CHAPTER 10: COMMISSIONING
10.8 VERIFICATION OF MEASUREMENT
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
10-7
Percent of Load-to-Trip
The relevant actual values displays are shown below:
Actual > Metering > Primary Values > Current >
% of Load-to-trip
Note
Percent of load-to-trip is calculated from the phase with the highest current reading. It is the ratio of this current to
the lowest pickup setting among the phase time and instantaneous overcurrent protection features. If all of these features
are disabled, the value displayed is “0”.
- Inject current of various values into Phase A.
- Verify that percent load-to-trip is calculated as the correct
percentage of the most sensitive operational Phase Overcurrent
element and displayed.
- Repeat for phases B and C.
10.8.3 Active, reactive power, and COSJ metering
Equations to be applied for powers in a wye connection are as follows:
Apply the following current and voltage values:
With the indicated voltage and current values, verify that the power measure corresponds to expected values indicated in
the following table:
Maximum admissible error is ± 1% of the test value for P and Q, and 0.02 for cosj.
Power per phase
Three-phase power
P=V*I*Cos
ϕ
P=Pa+Pb+Pc
Q=V*I*Sen
ϕ
Q=Qa+Qb+Qc
APPLIED VOLTAGE AND CURRENT VALUES PER PHASE
Phase a
Phase b
Phase c
V-I Angles
VI = 50 V, 0º
VII = 50 V , 120º
VIII = 50V, 240º
ϕ
=45º
Ia = 10
∠
45º
Ib= 10
∠
165º
Ic = 10
∠
285º
Cos
ϕ
= 0.707
EXPECTED POWER VALUES
Phase a
Phase b
Phase c
Three-phase
Pa = 353.55 MW
Pb = 353.55 MW
Pc = 353.55 MW
P = 1060.66 MW
Qa = 353.55 MVAr
Qb = 353.55 MVAr
Qc = 353.55 MVAr
Q = 1060.66 MVAr
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...