GEM F687 Скачать руководство пользователя страница 4

GENERAL TECHNICAL DATA

Sprinkler Assemblies:

The 5.8 K-factor, Model F687 Residen-
tial Horizontal Sidewall Sprinklers are
available in a 155°F/68°C temperature
rating and they are rated for use at a
maximum service pressure of 175 psi.
They are available chrome plated,
natural brass, or polyester coated in
any color.

The nominal flow “Q” in GPM (LPM) is
determined by the following formula:

Q = K (p

1/2

)

where the nominal sprinkler discharge
coefficient “K” equals 5.8 (83,5) and “p”
equals residual pressure in psi (bar).

The F687 utilizes a 3 mm Bulb with a
cast dezincification resistant bronze
alloy Frame. The two pieces of the But-
ton Assembly are constructed from
brass per ASTM B16 (C36000) and
copper (C12200). The Gasketed
Spring Plate consists of a Beryllium
Nickel (N03360) disc spring  that is
sealed on both its inside and outside
edges with a Teflon

†

gasket. The Com-

pression Screw is a brass per ASTM
B16 (C36000), and the Deflector is
brass per ASTM B36 (C22000).

Escutcheon Plates:

A separately ordered escutcheon plate
is required for concealed piping instal-
lations.

Figure B-1 illustrates a typical installa-
tion of an F687 Sprinkler using a
standard one-piece escutcheon plate
like that described in Technical Data
Sheet TD805. Refer to Technical Data
Sheet TD805 for information on other
available flush mount escutcheons.

Figure B-2 illustrates the Model F705
Recessed Escutcheon which is the
only recessed escutcheon that is ac-
ceptable for use with the Model F687
Horizontal Sidewall Sprinkler. It has a
Closure and Mounting Plate fabricated
from low carbon steel. The Mounting
Plate prongs, which are compressed
back into the Mounting Plate as the
Closure is pushed over it, maintain a
tight friction fit between the two pieces.
The Mounting Plate and Closure can
also swivel relative to each other and
compensate for minor non-perpen-
dicularity between the Model F687
Sprinkler and the wall.

The F705 Escutcheons are available
with a chrome plated finish or a coated
finish in any color.

NOTES

Absence of an escutcheon may de-

lay the time to sprinkler opera-

tion in a fire situation.

Only use escutcheons which con-

sist of metallic materials that

will not deform or dislodge at a

temperature

of

less

than

1200°F/649°C and/or which have

been listed by Underwriters Labo-

ratories Inc. for fire protection

service.

The escutcheon plates like those

shown in Technical Data Sheet

TD805, as well as the F705 Es-

cutcheon, cannot be used to hold

the F687 in position. The F687

must be secured in position by

firmly fastening the sprinkler sys-

tem piping to the dwelling struc-

ture. If the F687 is not properly

secured in position, reaction

forces resulting from sprinkler

operation could alter its orienta-

tion and water distribution pat-

tern.

RESIDENTIAL DESIGN CRITERIA

The 5.8

K-factor, Model F687 Resi-

dential Horizontal and Recessed Hori-
zontal Sidewall Sprinklers must only
be installed and utilized in accordance
with the following described criteria
which are provided by the manufac-
turer.

NOTES

1. Residential Fire Sprinkler Sys-

tems should only be designed

and installed by those compe-

tent and completely familiar

with automatic sprinkler sys-

tem design, installation pro-

cedures, and techniques.

2. Several criteria may apply to

the installation and usage of

each sprinkler. Consequently,

it is recommended that the

sprinkler system designer re-

view and develop a working un-

derstanding of the complete

list of criteria, prior to initiat-

ing the design of the sprinkler

system.

3. Questions concerning sprink-

ler installation and usage cri-

teria, which are not covered by

the following instructions,

should be mailed to the atten-

tion of the Technical Data De-

partment. Include sketches

and technical details, as ap-

propriate.

4. In some instances, the require-

ments of this document may

concern specifications which

are more stringent and which

take precedence over those

specified in NFPA 13, NFPA

13D, NFPA 13R, or by the

authority having jurisdiction.

General Service Conditions.

The

F687 Sprinklers must only be utilized
in wet pipe sprinkler systems with all
interconnecting system piping as well
as the sprinklers maintained at a mini-
mum temperature of 40°F/4°C, and
with water supplies which are substan-
tially free of contaminants and parti-
cles of a size greater than 1/8 inch (3,2
mm).

Hydraulic Design Criteria.

The mini-

mum required flow rates for residential
applications are given in Table A as a
function of the maximum allowable
coverage areas. The NFPA 13D/13R
single sprinkler flow rate is the mini-
mum required discharge from the most
hydraulically demanding single sprin-
kler and the NFPA 13D/13R multiple
sprinkler flow rate is the minimum re-
quired discharge from each of the total
number of “design sprinklers” as speci-
fied in NFPA 13D or 13R.

TIA 99-1 (Tentative Interim Amend-
ment) with an effective date of May 22,
2000 states

that the minimum re-

quired discharge from each of the “de-
sign sprinklers” for systems designed
to NFPA 13 must be calculated based
on delivering a minimum design den-
sity of 0.1 gpm/sq. ft. for each of the
listed coverage areas shown in Table
A. Consult with the Authority Having
Jurisdiction regarding the application
of  this TIA to  the currently adopted
NFPA 13.

NOTE

The number of sprinklers within

each compartment (as defined by

NFPA 13, 13D, or 13R), must be

kept as few as possible. Do NOT

use more sprinklers than neces-

sary to cover a particular space.

Spray Coverage Criteria.

Each F687

Sprinkler must only be used in accord-
ance with one of the designated width
by  length  (W x L)  coverage  criteria
specified in Table A.

Ceiling mounted obstructions such as
heating or air conditioning diffusers,
overhangs, and light fixtures must be
located above an elevation, as shown
in Figure C, where they will not inter-
fere with the proper distribution of
water by the sprinkler.

F687 Sprinklers may be installed along
overhangs or soffits that are a maxi-
mum of 8 inches wide (distance from
wall); with a maximum vertical dis-
tance of 4 inches from the centerline of
the sprinkler waterway to the bottom of
the overhang/soffit; and, with a de-
flector-to-soffit

surface distance of

—4—

†

DuPont Registered Trademark

OBSOLETE

Содержание F687

Страница 1: ...application of a fin ish coat to the wall They also permit refinishing of a wall surface without having to first shut down the fire pro tection system and remove the sprin klers They are designed for...

Страница 2: ...rtment designs which cannot be fully sprinklered in accordance with the recommendations of NFPA 13 13D or 13R In the event of this condition consult the authorities having jurisdiction for guidance an...

Страница 3: ...SED DIMENSIONS Up to 1 4 inch adjustment from minimum 1 4 inch to maximum 1 2 inch recessed position HIGH ADJUSTMENT DIMENSIONS Up to 1 2 inch adjustment from the flush sidewall position to 1 2 inch r...

Страница 4: ...ac turer NOTES 1 Residential Fire Sprinkler Sys tems should only be designed and installed by those compe tent and completely familiar with automatic sprinkler sys tem design installation pro cedures...

Страница 5: ...TE Where utilized beams joists or ducts must be located with their centerlines along the boundaries separating adjacent sprinkler coverage areas It is recommended that as part of the sprinkler system...

Страница 6: ...ensate for the possible manufac turing variations in the take out of the fitting as well as in the make in of the sprinklers as permitted by ANSI B1 20 1 3 After installing the F705 Mounting Plate or...

Страница 7: ...the heat responsive element Bulb can result Do NOT cleanse the sprinklers with soap and water detergents ammonia cleaning fluids or other chemicals Remove dust lint cobwebs cocoons insects and larvae...

Страница 8: ...inish PSN specify Chrome Plated Finish 155F 68C PSN 51 687 9 155 Natural Brass Finish 155F 68C PSN 51 687 1 155 White Polyester Finish 155F 68C PSN 51 687 4 155 Recessed Escutcheon Specify 1 2 15 mm M...

Отзывы: