background image

F220 Series | 

Installation Instructions | 2.0 

Product family description

 

EN 

| 4 

 

 

Bosch Security Systems | 8/05 | 4998138694D 

 

Figure 3: 

Normal Sensitivity example of LED 
flashes for CleanMe 

3

5

4

1

2

 

1 -  Sequence of three green LED flashes 
2 -  Sequence of three red LED flashes 

3 -  Two green LED flashes to leave sensitivity 

mode 

4 -  8 seconds later 
5 -  Two green LED flashes to return to normal 

operation 

 

1.7 

Flash rate and trouble indication 

A unit with CleanMe activated double flashes (two 
flashes within a half second of each other) every eight 
seconds at the same rates as a normal detector. A 
normally operating unit flashes every eight seconds. If 
a detector is in a trouble condition due to a dirty lens 
or a sensor malfunction, it single or double flashes 
every four seconds, and the CleanMe trouble signal if 
enabled, is sent. 

 

If CleanMe is selected and a non-CleanMe panel 
monitors the detectors when the CleanMe signal is 
sent to the panel, it considers the signal an alarm.

1.8 

Electrical supervision  

When the F220-B6 Series Bases are properly installed, 
tamper protection is provided by IN/OUT wiring of 
the positive power line. The control panel initiates a 
trouble signal when a detector is removed from its 
base. The control panel supervises two-wire systems. 
An EOL power supervision device, such as an D275 or 
an F220-B6E Power Supervision Base and an EOL 
resistor as specified by the control panel manufacturer, 
supervises a four-wire system. 

2.0 Product 

family 

description 

Table 3:  Product Family Description 

 

 

 

 

F220-P 

Photoelectric smoke detector only, 
requires base. 

F220-PTH 

Photoelectric smoke detector w/integral 
135°F (57°C) heat sensor, requires base 

F220-PTHC* 

Photoelectric smoke detector w/integral 
135°F (57°C) heat sensor and CO 
enhanced smoke detection, requires base. 

F220-PC* 

Photoelectric smoke detector with CO 
enhanced smoke detection, requires base. 

F220-B6 

Base only, two-wire 

F220-B6C 

Base only, four-wire, Form C Auxiliary relay 

F220-B6R 

Base only, four-wire, Form A only 

F220-B6E 

Base only, for power supervision, four-wire, 
EOL relay and Form A fire contacts 

F220-B6RS 

Base only, four-wire with sounder and 
Form A fire contact 

F220-135 

Electronic heat detector 135°F (57°C), 
fixed temperature/rate-of-rise, requires 
base 

F220-135F 

Electronic heat detector 135°F (57°C), 
fixed temperature only, requires base 

F220-190F 

Electronic Heat Detector 190°F (88°C), 
fixed temperature only, requires base 

D275 

EOL supervision module for four-wire 
systems 

DRA-5 

Remote alarm indicator 

*  The F220PC and F220PTHC detect CO as a component 

of a fire. Do not use the F220PC and F220PTHC as CO 
detectors. 

 

2.1 

Compatible control panels 

Two-wire:

 See 

Technical Service Note

 

(P/N: 4998148185). 

 

Bosch Security Systems makes no claim 
written, oral, or implied that the F220 
Series Smoke Detectors work with any 
two-wire control panels except those 
specified in the Base Compatibility chart in 

Technical Service Note

 

(P/N: 4998148185). 

Four-wire:

 Compatible with all UL Listed four-wire 

control panels. Refer to the manufacturer’s 

Installation 

Instructions

 for proper EOL resistor selection. 

Содержание F220

Страница 1: ...EN Installation Instructions Photoelectric Smoke Heat Detectors F220 Series ...

Страница 2: ...open area photoelectric smoke detectors that work with commercial fire protective signaling systems and household fire warning systems Select the appropriate mounting base to configure the detectors for two wire or four wire versions For commercial and industrial installations 30 ft 9 14 m spacing between detectors is recommended To verify power to the detector and a functioning smoke sampling cir...

Страница 3: ...nce of false alarm greatly increased 15 0 5 ft 0 5 0 3 m false alarm very likely 1 6 1 The LED sensitivity flash procedure 1 Briefly place the magnet at the T on the detector base for at least one red LED flash but less then three LED flashes 2 Wait for the first single green LED flash 3 Count the number of red LED flashes that follow This indicates the sensitivity 1 6 2 Normal sensitivity LED fla...

Страница 4: ...our wire system 2 0 Product family description Table 3 Product Family Description F220 P Photoelectric smoke detector only requires base F220 PTH Photoelectric smoke detector w integral 135 F 57 C heat sensor requires base F220 PTHC Photoelectric smoke detector w integral 135 F 57 C heat sensor and CO enhanced smoke detection requires base F220 PC Photoelectric smoke detector with CO enhanced smok...

Страница 5: ...ten Depending on local regulations you can surface mount the bases using anchors mollies or wing nuts or you can mount directly to 4 in 10 cm octagonal electrical boxes and single gang switch boxes The electrical box must be large enough to accommodate the number and size of conductors specified by the National Electrical Code or any local Authorities Having Jurisdiction AHJ 4 0 Wiring information...

Страница 6: ...erted as individual ends EOL Resistors Use the EOL resistors supplied or specified by the control panel manufacturer This also applies to the D275 Module D275 Power Supervision Relay When used with 12 VDC systems connect the red wire to Terminal b1 on the last base in the run The yellow wire remains unconnected For 24 VDC systems connect the yellow wire to Terminal b1 The red wire remains unconnec...

Страница 7: ...arm Relay Form A C Terminal 4 Alarm Relay Form A NO Terminal 5 Figure 7 F220 B6C auxiliary alarm contact wiring 1 2 3 1 2 NC C NO NO C 1 Alarm NO 2 Auxiliary alarm relay 4 5 Wiring the F220 B6E The F220 B6E base has a normally open alarm loop relay and an auxiliary set of normally open contacts The contacts are rated 0 5 A use at 125 VAC and 1 0 A use at 30 VDC for resistive loads Do not use with ...

Страница 8: ...instructions 2 Attach the base skirt by aligning the four hardware keys or turn the base skirt slowly clockwise until it rests in place Press firmly to latch it onto the fixing clamps See Figure 10 Use the tamper tab locking bar to prohibit detector removal as follows 3 The snap off locking bar X is part of the base molding Shift the locking bar X into the position shown in Figure 9 to engage it 4...

Страница 9: ...March Time signal Positions 3 and 4 off Steady signal Figure 12 F220 B6RS 4 wire configuration with D275 tandem connection NO C INT b1 b2 c a1 a2 NO C INT b2 c a1 a2 NO C INT b2 c a1 a2 1 2 3 3 4 5 1 2 1 2 1 2 3 3 3 SEP SEP SEP SEP SEP SEP 6 7 b1 b1 8 8 8 1 D275 2 Alarm loop Terminal 1 and 2 3 Blue wire D275 Terminal 1 and EOLR 4 Black wire D275 Common 5 Yellow wire D275 for 24 V systems 6 Red wir...

Страница 10: ... second rate the detector is either cold out of sensitivity range or defective If the smoke detector LED flashes at a four second rate the detector is out of sensitivity range or defective 12 Test each detector to ensure it causes a control panel alarm Reset the control panel after each test To alarm the F220 135 135F 190F Detectors either Place a magnet horizontally against the T and hold it ther...

Страница 11: ...tion tests at installation then every other year Perform functional testing yearly Notify all concerned parties before any maintenance or testing of the fire alarm system and upon completion of these activities Test the calibration to meet NFPA using either the magnet test or measuring the calibration with a calibrated product from No Climb Products Ltd Quickly determine the calibration by a visua...

Страница 12: ... Time 22 second maximum Alarm current for all F220 Detectors 20 mA minimum use at 8 5 VDC 35 mA maximum use at 32 VDC F220 B6 2 wire 8 5 to 32 0 VDC F220 B6 R C E RS 4 wire 10 0 to 30 0 VDC Alarm Current only base current head current excluded F220 B6C 31 mA use at 12 VDC 35 mA use at 24 VDC 40 mA maximum use at 30 VDC F220 B6R 13 5 mA use at 12 VDC 16 5 mA use at 24 VDC 19 mA maximum use at 30 VD...

Страница 13: ... 13 Bosch Security Systems 8 05 4998138694D Trademarks CleanMe is a trademark of GE Interlogix ChamberMaid and Chamber Check are a trademarks of Bosch Security Systems TECHSPRAY is a registered trademark and ENVI RO TECH is a trademark of Tech Spray L P ...

Страница 14: ...F220 Series Installation Instructions Notes EN 14 Bosch Security Systems 8 05 4998138694D Notes ...

Страница 15: ...F220 Series Installation Instructions Notes EN 15 Bosch Security Systems 8 05 4998138694D Notes ...

Страница 16: ... 2005 Bosch Security Systems 4998138694D Bosch Security Systems 130 Perinton Parkway Fairport NY 14450 9199 Customer Service 800 289 0096 Technical Support 888 886 6189 ...

Отзывы: