Figure 6: Chassis ground lugs (with and without protective cap)
Connect the ground lug to the ground terminal
You must provide these components to properly ground the chassis:
•
Crimping tool
•
Dual ring ground terminal lug (for example, Panduit dual ring grounding lug, part number
LCDX6-10AF-L)
•
One 6 AWG copper wire long enough to reach from the chassis to the common bonding network (CBN)
After the unit is installed in the rack and before you provide power to the system, you need to connect the
grounding hardware.
1.
Remove the M4 Keps nuts from the ground lug on the back of the chassis.
2.
Attach a ground ring terminal to the 6 AWG copper ground wire.
3.
Install the ground ring terminal onto the chassis ground terminal.
4.
Secure the ground ring terminal with the M4 Keps nuts.
Use 18 to 24 inch-pounds (2.0 to 2.7 Newton-meters) of torque on these Keps nuts.
5.
Connect the ground wire to a common bonding network (CBN).
Connect the cables and other hardware
After you have installed the unit into the rack, connect the cables and other hardware.