5-208
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
FLEXLOGIC
CHAPTER 5: SETTINGS
5
ELEMENT:
Breaker control
BREAKER 1 OFF CMD
BREAKER 1 ON CMD
BREAKER 1
Φ
A BAD ST
BREAKER 1
Φ
A INTERM
BREAKER 1
Φ
A CLSD
BREAKER 1
Φ
A OPEN
BREAKER 1
Φ
B BAD ST
BREAKER 1
Φ
B INTERM
BREAKER 1
Φ
B CLSD
BREAKER 1
Φ
B OPEN
BREAKER 1
Φ
C BAD ST
BREAKER 1
Φ
C INTERM
BREAKER 1
Φ
C CLSD
BREAKER 1
Φ
C OPEN
BREAKER 1 BAD STATUS
BREAKER 1 CLOSED
BREAKER 1 OPEN
BREAKER 1 DISCREP
BREAKER 1 TROUBLE
BREAKER 1 MNL OPEN
BREAKER 1 MNL CLS
BREAKER 1 TRIP A
BREAKER 1 TRIP B
BREAKER 1 TRIP C
BREAKER 1 ANY P OPEN
BREAKER 1 ONE P OPEN
BREAKER 1 OOS
BREAKER 1 TAG ON
BREAKER 1 TAG OFF
BREAKER 1 SUBD CLSD
BREAKER 1 SUBD OPEN
BREAKER 1 BYPASS ON
BREAKER 1 BYPASS OFF
BREAKER 1 BLK RCLS
BREAKER 1 ENA RCLS
Breaker 1 3-pole open command/trip initiated
Breaker 1 close command initiated
Breaker 1 phase A bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase A intermediate status is detected (transition from one
position to another)
Breaker 1 phase A is closed
Breaker 1 phase A is open
Breaker 1 phase B bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase B intermediate status is detected (transition from one
position to another)
Breaker 1 phase B is closed
Breaker 1 phase B is open
Breaker 1 phase C bad status is detected (discrepancy between the 52/a and
52/b contacts)
Breaker 1 phase C intermediate status is detected (transition from one
position to another)
Breaker 1 phase C is closed
Breaker 1 phase C is open
Breaker 1 bad status is detected on any pole
Breaker 1 is closed
Breaker 1 is open
Breaker 1 has discrepancy
Breaker 1 trouble alarm
Breaker 1 manual open
Breaker 1 manual close
Breaker 1 trip phase A command
Breaker 1 trip phase B command
Breaker 1 trip phase C command
At least one pole of breaker 1 is open
Only one pole of breaker 1 is open
Breaker 1 is out of service
Breaker 1 tagged so manual trip and close and autoreclose are blocked
Breaker 1 not tagged
Breaker 1 status manually substituted to closed
Breaker 1 status manually substituted to open
Breaker 1 control interlocking is manually bypassed
Breaker 1 control interlocking is not manually bypassed
Breaker 1 command to manually block autoreclose
Breaker 1 command to manually enable autoreclose
BREAKER 2 to 6
Same set of operands as shown for BREAKER 1
ELEMENT:
Broken conductor
BROKEN CONDUCT 1 OP
BROKEN CONDUCT 1 PKP
Asserted when the broken conductor 1 element operates
Asserted when the broken conductor 1 element picks up
BROKEN CONDUCT 2 to 6
Same set of operands as shown for BROKEN CONDUCTOR 1
ELEMENT:
Cold load pickup
COLD LOAD 1 OP
Cold load pickup element 1 has operated
COLD LOAD 2 to 6
Same set of operands as shown for COLD LOAD 1
ELEMENT:
Digital counters
Counter 1 HI
Counter 1 EQL
Counter 1 LO
Digital counter 1 output is ‘more than’ comparison value
Digital counter 1 output is ‘equal to’ comparison value
Digital counter 1 output is ‘less than’ comparison value
Counter 2 to 8
Same set of operands as shown for Counter 1
ELEMENT:
Digital elements
Dig Element 1 PKP
Dig Element 1 OP
Dig Element 1 DPO
Digital Element 1 is picked up
Digital Element 1 is operated
Digital Element 1 is dropped out
Dig Element 2 to 48
Same set of operands as shown for Dig Element 1
ELEMENT:
FlexElements
FxE 1 PKP
FxE 1 OP
FxE 1 DPO
FlexElement 1 has picked up
FlexElement 1 has operated
FlexElement 1 has dropped out
FxE 2 to 16
Same set of operands as shown for FxE 1
ELEMENT:
Ground
instantaneous
overcurrent
GROUND IOC1 PKP
GROUND IOC1 OP
GROUND IOC1 DPO
Ground instantaneous overcurrent 1 has picked up
Ground instantaneous overcurrent 1 has operated
Ground instantaneous overcurrent 1 has dropped out
Operand type
Operand syntax
Operand description