background image

F220 Series | 

Installation Instructions | 6.0 

Testing the installation

 

EN 

| 10 

 

 

Bosch Security Systems | 8/05 | 4998138694D 

 

 

Table 10: Interconnected Units (five units total) 

Maximum Wire Length  

Wire size 

Wire length 

18 AWG (1.2 mm) 

300 ft (91 m) 

16 AWG (1.5 mm) 

450 ft (137 m) 

14 AWG (1.8 mm) 

750 ft (229 m) 

 

 

 

 

Up to five interconnected units activate per 
circuit. If more than five units activate, only 
individual detectors are guaranteed to 
activate the correct output pattern. Tandem 
units cannot activate the correct output 
pattern. 

6.0 Testing 

the 

installation 

1.

 

Check the wiring from the control panel to the last 
head on each run for proper polarity and 
continuity. 

2.

 

Make sure each run terminates with an EOL 
resistor as specified by the control panel 
manufacturer. 

3.

 

Make sure four-wire runs terminate at EOL 
Modules or F220-B6E bases. 

4.

 

Apply power to the system. Check for alarms and 
troubles. 

5.

 

Note which detectors alarmed (if any), and shut 
down the system.  

6.

 

Remove these detectors from their bases and 
recheck the bases for proper wiring.  

7.

 

If the problem persists, determine if the problem is 
caused by the detector or the base.  

8.

 

Replace the affected detectors or swap them with 
known good units. 

9.

 

If a system alarm occurs with no detector alarms 
present, remove all detectors and check the wiring 
at each base.  

10.

 

Closely check the wiring of each EOL resistor and 
EOL module. 

11.

 

When the system is alarm free, check each detector 
to ensure that the green LED indicator flashes 
approximately every eight seconds. This verifies 
the detector is receiving power and operating 
properly. 

 

 

If the heat detector LED flashes at a four 
second rate, the detector is either cold, out 
of sensitivity range, or defective. If the 
smoke detector LED flashes at a four 
second rate the detector is out of 
sensitivity range or defective. 

12.

 

Test each detector to ensure it causes a control 
panel alarm. Reset the control panel after each test. 

To alarm the F220-135/135F/190F Detectors either: 

 

Place a magnet horizontally against the “T” and 
hold it there for three consecutive LED flashes (see 

Figure 1, #4

). This activates an internal reed switch 

thereby sending an alarm signal. 

or 

 

Expose the thermistor (see 

Figure 1, #3

) to a heat 

source such as a hair dryer or a shielded heat 
lamp. Expose the thermistor until the detector 
alarms and the alarm LED lights. 

To alarm the F220-P/PTH/PC/PTHC Detectors either: 
1.

 

Place a magnet horizontally against the “T” and 
hold it there for three consecutive LED flashes (see 

Figure 1, #4

). This activates an internal reed switch 

thereby sending an alarm signal. 
or 

Use a UL Listed aerosol smoke detector tester to 
simulate an alarm. Follow the instructions provided 
with the aerosol smoke detector tester. 

 

When a detector alarms, the red LED 
indicator activates and latches into the ON 
position. Clear the alarm before proceeding 
to the next detector. 

2.

 

Reset the detector by momentarily removing 
power. 

3.

 

Check the load on the alarm loop by measuring 
the voltage across each EOL resistor. This voltage 
should equal or exceed the minimum specified by 
the control panel manufacturer. 

6.1 

CO detector testing 

Removing the detector or resetting the detector’s 
power places the detector in a special test mode for the 
next 15 minutes. If over 35 ppm of CO is applied to 
the detector within this 15-minute period, the detector 
alarms. 

 

The F220PC and F220PTHC detect CO 
as a component of a fire. Do not use the 
F220PC and F220PTHC as CO detectors. 

Summary of Contents for F220

Page 1: ...EN Installation Instructions Photoelectric Smoke Heat Detectors F220 Series ...

Page 2: ...open area photoelectric smoke detectors that work with commercial fire protective signaling systems and household fire warning systems Select the appropriate mounting base to configure the detectors for two wire or four wire versions For commercial and industrial installations 30 ft 9 14 m spacing between detectors is recommended To verify power to the detector and a functioning smoke sampling cir...

Page 3: ...nce of false alarm greatly increased 15 0 5 ft 0 5 0 3 m false alarm very likely 1 6 1 The LED sensitivity flash procedure 1 Briefly place the magnet at the T on the detector base for at least one red LED flash but less then three LED flashes 2 Wait for the first single green LED flash 3 Count the number of red LED flashes that follow This indicates the sensitivity 1 6 2 Normal sensitivity LED fla...

Page 4: ...our wire system 2 0 Product family description Table 3 Product Family Description F220 P Photoelectric smoke detector only requires base F220 PTH Photoelectric smoke detector w integral 135 F 57 C heat sensor requires base F220 PTHC Photoelectric smoke detector w integral 135 F 57 C heat sensor and CO enhanced smoke detection requires base F220 PC Photoelectric smoke detector with CO enhanced smok...

Page 5: ...ten Depending on local regulations you can surface mount the bases using anchors mollies or wing nuts or you can mount directly to 4 in 10 cm octagonal electrical boxes and single gang switch boxes The electrical box must be large enough to accommodate the number and size of conductors specified by the National Electrical Code or any local Authorities Having Jurisdiction AHJ 4 0 Wiring information...

Page 6: ...erted as individual ends EOL Resistors Use the EOL resistors supplied or specified by the control panel manufacturer This also applies to the D275 Module D275 Power Supervision Relay When used with 12 VDC systems connect the red wire to Terminal b1 on the last base in the run The yellow wire remains unconnected For 24 VDC systems connect the yellow wire to Terminal b1 The red wire remains unconnec...

Page 7: ...arm Relay Form A C Terminal 4 Alarm Relay Form A NO Terminal 5 Figure 7 F220 B6C auxiliary alarm contact wiring 1 2 3 1 2 NC C NO NO C 1 Alarm NO 2 Auxiliary alarm relay 4 5 Wiring the F220 B6E The F220 B6E base has a normally open alarm loop relay and an auxiliary set of normally open contacts The contacts are rated 0 5 A use at 125 VAC and 1 0 A use at 30 VDC for resistive loads Do not use with ...

Page 8: ...instructions 2 Attach the base skirt by aligning the four hardware keys or turn the base skirt slowly clockwise until it rests in place Press firmly to latch it onto the fixing clamps See Figure 10 Use the tamper tab locking bar to prohibit detector removal as follows 3 The snap off locking bar X is part of the base molding Shift the locking bar X into the position shown in Figure 9 to engage it 4...

Page 9: ...March Time signal Positions 3 and 4 off Steady signal Figure 12 F220 B6RS 4 wire configuration with D275 tandem connection NO C INT b1 b2 c a1 a2 NO C INT b2 c a1 a2 NO C INT b2 c a1 a2 1 2 3 3 4 5 1 2 1 2 1 2 3 3 3 SEP SEP SEP SEP SEP SEP 6 7 b1 b1 8 8 8 1 D275 2 Alarm loop Terminal 1 and 2 3 Blue wire D275 Terminal 1 and EOLR 4 Black wire D275 Common 5 Yellow wire D275 for 24 V systems 6 Red wir...

Page 10: ... second rate the detector is either cold out of sensitivity range or defective If the smoke detector LED flashes at a four second rate the detector is out of sensitivity range or defective 12 Test each detector to ensure it causes a control panel alarm Reset the control panel after each test To alarm the F220 135 135F 190F Detectors either Place a magnet horizontally against the T and hold it ther...

Page 11: ...tion tests at installation then every other year Perform functional testing yearly Notify all concerned parties before any maintenance or testing of the fire alarm system and upon completion of these activities Test the calibration to meet NFPA using either the magnet test or measuring the calibration with a calibrated product from No Climb Products Ltd Quickly determine the calibration by a visua...

Page 12: ... Time 22 second maximum Alarm current for all F220 Detectors 20 mA minimum use at 8 5 VDC 35 mA maximum use at 32 VDC F220 B6 2 wire 8 5 to 32 0 VDC F220 B6 R C E RS 4 wire 10 0 to 30 0 VDC Alarm Current only base current head current excluded F220 B6C 31 mA use at 12 VDC 35 mA use at 24 VDC 40 mA maximum use at 30 VDC F220 B6R 13 5 mA use at 12 VDC 16 5 mA use at 24 VDC 19 mA maximum use at 30 VD...

Page 13: ... 13 Bosch Security Systems 8 05 4998138694D Trademarks CleanMe is a trademark of GE Interlogix ChamberMaid and Chamber Check are a trademarks of Bosch Security Systems TECHSPRAY is a registered trademark and ENVI RO TECH is a trademark of Tech Spray L P ...

Page 14: ...F220 Series Installation Instructions Notes EN 14 Bosch Security Systems 8 05 4998138694D Notes ...

Page 15: ...F220 Series Installation Instructions Notes EN 15 Bosch Security Systems 8 05 4998138694D Notes ...

Page 16: ... 2005 Bosch Security Systems 4998138694D Bosch Security Systems 130 Perinton Parkway Fairport NY 14450 9199 Customer Service 800 289 0096 Technical Support 888 886 6189 ...

Reviews: