CHAPTER 10: COMMISSIONING
10.12 TIME OVERCURRENT (51PH, 51PL, 51N, 51G, 46)
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
10-13
10.12 Time overcurrent (51PH, 51PL, 51N, 51G, 46)
Set the relay to trip for the protection element being tested. Configure any of the outputs to be activated only by the
protection element being tested.
Apply 0.9 times the Pickup current and check that the relay does not trip.
Apply 1.5 times the Pickup current. The relay should trip according to the time corresponding to its set curve.
Apply 5 times the Pickup current. The relay should trip according to the time corresponding to its set curve.
Protection Element Settings (51PH, 51PL, 51N, 51G and 46)
Setting
Value
Unit
Function
Enabled
Input
Phasor (DFT)
Pickup Level
1
A
Curve
Modify for each test
TD Multiplier
Modify for each test
Voltage Restraint
Disabled
Element
Phase
Curve type
Dial
Times Ipickup Tripping times (sec)
EXPECTED
Admissible
51PH
IA
IEEE Ext Inv
0.5
0.9
NA
1.5
11.34
[11.00 – 11.90]
5
0.648
[0.600 – 0.710]
IB
IEC Curve A
0.05
0.9
NA
1.5
0.860
[0.750 – 0.950]
5
0.214
[0.200 – 0.300]
51PL
IC
IEEE Ext Inv
0.5
0.9
NA
1.5
11.34
[11.00 – 11.60]
5
0.648
[0.600 – 0.710]
IB
IEC Curve A
0.05
0.9
NA
1.5
0.860
[0.750 – 0.950]
5
0.214
[0.200 – 0.300]
51N
IC
IEEE Ext Inv
0.5
0.9
NA
1.5
11.34
[11.00 – 11.60]
5
0.648
[0.600 – 0.710]
51G
IG
Definite Time
2
0.9
NA
5
2.000
[1.900 – 2.100]
46
I2
IEC Curve A
0.05
0.9
NA
1.5
0.860
[0.750 – 0.950]
5
0.214
[0.200 – 0.300]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...