Figure 13: Example of label to check PWR-XXXX part number
If you cannot read the base part number, ensure that the pull handles are both in a horizontal orientation
and that the sheet metal on the power cord face for each supply has the same perforation shapes.
When you add or replace a power supply unit in your system, be sure to verify the supply's features and
that the PWR-XXXX part numbers match to ensure that you have the correct supply.
Guidelines for AC-powered equipment
An AC-powered installation must meet these requirements:
• Use a 15 amp external branch circuit protection device to install the unit.
• Use one power feed for each individual power supply.
Important: The platform must be installed in a RESTRICTED ACCESS LOCATION, such as a central
office or customer premises environment.
Note: The power cables included with this unit are for exclusive use with this unit and should not be used
with other electrical appliances.
Note: These guidelines apply to STATIONARY PLUGGABLE EQUIPMENT TYPE A with simultaneous
multiple connections to the AC MAINS SUPPLY:
• The building installation shall provide a means for connection to protective earth; and
• The equipment is to be connected to that means; and
• A SERVICE PERSON shall check whether or not the socket-outlet from which the equipment is to be
powered provides a connection to the building protective earth. If not, the SERVICE PERSON shall
arrange for the installation of a PROTECTIVE EARTHING CONDUCTOR from the separate
protective earthing terminal to the protective earth wire in the building.
Caution: High leakage current. Earth connection essential before connecting supply.
Environmental Guidelines
44
Содержание i2000 Series
Страница 1: ...Platform Guide i2000 i4000 Series MAN 0640 02 ...
Страница 2: ......
Страница 24: ...Platform Overview 24 ...
Страница 42: ...Figure 11 Rack mounting spatial requirements for the i2000 i4000 Series platform Environmental Guidelines 42 ...
Страница 46: ...Figure 14 Airflow in iSeries platforms Environmental Guidelines 46 ...
Страница 54: ...Repackaging Guidelines 54 ...