin F35 Instruction Manual Download Page 153](http://html.mh-extra.com/html/ge-multilin/f35/f35_instruction-manual_572024153.webp)
GE Multilin
F35 Multiple Feeder Protection System
5-31
5 SETTINGS
5.2 PRODUCT SETUP
5
The relay supports one fast Ethernet Global Data (EGD) exchange and two slow EGD exchanges. There are 20 data items
in the fast-produced EGD exchange and 50 data items in each slow-produced exchange.
Ethernet Global Data (EGD) is a suite of protocols used for the real-time transfer of data for display and control purposes.
The relay can be configured to ‘produce’ EGD data exchanges, and other devices can be configured to ‘consume’ EGD
data exchanges. The number of produced exchanges (up to three), the data items in each exchange (up to 50), and the
exchange production rate can be configured.
EGD cannot be used to transfer data between UR-series relays. The relay supports EGD production only. An EGD
exchange will not be transmitted unless the destination address is non-zero, and at least the first data item address is set to
a valid Modbus register address. Note that the default setting value of “0” is considered invalid.
The settings menu for the fast EGD exchange is shown below:
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
EGD PROTOCOL
Ö
FAST PROD EXCH 1 CONFIGURATION
Fast exchanges (50 to 1000 ms) are generally used in control schemes. The F35 has one fast exchange (Exchange 1) and
two slow exchanges (Exchanges 2 and 3).
The settings menu for the slow EGD exchanges is shown below:
PATH: SETTINGS
Ö
PRODUCT SETUP
ÖØ
COMMUNICATIONS
ÖØ
EGD PROTOCOL
Ö
SLOW PROD EXCH 1(2) CONFIGURATION
Slow EGD exchanges (500 to 1000 ms) are generally used for the transfer and display of data items. The settings for the
fast and slow exchanges are described below:
•
EXCH 1 DESTINATION
: This setting specifies the destination IP address of the produced EGD exchange. This is usu-
ally unicast or broadcast.
•
EXCH 1 DATA RATE
: This setting specifies the rate at which this EGD exchange is transmitted. If the setting is 50 ms,
the exchange data will be updated and sent once every 50 ms. If the setting is 1000 ms, the exchange data will be
updated and sent once per second. EGD exchange 1 has a setting range of 50 to 1000 ms. Exchanges 2 and 3 have a
setting range of 500 to 1000 ms.
FAST PROD EXCH 1
CONFIGURATION
EXCH 1 FUNCTION:
Disable
Range: Disable, Enable
MESSAGE
EXCH 1 DESTINATION:
0.0.0.0
Range: standard IP address
MESSAGE
EXCH 1 DATA RATE:
1000 ms
Range: 50 to 1000 ms in steps of 1
MESSAGE
EXCH 1 DATA ITEM 1:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
↓
MESSAGE
EXCH 1 DATA ITEM 20:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range)
SLOW PROD EXCH 1
CONFIGURATION
EXCH 1 FUNCTION:
Disable
Range: Disable, Enable
MESSAGE
EXCH 1 DESTINATION:
0.0.0.0
Range: standard IP address
MESSAGE
EXCH 1 DATA RATE:
1000 ms
Range: 500 to 1000 ms in steps of 1
MESSAGE
EXCH 1 DATA ITEM 1:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
↓
MESSAGE
EXCH 1 DATA ITEM 50:
0
Range: 0 to 65535 in steps of 1
(Modbus register address range in decimal)
Summary of Contents for F35
Page 2: ......
Page 4: ......
Page 296: ...5 174 F35 Multiple Feeder Protection System GE Multilin 5 9 TESTING 5 SETTINGS 5 ...
Page 328: ...7 8 F35 Multiple Feeder Protection System GE Multilin 7 2 TARGETS 7 COMMANDS AND TARGETS 7 ...
Page 350: ...A 16 F35 Multiple Feeder Protection System GE Multilin A 1 PARAMETER LIST APPENDIXA A ...
Page 422: ...B 72 F35 Multiple Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIXB B ...
Page 472: ...E 12 F35 Multiple Feeder Protection System GE Multilin E 2 DNP POINT LISTS APPENDIXE E ...