background image

F220 Series | 

Installation Instructions | 1.0 

General Information

 

EN 

| 2 

 

 

Bosch Security Systems | 8/05 | 4998138694D 

 

1.0 General 

Information 

1.1 

F220-B6 Series Bases  

Use with the F220 Series Heat and Photoelectric 
Smoke Detectors. Install them in accordance with 
NFPA 72, The National Fire Alarm Code. 

 

For proper system installation, read and 
understand NFPA-72, The National Fire 
Alarm Code before installation. 

This document covers mounting, wiring, power 
requirements, testing, and maintenance for the bases 
and detectors:  

 

For two-wire compatibility information see the 

Technical Service Note

 (P/N: 4998148185). 

 

For installation guidelines see the 

Technical Service 

Note

 (P/N: 26715). 

1.2 Detector 

Features 

Figure 1: 

F220 Series features 

T

2

4

1

5

6

3

 

1 -  Detector front 
2 -  LED 
3 -  Thermistor 
4 -  “T” mark 
5 -   Detector back 
6 -  ChamberMaid™ location 

 

1.3 F220 

-135/135F/190F Electronic 

Rate-of-Rise/Fixed Temperature 
Heat Detectors 

Table 1:  Color coding for heat detectors 

 

 

 

 

F220-135/135F 

A gray circle around the thermistor. 

F220-190F 

A black circle around the thermistor. 

 

 

Use with F220 Series bases to provide general property 
protection. 

 

The F220-135, F220-135F and F220-
190F are not life safety devices. 

1.4 F220-P/-PTH/-PC/-PTHC 

Photoelectronic Smoke Detectors 

The F220P Series Detectors are UL Listed, open-area 
photoelectric smoke detectors that work with 
commercial fire protective signaling systems and 
household fire warning systems. Select the appropriate 
mounting base to configure the detectors for two-wire 
or four-wire versions. 

For commercial and industrial installations, 30 ft 
(9.14 m) spacing between detectors is recommended. 

To verify power to the detector and a functioning 
smoke sampling circuitry, a dual color LED indicator 
flashes green every eight seconds when operating 
normally. It flashes once every four seconds when a 
trouble condition exists. 

If the detector finds an alarm condition, the LED 
changes from flashing green to steady red. The detector 
returns to normal when power is interrupted and the 
alarm condition clears. 

Throughout its normal life cycle, the smoke detector 
monitors and periodically readjusts itself to keep the 
sensitivity at its factory calibrated level. When 
excessively dirty, the detector’s LED flash rate changes 
from an eight second flash rate to a four second rate. If 
CleanMe™ is selected, the detector transmits a 
CleanMe signal to the compatible control panel to 
indicate a dirty smoke detector. 
See 

Section 1.5 CleanMe toggle 

to enable CleanMe. 

1.5 CleanMe 

toggle 

To activate the CleanMe feature: 
1.

 

Place a magnet next to the “T” marked on the 
detector base for more than one red LED flash but 
less than three red LED flashes. The LED flashes 
green one time and proceeds into the first of two 
sensitivity reading displays. 

Содержание F220

Страница 1: ...EN Installation Instructions Photoelectric Smoke Heat Detectors F220 Series ...

Страница 2: ...open area photoelectric smoke detectors that work with commercial fire protective signaling systems and household fire warning systems Select the appropriate mounting base to configure the detectors for two wire or four wire versions For commercial and industrial installations 30 ft 9 14 m spacing between detectors is recommended To verify power to the detector and a functioning smoke sampling cir...

Страница 3: ...nce of false alarm greatly increased 15 0 5 ft 0 5 0 3 m false alarm very likely 1 6 1 The LED sensitivity flash procedure 1 Briefly place the magnet at the T on the detector base for at least one red LED flash but less then three LED flashes 2 Wait for the first single green LED flash 3 Count the number of red LED flashes that follow This indicates the sensitivity 1 6 2 Normal sensitivity LED fla...

Страница 4: ...our wire system 2 0 Product family description Table 3 Product Family Description F220 P Photoelectric smoke detector only requires base F220 PTH Photoelectric smoke detector w integral 135 F 57 C heat sensor requires base F220 PTHC Photoelectric smoke detector w integral 135 F 57 C heat sensor and CO enhanced smoke detection requires base F220 PC Photoelectric smoke detector with CO enhanced smok...

Страница 5: ...ten Depending on local regulations you can surface mount the bases using anchors mollies or wing nuts or you can mount directly to 4 in 10 cm octagonal electrical boxes and single gang switch boxes The electrical box must be large enough to accommodate the number and size of conductors specified by the National Electrical Code or any local Authorities Having Jurisdiction AHJ 4 0 Wiring information...

Страница 6: ...erted as individual ends EOL Resistors Use the EOL resistors supplied or specified by the control panel manufacturer This also applies to the D275 Module D275 Power Supervision Relay When used with 12 VDC systems connect the red wire to Terminal b1 on the last base in the run The yellow wire remains unconnected For 24 VDC systems connect the yellow wire to Terminal b1 The red wire remains unconnec...

Страница 7: ...arm Relay Form A C Terminal 4 Alarm Relay Form A NO Terminal 5 Figure 7 F220 B6C auxiliary alarm contact wiring 1 2 3 1 2 NC C NO NO C 1 Alarm NO 2 Auxiliary alarm relay 4 5 Wiring the F220 B6E The F220 B6E base has a normally open alarm loop relay and an auxiliary set of normally open contacts The contacts are rated 0 5 A use at 125 VAC and 1 0 A use at 30 VDC for resistive loads Do not use with ...

Страница 8: ...instructions 2 Attach the base skirt by aligning the four hardware keys or turn the base skirt slowly clockwise until it rests in place Press firmly to latch it onto the fixing clamps See Figure 10 Use the tamper tab locking bar to prohibit detector removal as follows 3 The snap off locking bar X is part of the base molding Shift the locking bar X into the position shown in Figure 9 to engage it 4...

Страница 9: ...March Time signal Positions 3 and 4 off Steady signal Figure 12 F220 B6RS 4 wire configuration with D275 tandem connection NO C INT b1 b2 c a1 a2 NO C INT b2 c a1 a2 NO C INT b2 c a1 a2 1 2 3 3 4 5 1 2 1 2 1 2 3 3 3 SEP SEP SEP SEP SEP SEP 6 7 b1 b1 8 8 8 1 D275 2 Alarm loop Terminal 1 and 2 3 Blue wire D275 Terminal 1 and EOLR 4 Black wire D275 Common 5 Yellow wire D275 for 24 V systems 6 Red wir...

Страница 10: ... second rate the detector is either cold out of sensitivity range or defective If the smoke detector LED flashes at a four second rate the detector is out of sensitivity range or defective 12 Test each detector to ensure it causes a control panel alarm Reset the control panel after each test To alarm the F220 135 135F 190F Detectors either Place a magnet horizontally against the T and hold it ther...

Страница 11: ...tion tests at installation then every other year Perform functional testing yearly Notify all concerned parties before any maintenance or testing of the fire alarm system and upon completion of these activities Test the calibration to meet NFPA using either the magnet test or measuring the calibration with a calibrated product from No Climb Products Ltd Quickly determine the calibration by a visua...

Страница 12: ... Time 22 second maximum Alarm current for all F220 Detectors 20 mA minimum use at 8 5 VDC 35 mA maximum use at 32 VDC F220 B6 2 wire 8 5 to 32 0 VDC F220 B6 R C E RS 4 wire 10 0 to 30 0 VDC Alarm Current only base current head current excluded F220 B6C 31 mA use at 12 VDC 35 mA use at 24 VDC 40 mA maximum use at 30 VDC F220 B6R 13 5 mA use at 12 VDC 16 5 mA use at 24 VDC 19 mA maximum use at 30 VD...

Страница 13: ... 13 Bosch Security Systems 8 05 4998138694D Trademarks CleanMe is a trademark of GE Interlogix ChamberMaid and Chamber Check are a trademarks of Bosch Security Systems TECHSPRAY is a registered trademark and ENVI RO TECH is a trademark of Tech Spray L P ...

Страница 14: ...F220 Series Installation Instructions Notes EN 14 Bosch Security Systems 8 05 4998138694D Notes ...

Страница 15: ...F220 Series Installation Instructions Notes EN 15 Bosch Security Systems 8 05 4998138694D Notes ...

Страница 16: ... 2005 Bosch Security Systems 4998138694D Bosch Security Systems 130 Perinton Parkway Fairport NY 14450 9199 Customer Service 800 289 0096 Technical Support 888 886 6189 ...

Отзывы: