2-18
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
SPECIFICATIONS
CHAPTER 2: PRODUCT DESCRIPTION
2
Other advanced UR order code options are available to support IEC 61850 Ed2.0 (including fast GOOSE, MMS server, 61850
services, ICD/CID/IID files, and so on), IEEE 1588 (IEEE C37.238 power profile) based time synchronization, CyberSentry
(advanced cyber security), the Parallel Redundancy Protocol (PRP), IEC 60870-5-103, and so on.
2.5 Specifications
Specifications are subject to change without notice.
2.5.1 Protection elements
The operating times include the activation time of a trip rated form-A output contact unless otherwise indicated. FlexLogic
operands of a given element are 4 ms faster. Take this into account when using FlexLogic to interconnect with other
protection or control elements of the relay, building FlexLogic equations, or interfacing with other intelligent electronic
devices (IEDs) or power system devices via communications or different output contacts. If not specified, the operate times
given here are for a 60 Hz system at nominal system frequency. Operate times for a 50 Hz system are 1.2 times longer.
PHASE/NEUTRAL/GROUND TOC
Current:
Phasor or RMS
Pickup level:
0.020 to 30.000 pu in steps of 0.001
Dropout level:
97% to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT:
±0.5% of reading or ±0.4% of rated (whichever is greater)
> 2.0
×
CT:
±1.5% of reading > 2.0
×
CT rating
Curve shapes:
IEEE Moderately/Very/Extremely Inverse; IEC (and BS) A/B/C and Short Inverse; GE IAC Inverse,
Short/Very/ Extremely Inverse; I
2
t; FlexCurves™ (programmable); Definite Time (0.01 s base
curve)
Curve multiplier:
Time Dial = 0.00 to 600.00 in steps of 0.01
Reset type:
Instantaneous/Timed (per IEEE)
Curve timing accuracy at 1.03 to 20 x pickup:
±3.5% of operate time or ±½ cycle (whichever is greater) from pickup to operate
Voltage restraint:
Modifies pickup current for voltage in the range of 0.1 < V < 0.9 VT Nominal in a fixed linear rela-
tionship
PHASE/NEUTRAL/GROUND IOC
Pickup level:
0.020 to 30.000 pu in steps of 0.001
Dropout level:
97 to 98% of pickup
Level accuracy:
0.1 to 2.0
×
CT rating:
±0.5% of reading or ±0.4% of rated (whichever is greater)
> 2.0
×
CT rating:
±1.5% of reading
Overreach:
<2%
Pickup delay:
0.00 to 600.00 s in steps of 0.01
Reset delay:
0.00 to 600.00 s in steps of 0.01
Operate time:
<16 ms at 3
×
pickup at 60 Hz (Phase/Ground IOC)
<20 ms at 3
×
pickup at 60 Hz (Neutral IOC)
Timer accuracy:
±3% of operate time or ±1/4 cycle (whichever is greater)
NEGATIVE SEQUENCE TOC
Pickup level:
0.020 to 30.000 pu in steps of 0.001
Dropout level:
97% to 98% of pickup
Level accuracy:
±0.5% of reading or ±0.4% of rated (whichever is greater)
from 0.1 to 2.0 x CT rating
±1.5% of reading > 2.0 x CT rating