Installation & Servicing

GENERAL

Rated output

Minimum bore

Nominal Size (DN)

kW

m m

in

61 to 150

32

1

/

4

151 to 300

38

1

/

2

'Steel pipe sizes complying with medium or heavy quality or BS 1387.

Detail reference should be made to the appropriate standards listed on
page 4.
The information and guidance given below is not intended to override any
requirements of the above publications or the requirements of the local
authority, gas or water undertakings.
The vertical distance between the pump and feed/expansion cistern MUST
comply with the pump manufacturer's minimum requirements, to avoid
cavitation.  Should these conditions not apply either lower the pump
position or raise the cistern above the minimum requirement specified by

Ideal Stelrad Group

.  The isolation valves should be fitted as close to the

pump as possible.
The information provided is based on the following assumptions:

1.

An independent open vent/safety pipe connection is made immediately
after the system flow pipe connection.

2.

An independent cold feed/expansion pipe connection is made
immediately after the open vent/safety pipe connection.

3.

The maximum flow rate through the boiler is based on a temperature
difference of 11

o

C at full boiler output.

4.

The boiler is at the highest point of circulation in the system.  Systems
designed to rise above the boiler flow tappings will automatically
require a minimum static head higher than that shown.

5.

The position of the open vent/safety pipe above the expansion cistern
water level is given as a guide only.  The final position will depend upon
the particular characteristics of the system.  Pumping over of water into
the expansion cistern must be avoided.

6.

Both open vent/safety pipe and cold feed/expansion pipes must be of
adequate diameter to suit the output of the boiler.  Refer to Tables
below.

4

OPEN VENTED SYSTEM REQUIREMENTS

Note.

With a cold feed head of <8m, the pump
must be fitted on the return to the boiler.

This diagram does not show safety valves,
water flow switches, etc. necessary for the
safe operation of the system.

5

SEALED SYSTEM REQUIREMENTS

Open Vent Pipe Sizes

Rated output

Minimum bore

Nominal Size (DN)

kW

m m

in

60 to 150

25

1

151 to 300

32

1

/

4

'Steel pipe sizes complying with medium or heavy quality or  BS 1387.

Cold Feed Pipe Sizes

Note.

  

Refer to Frame 22 for typical system arrangements.

Feed/expansion

cistern

Open vent
safety pipe

3 m 
minimum
see notes

System
flow

Shunt Pump

(if required)

Inverted

cold feed

entry

Cold

Feed

Water

level

(cold)

Open vent

System
return

im8250

Connections

to boiler

Working pressure 6 bar maximum.

Particular reference should be made to BS. 6644 and
Guidance note PM5 "Automatically controlled steam and hot
water boilers" published by the Health and Safety Executive.
The information and guidance given below is not intended to
override any requirements of either of the above publications or
the requirements of the local authority, gas or water
undertakings.
In general commercial closed pressurised systems are
provided with either manual or automatic water make up.
In both instances it will be necessary to fit automatic controls
intended to protect the boiler, circulating system and ancillary
equipment by shutting down the boiler plant if a potentially
hazardous situation should arise.
Examples of such situations are low water level and operating
pressure or excessive pressure within the system.  Depending
on circumstances, controls will need to be either manual or
automatic reset.  In the event of a shutdown both visual and
audible alarms may be necessary.

Expansion vessels used must comply with BS. 4814 and must
be sized on the basis of the total system volume and initial
charge pressure.
Initial minimum charge pressure should not be less than 0.5
bar (7.2psi) and must take account of the static head and
specification of the pressurising equipment.  The maximum
water temperatures permissible at the point of minimum
pressure in the system are specified in Guidance Note PM5.
When make up water is not provided automatically it will be
necessary to fit controls which shut down the plant in the event
of the maximum system pressure approaching to within
0.35bar (5psi) of the safety valve setting.
Other British Standards applicable to commercial sealed
systems are:
BS. 6880: Part 2
BS. 1212
BS. 6281: Part 1
BS. 6282: Part 1
BS. 6283: Part 4

Summary of Contents for F80

Page 1: ...ing any part on this appliance use only spare parts that you can be assured conform to the safety and performance specification that we require Do not use reconditioned or copy parts that have not bee...

Page 2: ...37 8MJ m3 1038Btu ft3 gross or 34 MJ m3 910 Btu ft3 nett at 15o C and 1013 25 mbar a For l s divide the gross heat input kW by the gross C V of the gas MJ m3 b For ft h3 divide the gross heat input Bt...

Page 3: ...tion Countries GB IE Key to symbols IE Ireland GB United Kingdom Countries of destination PMS Maximum operating pressure of water C53 A room sealed appliance which is connected via its separate ducts...

Page 4: ...mmercial premises IGE UP 10 Installation of gas appliances in industrial and commercial premises SAFE HANDLING OF SUBSTANCES No asbestos mercury or CFCs are included in any part of the boiler or its m...

Page 5: ...system must be impervious to condensate leakage Low points in the flue system should be drained using pipe of material resistant to condensate corrosion All drains in the flue should incorporate a wat...

Page 6: ...e of Fernox Copal or MB1 or GE Betz Sentinel X100 inhibitors and associated water treatment products which must be used in accordance with the manufacturers instructions For further information contac...

Page 7: ...B 600 510 232 125 R2 Flow Connection R1 Gas Connection Electrical Conduit Electrical Conduit Air Inlet O110 678 382 125 333 869 C 30 200 SIDE VIEW REAR VIEW PLAN VIEW FRONT VIEW im8252 A B C D F80 F1...

Page 8: ...from a clean source outside the boiler room building Open Flued Installations If ventilation is to be provided by means of permanent high and low vents communicating direct with outside air then refe...

Page 9: ...ALED SYSTEM REQUIREMENTS Open Vent Pipe Sizes Rated output Minimum bore Nominal Size DN kW m m in 60 to 150 25 1 151 to 300 32 1 1 4 Steel pipe sizes complying with medium or heavy quality or BS 1387...

Page 10: ...panel 2 Burner switch 3 Pressure gauge 5 Casing front panel 6 Casing top panel 7 Casing side panel 8 Fan 9 Gas Valve 11 Venturi 12 Control Module 14 Alarm boiler run relays board 19 Union Gas cock 20...

Page 11: ...ir direct from outside use any proprietary 110mm soil drain pipe The air duct should be terminated with a suitable fixed grille to prevent entry of vermin This terminal should be positioned as such to...

Page 12: ...before connecting the system pipework An air vent must be provided immediately after the flow connection If installing the boiler onto an existing system it is strongly recommended that the system be...

Page 13: ...e pole switch having a 3mm 1 8 contact separation in both poles or a plug and unswitched socket serving only the boiler and system controls The means of isolation must be accessible to the user after...

Page 14: ...ure 0 10V DC 0 10 Micro amp flame ionisation current Optional connections for DHW tank sensor kit 230V AC output for CH system pump max 1 amp Optional 230V AC output for DHW pump or divertor valve max...

Page 15: ...pplied to CH call the boiler is not switched off but simply reduces the flow temperature by a fixed value parameter 20 see instructions with kit for more details 3 Programmable Room Thermostat Kit The...

Page 16: ...rcuit is off 1 3 1 1 1 2 4 2 2 2 4 4 4 6 6 6 7 7 3 3 3 5 5 5 9 9 11 11 8 8 10 10 12 12 1 1 2 2 3 3 4 4 5 5 6 6 7 7 8 8 9 10 11 12 PWM TACH E L N 13 14 DISPLAY AM3 BOILER ON VOLT FREE CONTACTS BOILER L...

Page 17: ...provides enhanced user comfort Full instructions provided with kits Pump Pump Non return valve Non return valve Cylinder thermostat Programmer Room stat im8191 The switched live from external controls...

Page 18: ...CALL The boiler will be limited to responding with a set flow temperature set by parameter 4 If all zones are fitted with individual zone valves a hydraulic bypass will be required to allow pump over...

Page 19: ...h to have a 3 way valve normally open towards the storage tank DHW circuit from AB to B Upon CH request terminal L on DHW PUMP OR VALVE is energised which through a relay powers the 3 way valve thus c...

Page 20: ...switching on the mains power or after a reset the boiler performs a selfcheck i e the DHW valve is energised and the CH pump is switched on for 10 seconds This cycle repeats itself every 24hrs as long...

Page 21: ...o show it has been accepted The new setting will become active when the parameter mode is left 24 STANDARD CONTROLS ACCESS Modes of Operation The standby parameter and information modes are accessible...

Page 22: ...36 displayed if tank sensor kit not fitted FLUE GAS Temperature T5 o C Set Flow Temperature o C 5 7 0 6 8 2 7 0 0 Rate of Return Temperature Rise o C s 8 0 0 Rate of Flow Temperature Rise o C s 9 0 0...

Page 23: ...100 thousands 10 thousands I 0 0 Boiler Control Module Internal Temperature o C Number of Ignitions CH tens units Number of Ignitions CH thousands hundreds Info mode cont d continued Burner Run Hours...

Page 24: ...iption Min Load Run for 15 mins Press the mode and button simultaneously for 3 seconds H 8 0 Press Display Description Max Load Run for 15 mins OR Last 3 digits are actual flow temperature This mode w...

Page 25: ...of access MUST NOT be entered by the user Code Mode By entering the service code the following additional features are accessible Parameters 5 to 53 Fan Speed Mode Communication Mode Error Mode Code M...

Page 26: ...4 8 2 2 0 1 2 3 4 P10 appears for 1 second then 10 Minimum outside temperature o C 20 10 05 Coldest outside temp the system is designed to work against 11 P11 Maximum outside temperature o C 15 25 20...

Page 27: ...Do not Do not 35 F200 adjust adjust 25 F240 25 F280 25 3 5 28 P28 P23 Maximum fan speed CH units F80 00 F120 50 F160 Do not Do not 00 F200 adjust adjust 00 F240 00 F280 00 P24 Maximum fan speed DHW h...

Page 28: ...35 P35 DHW modulation hysteresis on o C 03 30 03 0 5 36 P36 DHW modulation hysteresis off o C 03 30 03 0 5 37 P37 0 3 0 3 0 0 0 0 Blocking time DHW to CH seconds 0 30 05 0 switch with burner on x10 2...

Page 29: ...adjust 3x N A First digit factory set to 0 Do not adjust 4x N A First digit factory set to 0 Do not adjust 5x N A First digit factory set to 0 Do not adjust 6x N A First digit factory set to 0 Do not...

Page 30: ...ess Display Description In error mode the last error is shown and the boiler status and readings at that time are available The 1st digit flashes and shows the current step The last two digits show th...

Page 31: ...operate the boiler and measure the flue CO2 values at maximum and minimum rates whilst adjusting the gas valve if necessary Refer to Frame 44 8 Operate the boiler for 10 minutes and check the gas rat...

Page 32: ...with the regional gas authority or a CORGI registered heating installer In IE servicing work must be carried out by a competent person 42 SAFETY It is the law that any service work must be carried ou...

Page 33: ...st annually Ideal Stelrad Group does not accept any liability resulting from the use of unauthorised parts or the repair and servicing of appliances not carried out in accordance with the Company s re...

Page 34: ...to rest on the hinge lugs Top Panel 5 Undo the 2 screws at the rear edge of the panel lift from the side panel studs and remove 6 1 Side Panels 6 Undo the 2 screws at the rear and the 2 screws at the...

Page 35: ...cket right jacket top and controls fascia panels Refer to Frame 45 3 Disconnect the electrical connections from the fan 4 Remove 4 bolts securing inlet air pipe silencer to the venturi taking care to...

Page 36: ...replacing any seals gaskets which show signs of wear When re fitting the burner there are 2 small lugs cast into the end of the combustion chamber which support the end of the burner 7 Refer to Frame...

Page 37: ...ront controls fascia top and left side panels Refer to Frame 45 3 Place a container beneath the condensate trap to collect the condensate contained within 4 Remove bottom nut plug from the condensate...

Page 38: ...sing pliers to apply the grip Replace gas valve inlet outlet O rings if showing signs of wear 10 Refer to instruciton sheet with spare gas valve for correct setting procedure 11 Refer to Frame 42 for...

Page 39: ...ll off the HT and earth leads from the spark detection electrode 7 Remove the 2 nuts and washers 8 Check the electrode gap is 4 0mm 9 Replace the electrode using the new gasket provided 10 Re assemble...

Page 40: ...e 45 3 Isolate water circuit and drain boiler 4 Pull off the electrical connections from the thermistor 5 Unscrew the thermistor 6 Fit the new thermistor with built in O ring seal Do not overtighten 7...

Page 41: ...splay board from the 4 studs 6 Fit the new display board and re assemble in reverse order 7 Refer to Frame 42 for final safety checks 4 3 59 BOILER CONTROL MODULE REPLACEMENT 1 Refer to Frame 42 2 Rem...

Page 42: ...ernal failure Check wiring harness connections If wiring OK replace control module 16 Internal failure Check wiring harness connections If wiring OK replace control module 17 Internal failure Check wi...

Page 43: ...t terminals from thermistor confirm open circuit using meter Replace thermistor 44 Internal Failure Check wiring harness connections If wiring OK replace control module 52 Flue gas temperature too hig...

Page 44: ...from thermistor confirm short circuit using meter Replace thermistor 38 Tank sensor open circuit If not fitted check parameter 46 settings Check wiring Disconnect terminals from tank sensor confirm op...