About grounding the platform
You must ground the platform after you install it in a rack. The chassis ground lug is located on the back
of the platform.
Do not secure multiple bonding or grounding connectors with the same bolt. The grounding connectors
do not need to be removed to perform service or installation procedures. You can connect other bonding
or grounding conductors to a grounding connector provided a reliable bond between the connector and
the equipment is not disturbed during installation, service, or maintenance of the platform.
Important: All grounding cable terminal lugs must meet appropriate safety standards.
Note: The platform must be grounded to a common bonding network (CBN).
Figure 10: Chassis ground lug
Connect the ground lug to the ground terminal
You must provide these components to properly ground the chassis:
• Crimping tool
• Single ring ground terminal lug
• One 12 AWG copper wire long enough to reach from the chassis to the common bonding network
(CBN)
After the unit is installed in the rack and before you provide power to the system, you need to connect the
grounding hardware.