Wiring information
EN
| 7
Bosch Security Systems | 8/05 | 4998138694D
4.3 Wiring
the
F220-B6R
The F220-B6R is the standard base for four-wire
configurations. The Alarm Loop Relay (terminals NO
and C) is a normally open relay rated 0.5 A use at
100 VDC. The relay closes on alarm.
Table 5: F220-B6R Terminal Functions
(see
Figure 6
)
DC
−
IN/OUT
a1/a2
DC + IN
b1
DC + OUT
b2
Remote LED output
c
Alarm Contact
NO (Terminal 1)
Alarm Relay
C (Terminal 2)
4.4 Wiring
the
F220-B6C
The F220-B6C base has a normally open alarm loop
relay and auxiliary Form C (NC/C/NO) contacts.
The contacts are rated 0.5 A use at 125 VAC and 1.0 A
use at 30 VDC for resistive loads. Do not use with
inductive or capacitive loads.
Table 6: F220-B6C terminal functions
(see
Figure 7
)
DC
−
IN/OUT
a1/a2
DC + IN
b1
DC + OUT
b2
Remote LED output
c
Auxiliary Form C
NC (Terminal 1)
Auxiliary Form C
C (Terminal 2)
Auxiliary Form C
NO (Terminal 3)
Alarm Relay Form A
C (Terminal 4)
Alarm Relay Form A
NO (Terminal 5)
Figure 7:
F220-B6C auxiliary/alarm contact
wiring
1 2 3
1
2
NC C NO
NO
C
1 - Alarm (NO)
2 - Auxiliary alarm relay
4.5 Wiring
the
F220-B6E
The F220-B6E base has a normally open alarm loop
relay and an auxiliary set of normally open contacts.
The contacts are rated 0.5 A use at 125 VAC and 1.0 A
use at 30 VDC for resistive loads. Do not use with
inductive or capacitive loads.
The F220-B6E base also provides EOL power
supervision through a built in relay. Separate power
supervision devices, such as the D275, are unnecessary.
Use only one F220-B6E per zone run. It must be the
last base on the run.
The EOL Relay is rated 0.5 A use at 100 VDC for
resistive loads.
Table 7: F220-B6E terminal functions
(see
Figure 8
)
DC
−
IN/OUT
a1/a2
DC + IN
b1
DC + OUT
b2
Remote LED output
c
Alarm Form A
NO (Terminal 1)
Alarm Relay Form A
C (Terminal 2)
EOL Relay Form A
NO (Terminal 3)
EOL Relay Form A
C (Terminal 4)
(Terminal 5) Not connected
Figure 8:
F220-B6E power supervision base
b1
b2
c
a1/a2
(+)
(–)
1 2 3
1
2
3
1 - Alarm loop (Terminals 1 and 2)
2 - Jumper (Terminals 2 and 3)
3 - EOL resistor (Terminals 1 and 4)