GEM F687 Скачать руководство пользователя страница 2

ated with  the F687 Sprinklers have
been proven to help in the control of
residential type fires and, therefore, to
improve the chance for occupants to
escape or be evacuated.

Fire sprinkler systems are not a substi-
tute for intelligent fire  safety aware-
ness or construction materials and
practices required by building codes.

APPROVALS AND STANDARDS

The 5.8 K-factor, Model F687 Residen-
tial Horizontal and Recessed Horizon-
tal Sidewall Sprinklers are listed by
Underwriters Laboratories Inc. and
Underwriters’ Laboratories of Canada.
The listings only apply to the sprinkler
finishes and service conditions indi-
cated in the General Technical Data
and Residential Design Criteria sec-
tions.

The 5.8 K-factor, Model F687 Residen-
tial Horizontal and Recessed Horizon-
tal Sidewall Sprinklers are  also  ap-
proved by the Scientific Ser vices

Laboratory (Australia), as well as ac-
cepted by the City of New York under
MEA 39-92-M.

Any questions concerning an interpre-
tation of NFPA 13, 13D, or 13R sprin-
kler system design/installation stand-
ards, as well as requests for system
design/installation standards not pres-
ently covered by NFPA 13,  13D, or
13R, should be addressed to the:

Secretary, Standards Council
National Fire Protection Association
Batterymarch Park
Quincy, MA 02269

WARNINGS

The Model F687 Residential Hori-

zontal and Recessed Horizontal

Sidewall Sprinklers described

herein must be installed and

maintained in compliance with

this document, as well as with the

applicable standards of the Na-

tional Fire Protection Associa-

tion, in addition to the standards

of any other authorities having

jurisdiction. Failure to do so may

impair the integrity of these de-

vices.

Because of the above cited stipu-

lations and the varied nature of

residential type architecture,

there may be some compartment

designs which cannot be fully

sprinklered in accordance with

the recommendations of NFPA 13,

13D, or 13R. In the event of this

condition, consult the authorities

having jurisdiction for guidance

and approval.

It is the responsibility of an in-

stalling contractor to provide a

copy of this document to the

owner or his representative and,

in turn, it is the obligation of the

owner to provide a copy of this

document to a succeeding owner.

The owner is responsible for

maintaining their fire protection

system and devices in proper op-

erating condition. The installing

contractor or sprinkler manufac-

turer should be contacted relative

to any questions.

—2—

NFPA 13D/13R

NFPA 13D/13R

MINIMUM

MINIMUM

SINGLE

MULTIPLE

SPRINKLER

(d)

SPRINKLER

(d)

W x  L

(b)

FLOW

FLOW

A

B

APPLICATION

FT x FT

GPM (psi)

(c)

GPM (psi)

(c)

INCHES

FEET

RES

(a)

12 x 12

18 (9.6)

15.3 (7.0)

4 to 12

(f)

6

RES

(a)

16 x 18

28 (23.3)

23 (15.7)

4 to 6

(e)

8

RES

(a)

16 x 20

29 (25.0)

26 (20.1)

4 to 6

(e)

8

NOTES:

(a) Wet pipe fire sprinkler systems in the residential portions of any occupancy per NFPA 13, in one- and two- family dwellings and mobile

homes per NFPA 13D, or residential occupancies per NFPA 13R.

(b) For coverage area dimensions less than or between those indicated, it is necessary to use the minimum required flow for the next highest

coverage area for which hydraulic design criteria are stated.

(c) Requirement is based on minimum flow in GPM from each sprinkler. The indicated residual pressures are based on the nominal K-factor.

(d) Refer to Hydraulic Design Criteria under Residential Design Criteria Section for details.

(e) To meet this requirement, the centerline of the waterway (Ref. Fig. A) must be installed between 4-3/8 and 6-3/8 inches below the ceiling.

(f) To meet this requirement, the centerline of the waterway (Ref. Fig. A) must be installed between 4-3/8 and 12-3/8 inches below the ceiling.

TABLE A

HYDRAULIC DESIGN CRITERIA FOR THE 5.8 K-FACTOR MODEL F687 RESIDENTIAL HORIZONTAL

AND RECESSED HORIZONTAL SIDEWALL SPRINKLERS

OBSOLETE

Содержание F687

Страница 1: ...application of a fin ish coat to the wall They also permit refinishing of a wall surface without having to first shut down the fire pro tection system and remove the sprin klers They are designed for...

Страница 2: ...rtment designs which cannot be fully sprinklered in accordance with the recommendations of NFPA 13 13D or 13R In the event of this condition consult the authorities having jurisdiction for guidance an...

Страница 3: ...SED DIMENSIONS Up to 1 4 inch adjustment from minimum 1 4 inch to maximum 1 2 inch recessed position HIGH ADJUSTMENT DIMENSIONS Up to 1 2 inch adjustment from the flush sidewall position to 1 2 inch r...

Страница 4: ...ac turer NOTES 1 Residential Fire Sprinkler Sys tems should only be designed and installed by those compe tent and completely familiar with automatic sprinkler sys tem design installation pro cedures...

Страница 5: ...TE Where utilized beams joists or ducts must be located with their centerlines along the boundaries separating adjacent sprinkler coverage areas It is recommended that as part of the sprinkler system...

Страница 6: ...ensate for the possible manufac turing variations in the take out of the fitting as well as in the make in of the sprinklers as permitted by ANSI B1 20 1 3 After installing the F705 Mounting Plate or...

Страница 7: ...the heat responsive element Bulb can result Do NOT cleanse the sprinklers with soap and water detergents ammonia cleaning fluids or other chemicals Remove dust lint cobwebs cocoons insects and larvae...

Страница 8: ...inish PSN specify Chrome Plated Finish 155F 68C PSN 51 687 9 155 Natural Brass Finish 155F 68C PSN 51 687 1 155 White Polyester Finish 155F 68C PSN 51 687 4 155 Recessed Escutcheon Specify 1 2 15 mm M...