background image

F30 CONTROL LAYOUT AND FUNCTION

1

 

START-UP TIMER  Adjustable in steps from 0 to 180 seconds, runs 
once only each time the controller is powered up or reset.

2

 

RUN-ON TIMER Adjustable in steps from 0 to 300 seconds. Can 
be  used  to  prevent  the  pump  from  cutting  out  on  minor  supply 
interruptions as caused by air in the piping. Can also be used to 
run the pump on after the flow stops, and pressurise pipes, or to 
charge an air cell.

3

 

PADDLE  status  LED  turns  green  whenever  the  paddle  is  on 
(whenever  there  is  flow),  slowly  blinks  red  when  the  controller  is 
in standby mode with the paddle off, to indicate the power is on 
and the pump is being monitored. This LED also flashes rapidly red 
in alarm mode, if the pump has run dry. Once in alarm mode, the 
controller will not allow the pump to restart until the power to the 
unit has been reset. This light is an excellent tool for setting up the 
controllers and for diagnosing problems with the pump system.

4

 

AUXILIARY  This  LED  turns  blue  to  indicate  the  true  status  of  a 
pressure switch connected to the auxiliary terminal. When this LED 
in on, the pressure switch contacts are closed, when it is off, the 
pressure switch contacts are open.

5

 

TIMERS  This  LED  turns  green  when  the  main  timer  is  running, 
which occurs each time the system is powered up. It also indicates 
when the run on timer is running by turning red. When setting up 
a controller this LED is essential because it allows you to observe 
exactly how long the timers run after the paddle has been pushed 
into the on position by the flow. It allows the timer dials to then be 
correctly set to slightly longer than the time it takes for the paddle 
LED to come on.

C

 

Common  output  terminal.  Power  is  normally  looped  into  the 
common terminal from the supply active.

NO

  Normally  open  terminal.  A  switch  wire  is  normally  run  from  this 

terminal directly to the pump motor.

NC

  Normally closed terminal. Usually left unused, but can be connected 

to an external alarm if required.

A

 

Active  terminal  connects  to  the  supply  active,  via  an  isolation 
switch.

N

 

Neutral terminal connects to the supply neutral.

AUX

  The  auxiliary  terminal  accepts  a  switched  input  from  an  external 

pressure switch. The switched supply to the AUX terminal should 
be  at  the  same  voltage,  and  from  the  same  phase  as  the  main 
supply to the controller.     

E

 

Earth terminal, isolated binding post for termination of earth wires.

5

30

60

60

5

0

30

TIMERS

PADDLE

RUN-ON

TIMER

START-UP

TIMER

SECONDS

NO

C

NC

A

N

E

AUX

1

2

3

4

AUXILIARY

5

GENERAL LAYOUT OF F30 CONTROLS

PRESSURE SWITCH SETTING

A pressure switch is usually set to switch the pump on at about 140kPa 
and to switch it off at about 420kPa. When used with an F30, the pressure 
switch  should  be  readjusted  so  it  switches  on  at  about  80  to  100kPa 
above the system’s static pressure, and switches after a minimal rise in 
pressure. Set the differential setting screw on the switch to the minimum 
differential, and adjust the cut in pressure so that with the pump switched 
off,  the  pressure  switch  closes  its  contacts  before  all  the  pressure 
dissipates and it reaches a static pressure state. The object is to have 
the pressure switch always close its contacts on a falling pressure before 
all the pressure dissipates. By setting the differential to a minimum, you 
ensure the pressure switch will open its contacts on a rising pressure just 
after the pump starts. The F30 uses the state of the pressure switch to 
identify if the pump is running dry. It is important to have the pressure 
switch open its contacts before the run-on timer in the F30 times out. By 
setting the differential to a minimum, you allow the full range of time delay 
setting on the F30 run-on timer to be available for adjustment.   
  

TIMER SETTINGS

Time delay adjustment is by means of two 16 position rotary switches.  

The time delays are individually programmed into the controllers to give 
the switches the following settings.

TIMER

DELAY IN SECONDS

Start-up Timer

0, 1, 2, 3, 4, 5, 10, 15, 20, 25, 30, 40, 50, 60, 120, 180

Run-on Timer

0, 1, 2, 3, 4, 5, 10, 15, 20, 25, 30, 40, 50, 60, 180, 300

ADJUSTING TIMER SETTINGS

When adjusting the timer settings, the power to the controller must be 

reset, that is, it must be turned off for a minimum of 1 second and then 

turned on again, before the changes will take effect. This applies to all 

the controllers. 

BASIC FLOW SWITCH FUNCTION

The  F30  pump  controllers  have  two  independent  timers  and  are 

individually  adjustable  in  steps.  With  both  timer  dials  set  to  zero,  the 

controllers behave like a basic flow switch, they respond solely to paddle 

movement. On power up, the only indication of activity will be the paddle 

light  slowly  blinking  red  to  indicate  the  power  is  on.  If  the  paddle  is 

pushed into the on position, the pump will start and the paddle light will 

turn green. If the paddle swings to the off position (because flow stops), 

the pump will stop and the paddle light will revert to slowly blinking red.

OVERRIDE ON START 

On power up, the F30 will start the pump. The green timer light will also 

come on and stay on for whatever time you have set the start-up timer 

to. If the paddle is pushed into the on position by flow during the time 

out period, the green paddle light will also come on. At the end of the 

time  out,  the  timer  light  will  go  out,  but  if  the  paddle  is  on,  the  pump 

will continue to run.  The green paddle light will remain on. If the paddle 

subsequently swings to the off position because flow stops, the paddle 

light will turn off and the pump will stop. The main paddle light will then 

revert to slowly blinking red.   
When running the controller in the override on start mode as described, 

the main timer is normally set to slightly longer than the time required for 

the paddle light to come on.  By watching the timer light and the paddle 

light  and  observing  what  happens  on  power  up,  it  becomes  a  simple 

matter to correctly set the timer.

RUN-ON TIMER 

On  power  up,  the  pump  will  start,  the  green  timer  light  will  also  come 

on.  If the paddle is pushed forward by flow, the green paddle light will 

also come on.  After the start-up timer’s initial time out, the green timer 

light will go out but the pump will continue to run and the paddle light 

will  remain  on,  green.  If  the  flow  stops,  the  green  paddle  light  will  go 

out and the timer light will turn on red indicating the pump is running on 

the run-on timer. The pump will continue to run while the run-on timer is 

running. If the paddle then swings back into the on position before the 

run-on timer times out, then the pump will continue to run seamlessly.  

If however the paddle fails to return to the on position by the time the 

run-on timer times out, the pump will stop. The run-on timer’s red light 

will go out and the green paddle light will also go out. If the paddle is 

subsequently pushed back into the on position, the paddle light will again 

come on and the pump will restart.  Every time the paddle swings back 

to the off position the run-on timer will re-run and keep the pump running 

while it times out.  
The main timer and the run-on timer function independently of each other 

and  are  totally  flexible.  For  example  you  can  set  the  main  timer  to  3 

seconds to get a pump started and the run-on timer to 2 minutes to run 

a pump on and pressurise a pipe system or very large air cell. Alternately, 

you could set the main timer to 3 minutes to allow a bore pump with a 

self draining riser time to prime its riser, and you could also set the run-on 

timer to 2 or 3 minutes to pressurise a feed line to a remote stock trough, 

long after the main flow has reduced to a trickle.
In addition to the simple override functions the F30 controllers can accept 

an input from an external switch, usually a pressure switch.  When used, 

the auxiliary input allows the controller to start on a falling pressure and 

to identify a dry run situation.  The F30 controllers also include an alarm 

routine that locks out the pump in the event of dry running, preventing it 

from restarting until the problem is fixed or the power is reset.
To use the auxiliary input, the pressure switch must be correctly adjusted, 

and should be set so its low pressure contacts close on a falling pressure 

at 8 to10M head pressure above the system’s static pressure.  In other 

words  in  a  pressurised  system  with  a  slow  leak,  the  pressure  switch 

contacts must close before all the pressure leaches away.  In addition, 

the pressure switch differential setting must be set to a minimum.  The 

object is to have the pressure switch start the pump only, and then for its 

contacts to open as soon as the pressure starts to rise, and before the 

run-on timer in the F30 controller times out.