Caution: Before you begin to work with one of these platforms, refer to the DC-powered equipment
environmental warnings for this platform and review any safety requirements for the facilities where the
DC-powered platforms will be installed.
Caution: Do not mix power supply models. If two power supplies are installed in the same system, use only
power supplies of the same model.
Important: You should use only one power supply type (AC or DC) in a platform. AC and DC interoperability
is not supported.
Important: This product is sensitive to electrostatic discharge (ESD). F5 recommends that you use proper
ESD grounding procedures and equipment when you install or maintain the unit.
Important: The platform must be installed in a RESTRICTED ACCESS LOCATION, such as a central
office or customer premises environment.
Note: Copper cables used for grounding must meet appropriate safety standards.
Note: Bare conductors should be coated with an appropriate antioxidant before being crimped. Make sure
to clean all unplated connectors, braided strap, and bus bars to a bright finish prior to coating them with
the antioxidant.
Note: The platform must be grounded to a common bonding network (CBN).
Note: The battery return terminals on the platform are in an isolated DC return (DC-I) configuration.
Wiring the DC power supply terminal block
You will need these tools to assemble and wire the DC terminal block:
•
Wire stripping tool
•
Small Phillips screwdriver
•
Small flat-head screwdriver
The 850W DC power supply includes a DC terminal block. You connect the wires to the terminal block
and then insert the terminal block into the DC power supply.
1.
Review the DC power supply label and determine the correct wire size for your installation.
2.
Use the wire stripping tool to remove 3/8 inch (9.56 mm) of insulation.
Important: Be sure to remove the appropriate amount of insulation from each wire. If you remove too
much insulation, exposed wire protruding from the terminal block can create an electrical hazard. If
you do not remove enough insulation, the wire might not make proper contact with the terminal.
3.
Thread the wires through the bottom of the terminal block, with the positive DC wire (typically red) on
the left, the chassis ground wire in the middle, and the negative DC wire (typically black) on the right.
Note the orientation of the keying notch on the terminal block. When the keying notch is up, the positive
terminal is on the left.
36
Platform Maintenance
Содержание BIG-IP 10000 Series
Страница 1: ...Platform Guide 10000 Series MAN 0408 08 ...
Страница 2: ......
Страница 6: ...6 Table of Contents ...
Страница 44: ......
Страница 48: ...Figure 13 Airflow in the 10000 Series platform 48 Environmental Guidelines ...
Страница 58: ......
Страница 60: ...7 Close and seal the shipping box 60 Repackaging Guidelines ...
Страница 64: ......