F111 (SERIES 3) IN CEILING MEDIA AIR CLEANER

3

68-0198—05

Fig. 1. Approximate dimensions of F111 

(Series 3) in in. (mm).

Installation Weight:

Approximately 115 lb to 155 lb (52.16 kg to 70.3 kg) 

depending on the filter configuration. Refer to Table 3.

Table 3. Sorbent Module Weight.

Sound Level at 3.3 ft (1m):

Low speed: 53 dBA
Medium speed: 57 dBA
High speed: 61 dBA

Grille Type: 

Perforated metal.

Mounting: 

Recesses into opening on the ceiling.

Approvals:

Underwriters Laboratories Inc.: Listed. 
Canadian Standards Association: Listed.

Accessories: 

Remote 3-Speed Wall Switch 

Replacement Parts 

See Parts List, Table 5.

PLANNING THE 
INSTALLATION

The number of F111 (Series 3) air cleaners that are needed 
is determined by taking into account the number of 
occupants and the volume of the space. Type of 
contamination, outdoor air quality and use of the area are 
also factors. Refer to Table 3 for general guidelines when 
determining how many air cleaners are needed.

EXAMPLE:   One air cleaner can provide 2.5 air changes per 

hour in a 24,000 cubic feet (720 cubic meters) 
no smoking area. Table 3 suggests two air 
cleaners for a 24,000 cubic feet area because 
most areas have contaminants that require 
more units to provide quality air.

If any questions should arise concerning determining the 
number of air cleaners needed for an area, consult your 
local Honeywell Commercial Air Cleaner Distributor.

Table 4. Determining the Minimum Number of

Air Cleaners Needed for a Space.

Media

Weight in lb (kg)

CPZ™ modules (2)

43 (20)

22-1/2 (572)

24 (610)

3/8 X 16
INTERNAL 
THREAD (4)

46-3/4 (1187)

48 (1219)

17-1/4

(438)

4-1/2

(114)

TOP VIEW

POWER CONNECTION 
POINT

CEILING

LINE

M11996A

Space Volume 

 (L x W x H) in Cubic 

Feet (Cubic Meter)

Number of 

Persons 

Present

Minimum 

Number of Air 

Cleaners

12000 to 18000 

(360 to 540)

30 to 60

1

18001 to 35000 

(540 to 1050)

61 to 90

2

35001 to 51000 

(1050 to 1530)

91 to 120

3

51001 to 65000 

(1530 to 1950)

121 to 180

4

65001 to 80000 

(1950 to 2400)

181 to 240

5

80001 to 95000 

(2400 to 2850)

241 to 300

6

Содержание F111

Страница 1: ...oking smoke from the air circulated through the filter FEATURES Three levels of filtration 99 97 High Efficiency Particulate Air HEPA Hospital grade filter 95 efficient at 0 3 micron MERV 16 95 ASHRAE MERV 12 Circulates up to 1250 cfm Designed to overcome the increase in air flow resistance normally caused by filter loading White or black color cover to complement the ceiling CPZ module removes up...

Страница 2: ... modules 825 1400 Black F111C1003W 3S 120 Vac 60 Hz 7 0A 99 97 HEPA 85 CPZ modules 825 1400 White F111C1012B 3S 120 Vac 60 Hz 8 0A 95 at 0 3 micron MERV 16 85 CPZ modules 1125 1910 Black F111C1012W 3S 120 Vac 60 Hz 8 0A 95 at 0 3 micron MERV 16 85 CPZ modules 1125 1910 White F111C1073B 3S 120 Vac 60 Hz 7 5A 95 ASHRAE MERV 12 85 CPZ modules 1150 1950 Black F111C1073W 3S 120 Vac 60 Hz 7 5A 95 ASHRAE...

Страница 3: ...s when determining how many air cleaners are needed EXAMPLE One air cleaner can provide 2 5 air changes per hour in a 24 000 cubic feet 720 cubic meters no smoking area Table 3 suggests two air cleaners for a 24 000 cubic feet area because most areas have contaminants that require more units to provide quality air If any questions should arise concerning determining the number of air cleaners need...

Страница 4: ...entrally in a space and mounted into or on a ceiling The cleaning footprint of the air cleaner is rectangular with air patterns that move clean air to the corners of the area while drawing contaminated air up from the center of the area See Fig 2 When multiple air cleaners are installed the allotted areas to be cleaned should be equal The air throw in one direction is approximately 55 ft 17m Air v...

Страница 5: ...ion and safety Canadian installation NEVER install in ceilings with thermal insulation value greater than R 40 Fig 3 Typical F111 Series 3 120V 60 Hz wiring diagram Mount Air Cleaner Cabinet The air cleaner can be mounted in a drop ceiling system or hung in an open area Both mounting methods require the air cleaner to be level and positioned facing downward for correct operation 1 Remove the lid f...

Страница 6: ...connect power to air cleaner at fuse or breaker before beginning work Failure to do so can result in shock hazard endangering equipment and personal safety of installer Only one air cleaner can be connected to a remote switch Fig 5 Wiring F111 Series 3 Air Cleaner 1 Disconnect power to air cleaner 2 Mount 4 x 4 outlet box at desired remote location 3 Attach 3 4 extension ring to outlet box 4 Run f...

Страница 7: ...dy of the spring loaded plunger see Fig 7 2 Turn the threaded barrel out of the spring plunger 3 Insert the threaded barrel through the hole in the lid and turn the spring loaded plunger onto it 4 Tighten the assembly with wrenches 5 Repeat steps 1 through 4 for the second plunger Opening Closing the Lid To open the lid pull the spring loaded plungers back to disengage the plunger Carefully swing ...

Страница 8: ...rs need to be changed more frequently in facilities that operate 24 hours a day Prefilter The disposable prefilter collects large dust particulates and lint type airborne fibers Check the filter every two weeks to determine the replacement frequency 1 Slowly open the lid supporting the lid so the filters do not fall out 2 Remove the dirty prefilter 3 Install the new prefilter in the air cleaner li...

Страница 9: ...fer to Fig 9 and Table 5 for replacement part information Table 5 Replacement Parts Fig Reference No Description Pack Qty Order Number 1 CPZ sorbent module requires 2 used with HEPA 95 DOP or 95 ASHRAE particle filters 1 32004078 003 Charcoal sorbent module requires 2 used with HEPA 95 DOP or 95 ASHRAE particle filters 1 32004078 002 Permanganate sorbent module requires 2 used with HEPA 95 DOP or ...

Страница 10: ...HES DISPOSABLE PREFILTER PART 32002307 001 HEPA MEDIA FILTER PART 32000204 002 95 ASHRAE PARTICLE FILTER PART 50004739 001 95 DOP FILTER PART NUMBER 32000203 001 MOTOR 120V 60 HZ MOTOR CAPACITOR 120V 60 HZ BLOWER WHEEL SORBENT MEDIA MODULE 2 REQUIRED CHARCOAL PART 32004078 002 ZEOLITE PART 32004078 003 PERMANGANATE PART 32004078 004 M11995E ...

Страница 11: ...11 68 0198 05 ...

Страница 12: ...gies In the U S Honeywell 715 Peachtree Street NE Atlanta GA 30308 customer honeywell com buildingcontrols honeywell com U S Registered Trademark 2020 Honeywell International Inc 68 0198 05 M S Rev 09 20 Printed in United States ...

Отзывы: