CHAPTER 5: SETTINGS
CONTROL ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
5-267
5
The steady-state frequency of a power system is a certain indicator of the existing balance between the generated power
and the load. Whenever this balance is disrupted through the loss of an important generating unit or the isolation of part
of the system from the rest of the system, the effect is a reduction in frequency. If the control systems of the system
generators do not respond fast enough, the system can collapse. A reliable method to quickly restore the balance between
load and generation is to automatically disconnect selected loads, based on the actual system frequency. This technique,
called “load-shedding,” maintains system integrity and minimize widespread outages. After the frequency returns to
normal, the load can be restored automatically or manually.
UNDERFREQ 1 SOURCE
— This setting is used to select the source for the signal to be measured. The element first checks for
a live phase voltage available from the selected source. If voltage is not available, the element attempts to use a phase
current. If neither voltage nor current is available, the element does not operate, as it does not measure a parameter
below the minimum voltage/current setting.
UNDERFREQ 1 MIN VOLT/AMP
— Selects the minimum per unit voltage or current level required to allow the underfrequency
element to operate. This threshold is used to prevent an incorrect operation because there is no signal to measure.
UNDERFREQ 1 PICKUP
— Selects the level at which the underfrequency element is to pickup. For example, if the system
frequency is 60 Hz and the load shedding is required at 59.5 Hz, the setting is 59.50 Hz.
Figure 5-146: Underfrequency logic
5.8.6 Autoreclose (ANSI 79)
SETTINGS
CONTROL ELEMENTS
AUTORECLOSE
AUTORECLOSE 1(6)
AUTORECLOSE 1
AR1 FUNCTION:
Disabled
Range: Disabled, Enabled
AR1 INITIATE:
Off
Range: FlexLogic operand
AR1 BLOCK:
Off
Range: FlexLogic operand
AR1 MAX NUMBER OF
SHOTS: 1
Range: 1, 2, 3, 4
AR1 REDUCE MAX TO 1:
Off
Range: FlexLogic operand
AR1 REDUCE MAX TO 2:
Off
Range: FlexLogic operand
AR1 REDUCE MAX TO 3:
Off
Range: FlexLogic operand
AR1 MANUAL CLOSE:
Off
Range: FlexLogic operand
AR1 MNL RST FRM LO:
Off
Range: FlexLogic operand
AR1 RESET LOCKOUT IF
BREAKER CLOSED: Off
Range: Off, On
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...