Fig. 14. Typical use of duct offset to make room for media 

air cleaner.

INSTALLATION AND CHECKOUT

When Installing this Product…

1.

Read these instructions carefully. Failure to follow them 

could damage the media air filter or cause a hazardous 

condition.

2.

Check the ratings given in the instructions and on the 

media air cleaner to make sure the product is suitable for 

your application.

3.

Installer must be a trained, experienced service

technician.

Remove Furnace Filter And Clean Blower 

Compartment

Before starting the installation, remove and discard the existing 

furnace filter (if used). Thoroughly clean the blower 

compartment. If possible, power vacuum the ductwork to 

remove accumulated dust in an occupied home or remove 

construction dirt in a new home. The media air cleaner cannot 

remove dirt that has settled in the blower compartment and 

distribution ducts.

Install The Cabinet

The following procedure describes a typical side installation on 

an existing highboy furnace. Alternate procedures are noted as 

appropriate. Other changes in installation procedures may be 

necessary to complete your installation.

Review The Installation Plan

Temporarily place the cabinet on the floor, oriented as it will be 

when installed. Insert and remove the cartridge to make sure 

the plan allows adequate clearance for easy removal and 

replacement of the cartridge.

Make sure that shop-fabricated sheetmetal components, such 

as turning vanes, are available.

Fasten The Cabinet To The Furnace

Align the cabinet with the return air opening. Place blocks 

under the cabinet, as necessary, to make sure the unit sits 

securely. Create an opening in the furnace to match the 

cabinet opening. Attach the cabinet securely to the furnace. 

Attach the unit directly or fit a starting collar in the furnace 

opening. Either drill holes and fasten with sheetmetal screws or 

rivets, or use slip joints. If you are drilling holes, use a locking 

pliers to help hold the unit in place during drilling.

Install Turning Vanes

Install turning vanes to help distribute air equally over the full 

surface of the upstream side of the media. Install them 

whenever an abrupt 90 degree elbow is installed directly 

against the media air cleaner cabinet.

Fasten Cabinet To Ductwork

Fasten side of cabinet to the ductwork using sheet-metal 

screws, rivets, or slip joints, as appropriate. 

Connect Ductwork

Connect the vertical duct section to the elbow. If the vertical 

drop of the duct is less than 7 in. (178 mm) from the side of the 

furnace, shorten the horizontal trunk or attach an offset fitting 

to the elbow. See Fig. 12. When ductwork is properly aligned, 

connect the vertical duct to the horizontal trunk.

Seal Joints

Seal all joints in the return air system between the media air 

filter and the furnace to prevent dust from entering the clean 

airstream.

Install Filter Cartridge

Slide the filter cartridge into the cabinet, making sure the arrow 

on the cartridge points in the direction of air flow.

Install battery in door. Replace access door. Insert the tab on 

the bottom of the door into the slot in the cabinet. Swing the 

door closed and press it into place.

Install RF AIRWATCH® Indicator

The AIRWATCH® Indicator provides a signal when the F200 

filter needs replacing. When the filter begins restricting airflow 

because of accumulated dirt, pressure sensors in the F200 

initiate a radio frequency signal to be sent to the AIRWATCH® 

Indicator. The AIRWATCH Indicator also has 12-month timers 

to indicate when the humidifier pad and the ultraviolet air 

treatment lamps need replacing.

Install Battery

1. Remove the AIRWATCH® Indicator from the base: 

a.   Depress the tab on the bottom edge of the base.

b.   Pull off the bottom of the front cover.

2. Install one CR123A Lithium Battery (provided) in the holder 

on the back of the unit.

3. Observe that the On/Battery LCD segment comes on.

M14794

LESS
THAN
7 in.
(178 mm)

OFFSET

AT LEAST
7 in.
(178 mm)

1

1   REQUIRED TURNING VANES HELP DISTRIBUTE AIRFLOW EVENLY.

Summary of Contents for F200

Page 1: ... cooling up to 5 tons Mounts in the return air duct Cabinet can support weight of residential furnace and evaporator coil Requires no electrical connections Mounts in any position Requires no maintenance except periodic battery and media filter replacement Quick and easy media filter replacement Later upgrade to electronic air cleaner is easy Integral pressure sensors signal when filter change is ...

Page 2: ... those con ditions are changed Model F200E Charged Media Air Cleaner includes a cabinet access door and pleated media filter and an RF AIRWATCH Indicator Application Use with gas oil and electric forced warm air furnaces and with compressor cooling Can be used with heat pumps if filter is changed regularly to prevent excessive pressure drop Efficiency Efficiency Ratings Based on American Society o...

Page 3: ...er press the reset button on the F200 door to reset both the door indicator light and the RF AIRWATCH Air Cleaner Indicator See Fig 2 See Table 1 for AIRWATCH operation Fig 2 RF transmitter door interior view M14784A F200E SIZE IN 16 X 25 16 X 20 20 X 25 20 X 20 MM 406 X 635 406 X 508 508 X 635 508 X 508 DIM A 14 7 16 14 7 16 18 7 16 18 7 16 367 367 468 468 DIM B 16 3 16 16 3 16 20 3 16 20 3 16 41...

Page 4: ...tor coil in a cooling system The filter will help to keep the coil clean and reduce maintenance Applications With A Humidifier The media air cleaner is compatible with humidifiers Avoid applications where water mist will reach the media If an atomizing humidifier is used the filter media will require replacement more often because of minerals in the water Choose Mounting Position The media air cle...

Page 5: ...ening in closet door Fig 7 Lowboy furnace with media air cleaner mounted horizontally in return plenum just above furnace and opposite heating plenum Fig 8 Counterflow furnace with media air cleaner mounted horizontally in return duct or plenum just above furnace Fig 9 Central fan installation with media air cleaner mounted horizontally in central return duct M941A M14788 M14789 M14790 ...

Page 6: ... Use gradual transitions to reduce air turbulence and increase efficiency See Fig 12 2 Use no more than 20 degrees about 4 in per running ft 100 mm per 300 linear mm of expansion on each side of a transition fitting Turning Vanes If the media air cleaner is installed next to an elbow or angle fitting add turning vanes inside the angle to distribute airflow more evenly across the face of the media ...

Page 7: ...ivets or use slip joints If you are drilling holes use a locking pliers to help hold the unit in place during drilling Install Turning Vanes Install turning vanes to help distribute air equally over the full surface of the upstream side of the media Install them whenever an abrupt 90 degree elbow is installed directly against the media air cleaner cabinet Fasten Cabinet To Ductwork Fasten side of ...

Page 8: ... AIRWATCH Indicator button until all four arrows come on about five seconds 3 Push the red reset button on the F200 door within two minutes 4 Observe the indicator arrows on the RF AIRWATCH begin to flash and continue for about two minutes until initialization is completed The AIRWATCH Indicator default setting is UV Light and Humidifier timers are disabled the Filter indicator is always enabled T...

Page 9: ... two seconds on six seconds off then two seconds on two seconds off Replace the batteries in both units Do not press any reset buttons after battery change Air Cleaner indicator flashing Signal was received from transmitter indicating either excessive pressure drop or 12 month timer has expired Replace filter and press reset button inside RF door See Fig 2 UV Air Treatment indicator flashing or Hu...

Page 10: ...LEANER U S Registered Trademark 2008 Honeywell International Inc 68 0238EF 03 M S Rev 06 08 Table 2 F200E Parts List Callout No Description F200E1003 16 x 20 in F200E1029 16 x 25 in F200E1011 20 x 20 in F200E1037 20 x 25 in 1 Replacement filter FC200E1003 FC200E1029 FC200E1011 FC200E1037 2 Door with RF Transmitter 32004876 002 32004876 002 32004876 001 32004876 001 3 AIRWATCH RF Receiver W8600B100...

Page 11: ...eurs de refroidissement allant jusqu à 5 tonnes S installe dans la gaine de reprise d air Le boîtier résistant peut recevoir le poids d un appareil de chauffage résidentiel et d un serpentin d évaporation Ne requiert aucun raccordement électrique S installe dans n importe quelle position N exige aucun entretien à l exception du remplacement périodique du filtre à fibres Remplacement simple et rapi...

Page 12: ...indicateur à radiofréquences AIRWATCHMC Application Convient aux appareils de chauffage à air pulsé au gaz au mazout et à l électricité et aux compresseurs de refroidissement Peut être utilisé dans un système à pompe à chaleur si le filtre est remplacé à intervalle régulier pour éviter une trop grande chute de pression Efficacité Efficacité établie d après la norme 52 2 1999 de l American Society ...

Page 13: ...e du F200 ainsi que sur celui de l indicateur mural à radiofréquences AIRWATCHMC Voir Fig 2 Voir le Tableau 1 pour savoir comment fonctionne l indicateur AIRWATCHMC Fig 2 Porte avec transmetteur RF vu de l intérieur M14784B F200E SIZE IN 16 X 25 16 X 20 20 X 25 20 X 20 MM 406 X 635 406 X 508 508 X 635 508 X 508 DIM A 14 7 16 14 7 16 18 7 16 18 7 16 367 367 468 468 DIM B 16 3 16 16 3 16 20 3 16 20 ...

Page 14: ... et permettra de réduire la fréquence de l entretien Applications humidificateur Le filtre à air convient aux systèmes avec humidificateurs Éviter les installations où l eau vaporisée peut atteindre le médium filtrant Dans le cas d une installation avec humidificateur atomiseur il faudra remplacer le médium filtrant plus souvent en raison des sédiments que contient l eau Choisir la position d inst...

Page 15: ...areil de chauffage à contre courant Filtre à air installé à l horizontale dans la gaine de reprise d air ou dans le plénum juste au dessus de l appareil de chauffage Fig 8 Appareil de ventilation centrale Filtre à air installé à l horizontale dans une gaine de reprise centrale Fig 9 Appareil de chauffage horizontal Le filtre à air est monté à la verticale à l endroit où entre l air repris près de ...

Page 16: ... et aug mentent l efficacité Voir la Fig 12 2 L expansion maximale doit être de 20 degrés environ 100 mm par 300 mm linéaires 4 po par pied linéaire de chaque côté du raccord de transition Déflecteurs Si le filtre à air est installé près d un coude raccord à angle installer les déflecteurs à l intérieur du coude pour assurer une distribution d air plus uniforme à la surface du filtre Voir la Fig 1...

Page 17: ...ier du filtre à air Fixer solidement le boîtier à l appareil de chauffage soit directement voir illustration soit à l aide d un collier de démarrage dans l appareil de chauffage Percer des trous et fixer l appareil à l aide de rivets ou de vis pour tôle ou utiliser des écrous coulissants S il faut percer des trous utiliser une pince étau pour maintenir l appareil en place pendant cette opération I...

Page 18: ... de l indicateur AIRWATCHMC s harmonise à la plus récente gamme de thermostats programmables de luxe ChronothermMC IV de Honeywell L appareil peut aussi être installé à tout autre endroit pratique dans la maison ou près de l appareil de chauffage Voir la Fig 15 Fig 15 Choix d un emplacement 1 Choisir l emplacement voulu à au moins 6 pieds de la porte du transmetteur dans la porte 2 Vérifier la com...

Page 19: ... aucun bouton de réarmement après le remplacement de la pile Deux secondes allumée deux secondes éteinte remplacer la pile de l indicateur AIRWATCHMC N appuyer sur aucun bouton de réarmement après le remplacement de la pile Le clignotement alterne et passe de deux secondes allumée six secondes éteinte à deux secondes allumée deux secondes éteinte remplacer les piles des deux appareils N appuyer su...

Page 20: ...commerce déposée aux É U 2008 Honeywell International Inc Tous droits réservés 68 0238EF 03 M S Rev 06 08 Tableau 2 Liste des pièces du F200 NO Description F200E1003 16 x 20 en po F200E1029 16 x 25 en po F200E1011 20 x 20 en po F200E1037 20 x 25 en po 1 Filtre de recharge FC200E1003 FC200E1029 FC200E1011 FC200E1037 2 Porte avec transmetteur RF 32004876 002 32004876 002 32004876 001 32004876 001 3 ...

Reviews: