background image

F220 Series | 

Installation Instructions | 7.0 

Maintenance

 

EN 

| 11 

 

 

Bosch Security Systems | 8/05 | 4998138694D 

 

7.0 Maintenance 

 

Notify all concerned parties before any 
maintenance or testing of the fire alarm 
system, and after completion of these 
activities. 

 

At least once a year vacuum or clean/dry the 
external part of the detector with compressed air. 
Pay particular attention to the screens in dusty 
areas or heavy insect activity. 

 

To clean the chamber, use a can of clean 
compressed air. Place the tube or needle valve 
through the ChamberMaid valve in the bottom of 
the detector (see 

Figure 1

, #5). 

 

Shorten the plastic tube that comes with 
the compressed air to about 2 in (5 cm). 
The compressed air (such as 
TECHSPRAY

®

 ENVI-RO-TECH™ 

DUSTER) is available at office and alarm 
supply stores. 

 

Do not paint the detectors. Paint or other foreign 
matter covering the thermistor or LED can 
prohibit detection. 

8.0 Periodic 

testing 

Keeping the detector calibrated is necessary for proper 
operation. Depending on local regulations, calibration 
testing can be required more than once a year. NFPA 
72 recommends performing calibration tests at 
installation, then every other year. Perform functional 
testing yearly. 

 

Notify all concerned parties before any 
maintenance or testing of the fire alarm 
system, and upon completion of these 
activities. 

Test the calibration (to meet NFPA) using either the 
magnet test or measuring the calibration with a 
calibrated product from No Climb Products Ltd. 
Quickly determine the calibration by a visual 
inspection of the detector’s LED (see

 Section 9.0 Visual 

check

). These tests confirm whether or not the detector 

is within its factory marked calibration range. 

9.0 Visual 

check 

These detectors includes the Chamber Check 
Automatic Trouble Indicator, which verifies that the 
detector’s calibration is within the factory listed range. 
You can meet the NFPA guidelines for sensitivity 
testing by visually inspecting the detector and checking 
the flash rate of the LED. If the calibration is out of 
range for more than 24 hours, the green LED on the 
detector begins to flash approximately once every four 
seconds. The LED flashes approximately once every 
eight seconds when the detector operates normally. 

 

Perform the visual check before resetting 
power. After a reset the trouble indicators 
clear for 70 seconds. After 70 seconds, if 
the detector is in a trouble condition, 
trouble indications begin again  

 

Summary of Contents for F220

Page 1: ...EN Installation Instructions Photoelectric Smoke Heat Detectors F220 Series ...

Page 2: ...open area photoelectric smoke detectors that work with commercial fire protective signaling systems and household fire warning systems Select the appropriate mounting base to configure the detectors for two wire or four wire versions For commercial and industrial installations 30 ft 9 14 m spacing between detectors is recommended To verify power to the detector and a functioning smoke sampling cir...

Page 3: ...nce of false alarm greatly increased 15 0 5 ft 0 5 0 3 m false alarm very likely 1 6 1 The LED sensitivity flash procedure 1 Briefly place the magnet at the T on the detector base for at least one red LED flash but less then three LED flashes 2 Wait for the first single green LED flash 3 Count the number of red LED flashes that follow This indicates the sensitivity 1 6 2 Normal sensitivity LED fla...

Page 4: ...our wire system 2 0 Product family description Table 3 Product Family Description F220 P Photoelectric smoke detector only requires base F220 PTH Photoelectric smoke detector w integral 135 F 57 C heat sensor requires base F220 PTHC Photoelectric smoke detector w integral 135 F 57 C heat sensor and CO enhanced smoke detection requires base F220 PC Photoelectric smoke detector with CO enhanced smok...

Page 5: ...ten Depending on local regulations you can surface mount the bases using anchors mollies or wing nuts or you can mount directly to 4 in 10 cm octagonal electrical boxes and single gang switch boxes The electrical box must be large enough to accommodate the number and size of conductors specified by the National Electrical Code or any local Authorities Having Jurisdiction AHJ 4 0 Wiring information...

Page 6: ...erted as individual ends EOL Resistors Use the EOL resistors supplied or specified by the control panel manufacturer This also applies to the D275 Module D275 Power Supervision Relay When used with 12 VDC systems connect the red wire to Terminal b1 on the last base in the run The yellow wire remains unconnected For 24 VDC systems connect the yellow wire to Terminal b1 The red wire remains unconnec...

Page 7: ...arm Relay Form A C Terminal 4 Alarm Relay Form A NO Terminal 5 Figure 7 F220 B6C auxiliary alarm contact wiring 1 2 3 1 2 NC C NO NO C 1 Alarm NO 2 Auxiliary alarm relay 4 5 Wiring the F220 B6E The F220 B6E base has a normally open alarm loop relay and an auxiliary set of normally open contacts The contacts are rated 0 5 A use at 125 VAC and 1 0 A use at 30 VDC for resistive loads Do not use with ...

Page 8: ...instructions 2 Attach the base skirt by aligning the four hardware keys or turn the base skirt slowly clockwise until it rests in place Press firmly to latch it onto the fixing clamps See Figure 10 Use the tamper tab locking bar to prohibit detector removal as follows 3 The snap off locking bar X is part of the base molding Shift the locking bar X into the position shown in Figure 9 to engage it 4...

Page 9: ...March Time signal Positions 3 and 4 off Steady signal Figure 12 F220 B6RS 4 wire configuration with D275 tandem connection NO C INT b1 b2 c a1 a2 NO C INT b2 c a1 a2 NO C INT b2 c a1 a2 1 2 3 3 4 5 1 2 1 2 1 2 3 3 3 SEP SEP SEP SEP SEP SEP 6 7 b1 b1 8 8 8 1 D275 2 Alarm loop Terminal 1 and 2 3 Blue wire D275 Terminal 1 and EOLR 4 Black wire D275 Common 5 Yellow wire D275 for 24 V systems 6 Red wir...

Page 10: ... second rate the detector is either cold out of sensitivity range or defective If the smoke detector LED flashes at a four second rate the detector is out of sensitivity range or defective 12 Test each detector to ensure it causes a control panel alarm Reset the control panel after each test To alarm the F220 135 135F 190F Detectors either Place a magnet horizontally against the T and hold it ther...

Page 11: ...tion tests at installation then every other year Perform functional testing yearly Notify all concerned parties before any maintenance or testing of the fire alarm system and upon completion of these activities Test the calibration to meet NFPA using either the magnet test or measuring the calibration with a calibrated product from No Climb Products Ltd Quickly determine the calibration by a visua...

Page 12: ... Time 22 second maximum Alarm current for all F220 Detectors 20 mA minimum use at 8 5 VDC 35 mA maximum use at 32 VDC F220 B6 2 wire 8 5 to 32 0 VDC F220 B6 R C E RS 4 wire 10 0 to 30 0 VDC Alarm Current only base current head current excluded F220 B6C 31 mA use at 12 VDC 35 mA use at 24 VDC 40 mA maximum use at 30 VDC F220 B6R 13 5 mA use at 12 VDC 16 5 mA use at 24 VDC 19 mA maximum use at 30 VD...

Page 13: ... 13 Bosch Security Systems 8 05 4998138694D Trademarks CleanMe is a trademark of GE Interlogix ChamberMaid and Chamber Check are a trademarks of Bosch Security Systems TECHSPRAY is a registered trademark and ENVI RO TECH is a trademark of Tech Spray L P ...

Page 14: ...F220 Series Installation Instructions Notes EN 14 Bosch Security Systems 8 05 4998138694D Notes ...

Page 15: ...F220 Series Installation Instructions Notes EN 15 Bosch Security Systems 8 05 4998138694D Notes ...

Page 16: ... 2005 Bosch Security Systems 4998138694D Bosch Security Systems 130 Perinton Parkway Fairport NY 14450 9199 Customer Service 800 289 0096 Technical Support 888 886 6189 ...

Reviews: