EJL-136F
10
Figure 9. Separate type converter LF622 and LF622F
External Connections
Combined type LF410/LF620 and LF414/LF620F flowmeters
Grounding with 100
Ω
or less
ground resistance
Instrument panel : Ordered separately
I/O cable
Ⅳ
wire 5.5mm
2
or more
Current output (4
~
20mAdc)
or PROFIBUS
Power supply
Power cable
Digital input
(20
~
30Vdc)
Signal common for DI and DO
Digital output 1
Digital output 2
Grounding with 100
Ω
or less
ground resistance
or Modbus
Power switch
(External double-pole power switch)
NOTE:
In the case of the integral type, the signal line
( A, B, G ) and the excitation line ( E, X, Y ) are
the connector joints.
Grounding with 100
Ω
or less
ground resistance
*1 Locate an external double-pole power switch on the power line near the flowmeter within easy reach of operation.
Use the appropriate switch rating as shown below:
Switch rating: 250Vac, 6A or more
In rush current: 15A or more
Figure 10. Combined type LF410/LF620 and LF414/LF620F flowmeters Wiring Diagram
Unit : inch(mm)
Weight: Approx. 7 lb (3.5 kg)
Note: Cable glands are not provided for LF622F cFMus approved type.
Refer to the part Cable connection port at detector.
Note: 1 inch = 25.4mm
LCD display
Attachment
I/O cable ground
Excitation cable ground
Power supply
cable ground
Option cable ground
Signal cable ground
IR Switch
Plate