17
xtra
-
Installation & Servicing
INSTALLATION
19 INDEPENDENT SYSTEM CONTROLS
If the system controls are to be independent of the boiler, then the following method should be used for connecting the boiler.
No parameter modifications are required.
Frost Stat if required*
230 VAC
Permanent
mains supply
Switched live (230 VAC)
from external controls
generating call for heat*
System pump
(maximum load 1 amp)
connect via a relay for
greater currents
CH
CALL
SEQUENCE SUPPLY
DHW PUMP OR VALVE
N
L
N
L
CH PUMP
N
L
MAINS IN
N
L
DHW
CALL
im8187
* The switched live from external
controls must be from the same
phase supply as the boiler mains
supply to ensure that when the
boiler supply is switched off the
controls are also isolated.
20 MAINS VOLTAGE CH AND DHW CONTROLS WITH DHW PUMP OUTPUT
No parameter
modifications are
required.
Alternatives
: The Ideal
programmable room
thermostat, outside
sensor and tank sensor kit
provides enhanced user
comfort. Full instructions
provided with kits.
Pump
Pump
Non return
valve
Non return
valve
Cylinder
thermostat
Programmer
Room
stat
im8191
* The switched live from external controls must be from the same phase supply as the boiler
mains supply to ensure that when the boiler supply is switched off the controls are also isolated.
230 VAC
Permanent
mains supply
If either pump requires more than
1 amp supply current, connection
must be made via a relay
Room
stat
Cyl
stat
DHW
CH
External 230 VAC
Programmer *
CH
CALL
SEQUENCE SUPPLY
DHW PUMP OR VALVE
N
L
N
L
N
L
CH PUMP
N
L
MAINS IN
N
L
DHW
CALL
im8192
D H W
This system provides heating to one zone at a time with DHW
priority controlled by parameter 43. To heat more than one zone
simultaneously, use zone thermostats to energise individual
zone valves with all calls for heat applied to 'CH CALL'. The
boiler will be limited to responding with a set flow temperature
set by parameter 4.
If all zones are fitted with individual zone valves a hydraulic
bypass will be required to allow pump overrun. See page
5 and 6 for details.