Note: You attach the cable management covers to the brackets after you connect the power supply
cables to the power supplies and connect all other cables.
About grounding the chassis
You should ground the platform after you install it in a rack. The chassis grounding stud is located behind
the nameplate on the front of the chassis.
Do not secure multiple bonding or grounding connectors with the same bolt. The grounding connectors do
not need to be removed to perform service or installation procedures. You can connect other bonding or
grounding conductors to a grounding connector provided a reliable bond between the connector and the
equipment is not disturbed during installation, service, or maintenance of the platform.
Important: All copper grounding cable compression-type terminal lugs used for grounding must meet all
appropriate safety standards.
Note: The VIPRION 2400 platform must be grounded to a common bonding network (CBN).
32
Platform Installation