32
5
Commissioning
5.3.3
Testing the Functions
Measurement of the signal voltage and the flame sensor
Flame radiation may be measured between the blue wire (ground) and the pink wire (meas-
uring line) of the sensor’s connecting cable. Therefore a standard measuring instrument e. g.
hand-held multi-meter according to EN 61010 with a measuring resistor > 5 M
may be used.
The measured voltage may lie in a range between a few mV up to 0,3 VAC with FFS08 UV
and up to 3 VAC by the other types.
NOTICE
The measuring output is intended for commissioning and maintenance.
A permanent connection of a measuring device is not intended.
In the following table, values are shown at which point the flame sensor interprets pending sig-
nals as flame signals.
For an optimal suppression of background radiation the measured values should be signifi-
cantly smaller than the described values below after the burner is switched off.
For reliable flame detection at a stable signal a two-fold value should be good enough. If the
flame detection is not stable higher values may be necessary.
After opening the housing, FFS08 IR-1 and FFS07 offers the opportunity to modify sensitivity
with the help of DIP switches (see chapter
). According to this the mini-
mum value for the signal "flame ON" changes.
FFS08 UV does not offer this opportunity for safty reasons.
Flame scanners FFS08 IR-1, FFS07 IR-1, FFS07 UV-1, FFS07 UV-4
Ultraviolet Flame scanners FFS08 UV-1/UV-4
Switch
Connection
Sx/1
Sx/2
Position
pink/blue
OFF
OFF
1
50 mV~
ON
OFF
2
30 mV~
IR factory setting
OFF
ON
3
20 mV~
ON
ON
4
15 mV~
UV factory setting
Amibent noise
without signal
typical
1 (<2) mV~
Connection
pink/blue
25 mV~
factory setting
Ambient noise
without signal
typical
6 (<8) mV~
Содержание F152
Страница 1: ...www lamtec de Sensors and Systems for Combustion Engineering Manual Flame Monitoring Device F152...
Страница 2: ......
Страница 16: ...15 3 Product Description Optimised LAMTEC ball and socket joint for FFS08 Fig 3 5 Brackets for FFS08...
Страница 37: ...36 5 Commissioning Closing of the sensor housing Fig 5 6 Close FFS08 IR...
Страница 61: ...60 11 Appendix 11 3 Declaration of Conformity...
Страница 62: ...61 11 Appendix...
Страница 65: ...64 11 Appendix...