30
5
Commissioning
5.3
Putting the Device into Operation for the First Time
5.3.1
Requirements
Prerequisites for putting the device into operation for the first time: :
•
The F152 and the respective flame scanner must be mounted as specified in chapter
•
The flame scanner must be aligned as specified in
5.3.2 Adjustment and Positioning
•
All electrical installations must have been tested.
•
All terminal and plug-in connections must have been tested.
NOTICE
Putting the device into operation
To operate the Flame scanner safely, you have to adhere to the following sequence when
putting it into operation for the first time:
NOTICE
Flame intensity indication F152
If no load is connected to the current loop terminal X14/3,4, it is necessary to insert a wire
bridge at the terminals on F152. Otherwise the flame intensity will not be displayed on the
F152.
5.3.2
Adjustment and Positioning
WARNING!
Checking the switch-off parameters
There is a risk of death and serious injury.
The switch-off parameters are to be verified through switch-off tests, see chapter
. Changes made to settings (increase or weighting of doublesensor) do af-
fect the switcht-off parameters and therefore new switch-off tests are to be carried out.
NOTICE
Reliable detection of the flame
Warning to avoid damage to property
Set the parameters in such a way that, across the entire performance range and in all of
the combustion's modes, safe detection of "flame OFF" and stable detection of "flame ON"
are ensured.