Brownout Or Blackout
If a blackout or brownout occurs the F60 pump controller will not retain any
memory of where in its run or stop cycle it may have been, it will simply shut down
the pump. When power resumes, the F60 will reboot, restart the pump and run
any timer settings from the beginning. A manual reboot can be done at any time
by simply pressing the controller’s reset button.
Cables
The F60 has 3 X M20 cable glands. As supplied, the cable glands are blanked
off. To use the glands first punch out the blanking barriers using a suitable punch.
The cable glands can accept cable from 7 to 9mm diameter. See attached sketch
for assembling the cable gland components. The controller is supplied with a set
of steel crimp rings. The crimp rings are to provide strain relief for the controller’s
cables. To use the crimps, place one on the cable approximately 3 to 4mm below
the end to the cable’s outer sheathing. Crimp the two ears of the ring flat using
bull nosed pliers. Pull the cable back through the cable gland until the crimp ring’s
ears are fully located into the slots in the cable gland housing.
17
The F60 derives low voltage for its operation
from a non-isolated reactance power supply
(not through an isolated transformer). All
external devices connected to the F60
controller must be earthed and must be
regarded as operating at full mains potential.
WARNING