GE Multilin
F60 Feeder Protection System
4-23
4 HUMAN INTERFACES
4.2 FACEPLATE INTERFACE
4
For this application (setup shown below), the relay is connected and programmed for both breaker 1 and breaker 2. The
USER 1 key performs the selection of which breaker is to be operated by the USER 2 and USER 3 keys. The USER 2 key
is used to manually close the breaker and the USER 3 key is used to manually open the breaker.
e) CONTROL OF ONE BREAKER
For this application the relay is connected and programmed for breaker 1 only. Operation for this application is identical to
that described above for two breakers.
4.2.6 KEYPAD
Display messages are organized into pages under the following headings: actual values, settings, commands, and targets.
The MENU key navigates through these pages. Each heading page is divided further into logical subgroups.
The MESSAGE keys navigate through the subgroups. The VALUE keys increment or decrement numerical setting values
when in programming mode. These keys also scroll through alphanumeric values in the text edit mode. Alternatively, val-
ues can be entered with the numeric keypad.
The decimal key initiates and advances to the next character in text edit mode or enters a decimal point.
The HELP key can be pressed at any time for context-sensitive help messages.
The ENTER key stores altered setting values.
When entering an IP address on the front panel, key in the first sequence of the number, then press the • key for the deci-
mal place. For example, for 127.0.0.1, press 127, then •, then 0, then •, then 0, then •, then 1. To save the address, press
the ENTER key.
4.2.7 MENUS
a) NAVIGATION
Press the MENU key to select a header display page (top-level menu). The header title appears momentarily followed by a
header display page menu item. Each press of the MENU key advances through the following main heading pages:
•
Actual values
•
Settings
ENTER COMMAND
PASSWORD
This message appears when the USER 1, USER 2, or USER 3 key is pressed and a
COMMAND PASSWORD
is required; i.e. if
COMMAND PASSWORD
is enabled and no com-
mands have been issued within the last 30 minutes.
Press USER 1
To Select Breaker
This message appears if the correct password is entered or if none is required. This mes-
sage displays for 30 seconds or until the USER 1 key is pressed again.
BKR1-(Name) SELECTED
USER 2=CLS/USER 3=OP
This message is displayed after the USER 1 key is pressed for the second time. Three
possible actions can be performed from this state within 30 seconds as per items
(1)
,
(2)
and
(3)
below:
(1)
USER 2 OFF/ON
To Close BKR1-(Name)
If the USER 2 key is pressed, this message appears for 20 seconds. If the USER 2 key is
pressed again within that time, a signal is created that can be programmed to operate an
output relay to close breaker 1.
(2)
USER 3 OFF/ON
To Open BKR1-(Name)
If the USER 3 key is pressed, this message appears for 20 seconds. If the USER 3 key is
pressed again within that time, a signal is created that can be programmed to operate an
output relay to open breaker 1.
(3)
BKR2-(Name) SELECTED
USER 2=CLS/USER 3=OP
If the USER 1 key is pressed at this step, this message appears showing that a different
breaker is selected. Three possible actions can be performed from this state as per
(1)
,
(2)
and
(3)
. Repeatedly pressing the USER 1 key alternates between available breakers.
Pressing keys other than USER 1, 2, or 3 at any time aborts the breaker control function.
Содержание F60
Страница 10: ...x F60 Feeder Protection System GE Multilin TABLE OF CONTENTS ...
Страница 30: ...1 20 F60 Feeder Protection System GE Multilin 1 5 USING THE RELAY 1 GETTING STARTED 1 ...
Страница 138: ...4 28 F60 Feeder Protection System GE Multilin 4 2 FACEPLATE INTERFACE 4 HUMAN INTERFACES 4 ...
Страница 454: ...5 316 F60 Feeder Protection System GE Multilin 5 10 TESTING 5 SETTINGS 5 ...
Страница 500: ...7 14 F60 Feeder Protection System GE Multilin 7 1 COMMANDS 7 COMMANDS AND TARGETS 7 ...
Страница 508: ...8 8 F60 Feeder Protection System GE Multilin 8 2 FAULT LOCATOR 8 THEORY OF OPERATION 8 ...
Страница 522: ...10 12 F60 Feeder Protection System GE Multilin 10 6 DISPOSAL 10 MAINTENANCE 10 ...
Страница 660: ...B 116 F60 Feeder Protection System GE Multilin B 4 MEMORY MAPPING APPENDIX B B ...
Страница 706: ...E 10 F60 Feeder Protection System GE Multilin E 1 IEC 60870 5 104 APPENDIX E E ...
Страница 718: ...F 12 F60 Feeder Protection System GE Multilin F 2 DNP POINT LISTS APPENDIX F F ...
Страница 728: ...H 8 F60 Feeder Protection System GE Multilin H 2 ABBREVIATIONS APPENDIX H H Z Impedance Zone ...
Страница 730: ...H 10 F60 Feeder Protection System GE Multilin H 3 WARRANTY APPENDIX H H ...