9.ERROR CODE
102
Calibration Error 9
Calibration procedures have not completed because the reading of F159 widly
fluctuated. Adjust parameters for stable readings (time, width) and make sure
“stable” bit turns on, then perform calibration again.
9-2-2. Weight Error
EXC ALM
The load cell excitatio voltage is too low. Check all the cables for proper
connection between F159 and the load cell, and if any of the cables are
overloaded.
Span adjustable range for F159 is from 0.3 to 3.2 (mV/V), within which
the Span value should fall.
Therefore, if the load cell output for the maximus loadable weight
(Capacity) falls short of 0.3 mV/V (Calibration Error 6) or exceeds 3.2
mV/V (Calibration Error 8), the Span calibration fails.
Capacity
0
0.3
3.2
Load
Load cell output
[
mV/V
]
Span adjustable range
“
Calibration Error 6
”
“
Calibration Error 8
”