52
11
Appendix
Input parameters
Auxiliary power
Supply voltage
Max. 42 V DC
Min. 24 V DC
Supply current
≤
20 mA
Pulse
Current
High > 0,8 mA
Low < 0,4 mA
Sensitivity measuring output
FFS07/ FFS08 IR
> 10 mV AC
FFS08 UV
> 25 mV AC
Output parameters
Signal Channels A + B
Frequency:
Max. 170 Hz
Min. 7 Hz
Connection cable/extension cable
Type
6 x 0,5 mm
2
shielded,
z.B. LiYCY minimum cross section 0,5 mm²
Cable length
< 300 m
Wear parts
none
Technical capacity
Operating mode
Continuous operation
72 h of operation according to TRD 604
Safety integrity level
DIN EN 61508 2 - SIL 3 in conjunction with F152
Over voltage category
DIN EN 60730-1 ÜKIII
Susceptibility to interference
DIN EN 60730-1
Emitted interference
DIN EN 55022:2006, class B
Climatic range
Protection class
DIN EN 60529:2000, IP67
Operating temperature range
1
IR - 20 ... + 60 °C, UV - 20 ... + 65°C
Relative humidity:
0 % ... 95 % non-condensing
Use in explosive atmospheres
only FFS07
device group/device categories, potentially
explosive atmosphere, Standard
II 3G, Zone 2, Zone 22, DIN EN 60079
Marking
IECEx IBE 15.0010X, ATEX conformity
Ex nA IIC T6...T5 Gc X, Ex tc IIIC T95°C Dc X
Operating temperature range
Ambient temperature
T6 -20 °C ... + 60 °C
Relative humidity
0 % ... 95 % non-condensing
Additional information
Respect section "Special information for usage in potentially
explosive areas".
Содержание F152
Страница 1: ...www lamtec de Sensors and Systems for Combustion Engineering Manual Flame Monitoring Device F152...
Страница 2: ......
Страница 16: ...15 3 Product Description Optimised LAMTEC ball and socket joint for FFS08 Fig 3 5 Brackets for FFS08...
Страница 37: ...36 5 Commissioning Closing of the sensor housing Fig 5 6 Close FFS08 IR...
Страница 61: ...60 11 Appendix 11 3 Declaration of Conformity...
Страница 62: ...61 11 Appendix...
Страница 65: ...64 11 Appendix...