Item
Controller
Drive tray
Input voltage (operable
voltage range) (V)
AC 200-240 +6%/-11%
FMD tray: AC 200-240
+6%/-11%
Frequency (Hz)
50/60 ±1
Number of phases, cabling Single-phase with protective grounding
Steady-state current 100V/
200V
1
,
2
CBL: 4.0x2
FMD tray: 2.6x2/1.3x2
Current rating of breaker/
fuse (A)
16.0 (each electrical)
Heat value (normal) (kJ/h)
CBL: 2810 or less
FMD tray: 1520 or less
Steady-state power (VA/W)
3
CBL: 1600/1560 or less
FMD tray: 520/490 or less
Power consumption (VA/W) CBL: 840/780 or less
FMD tray: 440/420 or less
Notes:
1. The power current of Nx2 described in this table is required for a single power
unit.
2. If one power unit fails, another power unit requires electric current for the two
power units. Therefore, plan the power supply facility so that the current-carrying
capacity for one power unit can provide the total capacity for two power units.
3. This table shows the power requirement (100 V or 200 V) for the maximum
configuration . The actual required power might exceed the value shown in the
table when the tolerance is included.
Environmental specifications
The environmental specifications for the storage systems are described in the following
table.
Temperature
Caution: The following storage system components are not supported in
high-temperature environments. Do not operate the following components at
temperatures of 40°C or higher:
■
Hitachi Vantara-provided service processor (SVP) server
■
First-generation FMDs (non-DC2 FMDs)