grounding conductors to a grounding connector provided a reliable bond between the connector and the
equipment is not disturbed during installation, service, or maintenance of the platform.
Important: All grounding cable terminal lugs must meet appropriate safety standards.
Note: The platform must be grounded to a common bonding network (CBN).
Figure 6: Chassis ground lug
Connecting the ground lug to the ground terminal
After the unit is installed in the rack and before you provide power to the system, you need to connect the
grounding hardware.
1.
Attach a grounding terminal lug to 12 AWG copper ground wire.
2.
Install the #8-32 Keps nuts on the ground terminal lugs.
Use 60 to 70 inch-pounds (6.8 to 8.0 Newton-meters) of torque on these Keps nuts.
3.
Connect the ground wire to a common bonding network (CBN).
About powering the platform
The AC platform ships with two power cords that you must use with the installed power supplies to power
the unit.
For DC platforms, the nominal operating DC voltage is 48 Volts.
Note: The power cables included with this unit are for exclusive use with this unit and should not be used
with other electrical appliances.
Connecting the cables and other hardware
After you have installed the unit into the rack, connect the cables and other hardware.
Important: In the event that network access is impaired or not yet configured, the serial console might be
the only way to access the unit. You should perform all installations and upgrades using the serial console,
as these procedures require reboots, in which network connectivity is lost temporarily.
30
Platform Installation
Содержание BIG-IP 10000 Series
Страница 1: ...Platform Guide 10000 Series MAN 0408 08 ...
Страница 2: ......
Страница 6: ...6 Table of Contents ...
Страница 44: ......
Страница 48: ...Figure 13 Airflow in the 10000 Series platform 48 Environmental Guidelines ...
Страница 58: ......
Страница 60: ...7 Close and seal the shipping box 60 Repackaging Guidelines ...
Страница 64: ......