![GE Multilin F650 Скачать руководство пользователя страница 292](http://html.mh-extra.com/html/ge-multilin/f650/f650_instruction-manual_572016292.webp)
5-140
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
5.6 INPUTS/OUTPUTS
CHAPTER 5: SETPOINTS
5.6.4 Outputs
Output settings description
Output Logic_0X _0Z:
Type of logic applied to outputs. Possible values are
positive
and
negative
. The default value is
positive. Depending on the type of setting selected, the physical output is in the same direction (positive) or opposite
(negative) the output activation command.
Output Type_0X _0Z:
Type of output adjusted. Possible values are
normal
,
pulse
or
latched
, the default value is
Normal
.
Normal
:
The contact output follows the activation command. Remains active while the operation signal is active.
Pulse
:
The contact output is active the pulse output time, according to the
Pulse Output Time
setting.
Latched
:
The output remains active after the operation signal has been cleared. The reset signal for the latched
outputs is configured at
Setpoint > Relay Configuration > Outputs > Contact Output Reset
”.
Pulse Output Time_0X _0Z:
This is the length of the output pulse in case the output type is selected as
pulse
; the default
value is 10000 ms.
Figure 5-36: Output logic typesshows the types of signals associated with the different output configuration types
.
Figure 5-36: Output logic types
5.6.4.1 Output status signals
Boards types 1 and 2 have both 8 outputs, so the representation is the same for both types as shown in Table 5-86:
Contact output signals
Actual > Inputs/Outputs >Contact Output Status
Real status of the contact output, which corresponds to the transformation of the output activation signal (Contact output
operate), by the logic applied to this output in
Setpoint > Inputs/Outputs >Contact I/O > Board X
Actual > Inputs/Outputs > Contact Output Operates
Activated or deactivated status of those variables used internally to operate a contact output.
Actual > Inputs/Outputs > Contact Output Resets
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...