Содержание F700

Страница 1: ... 0x Hardware Reference Guide This document provides information about the system hardware components and the mechanical and environmental specifications for the Hitachi Virtual Storage Platform F700 all flash array MK 97HM85017 01 September 2018 ...

Страница 2: ...rom authorized employees and other individuals and 2 Verifying that your data continues to be held retrieved deleted or otherwise processed in accordance with relevant laws Notice on Export Controls The technical data and technology inherent in this Document may be subject to U S export control laws including the U S Export Administration Act and its associated regulations and may be subject to ex...

Страница 3: ...without bezel 16 CBL controller rear panel LEDs 18 CBL controller power supply unit LEDs and connectors 18 Host Network and Drive Tray Ports and LEDs 19 Front end modules 19 10 Gbps iSCSI board LEDs and connectors optical 20 10 Gbps iSCSI board LEDs and connectors copper 20 8 Gbps 16 Gbps or 32 Gbps Fibre Channel 4 port board LEDs and connectors 22 16 Gbps Fibre Channel 2 port board LEDs and conne...

Страница 4: ... system parts list 41 VSP F700 parts list 41 Drive tray and drive configuration 44 Data and power cable model list 44 Appendix B System specifications 48 VSP F700 mechanical specifications 48 Electrical specifications 52 Environmental specifications 53 Shared memory 59 Appendix C Network access 62 TCP IP port assignments 62 Controller connections 65 Physical service processor connections 65 Append...

Страница 5: ...C19CE P 90 APAC and EMEA single phase PDU 1P32A 18C13 3C19CE P 91 APAC and EMEA three phase PDU 3P16A 9C13 3C19CE P 92 APAC and EMEA three phase PDU 3P16A 15C13 3C19CE P 93 APAC and EMEA three phase PDU 3P32A 24C13 6C19CE P 94 Appendix F Non Hitachi racks 96 Non Hitachi rack support 96 Hitachi Universal V2 Rack rail kits 96 Hitachi Universal V2 Rack accessories 97 Appendix G Warning labels on the ...

Страница 6: ...elopment Kit website http sourceforge net apps mediawiki tianocore index php title UDK2010 2004 Intel Corporation All rights reserved Redistribution and use in source and binary forms with or without modification are permitted provided that the following conditions are met Redistributions of source code must retain the above copyright notice this list of conditions and the following disclaimer Red...

Страница 7: ...ITY OF SUCH DAMAGE Product version This document revision applies to VSP F700 firmware 88 02 0x or later Release notes Read the release notes before installing and using this product They may contain requirements or restrictions that are not fully described in this document or updates or corrections to this document Release notes are available on Hitachi Vantara Support Connect https knowledge hit...

Страница 8: ...r output by the system Example pairdisplay g group For exceptions to this convention for variables see the entry for angle brackets Monospace Indicates text that is displayed on screen or entered by the user Example pairdisplay g oradb angle brackets Indicates variables in the following scenarios Variables are not clearly separated from the surrounding text or from other variables Example Status r...

Страница 9: ... a hazardous situation which if not avoided could result in death or serious injury Conventions for storage capacity values Physical storage capacity values for example disk drive capacity are calculated based on the following values Physical capacity unit Value 1 kilobyte KB 1 000 103 bytes 1 megabyte MB 1 000 KB or 1 0002 bytes 1 gigabyte GB 1 000 MB or 1 0003 bytes 1 terabyte TB 1 000 GB or 1 0...

Страница 10: ...fter the release of the product Getting help Hitachi Vantara Support Connect is the destination for technical support of products and solutions sold by Hitachi Vantara To contact technical support log on to Hitachi Vantara Support Connect for contact information https support hitachivantara com en_us contact us html Hitachi Vantara Community is a global online community for Hitachi Vantara custome...

Страница 11: ...de the document title and number including the revision level for example 07 and refer to specific sections and paragraphs whenever possible All comments become the property of Hitachi Vantara Corporation Thank you Comments Preface Hitachi Virtual Storage Platform F700 Hardware Reference Guide 11 ...

Страница 12: ...ndant configuration so that the storage system can remain operational if a component fails Adding and replacing components along with firmware upgrades can be conducted while the storage system is active and without interruption of data availability to the hosts A hot spare drive can be configured to replace a failed data drive automatically securing the fault tolerant integrity of the logical dri...

Страница 13: ... reliability Main system components are configured with redundancy to maintain continued service RAID 1 RAID 5 and RAID 6 support RAID 6 including 14D 2P Provides data security by transferring data to cache flash memory at the time of a power outage Scalability and versatility Flash drive tray DBF Up to 12 flash module drives FMD can be installed 2U size Supports system environments with mixed ope...

Страница 14: ...th LED indicators for monitoring its operating conditions and notifying possible component replacement CBL controller chassis The controller chassis houses controllers backup fan modules and power supplies The chassis also includes specific functional LEDs located on the front and rear of controller to provide its operating status The following table lists the controller board specifications Compo...

Страница 15: ... not blink even if the following failure service information messages SIM are issued 452xxx 462xxx 3077xx 4100xx and 410100 LED might turn off during user maintenance 4 ALARM LED Off Normal operation Red Processor failure system might be down For assistance contact customer support https support hitachivantara com en_us contact us html 5 POWER ON OFF main switch Powers the storage system CBL contr...

Страница 16: ...bes the definitions of the CBL controller front panel LEDs Number Item Description 1 POWER ON OFF main switch Powers the storage system 2 POWER READY WARNING and ALARM LEDs Note When System Option Mode 1097 is set to ON the WARNING LED does not blink even if the following failure service information messages SIM are issued 452xxx 462xxx 3077xx 4100xx and 410100 3 Controllers Controller 1 bottom an...

Страница 17: ... unit of the controller Amber LAN reset switch was pressed 9 LAN RST switch Use only when instructed by customer support 10 STATUS LED for BKMF Green Charging of the battery in the backup module is complete Red Backup module can be removed Blink red one time Main battery failure Blink red two times Backup battery failure Blink red three times Both batteries failed or preventive maintenance replace...

Страница 18: ... following table describes the definitions of the CBL controller rear panel LEDs Number Item 1 Power supply unit 2 Front end module 3 Back end module 4 LAN blade CBL controller power supply unit LEDs and connectors The following table lists the definitions of the CBL controller power supply unit LEDs and connectors CBL controller rear panel LEDs Chapter 2 System controller Hitachi Virtual Storage ...

Страница 19: ...e equipped with specific interfaces for connecting powering configuring and managing the storage system The component LEDs display the operating status of the storage system Front end modules The following front end modules are available for the controllers The LEDs display the operating status of the module Host Network and Drive Tray Ports and LEDs Chapter 2 System controller Hitachi Virtual Sto...

Страница 20: ...ly 2 PORT LED Red Small form factor pluggable can be removed Blue Normal link status Blink blue Front end module is in communication status 3 ISCSI connectors Connect to Ethernet cables 10 Gbps iSCSI board LEDs and connectors copper 10 Gbps iSCSI board LEDs and connectors optical Chapter 2 System controller Hitachi Virtual Storage Platform F700 Hardware Reference Guide 20 ...

Страница 21: ...nk Green 10 Gbps link Off No link connection 3 PORT LED Green Link connection is established Blinking Communication is in progress Off No link connection or not ready to communicate 4 ISCSI connectors Connect to Ethernet cables 10 Gbps iSCSI board LEDs and connectors copper Chapter 2 System controller Hitachi Virtual Storage Platform F700 Hardware Reference Guide 21 ...

Страница 22: ...l form factor pluggable can be removed Blue Normal link status at 8 Gbps Green Normal link status at 2 Gbps or 4 Gbps Table 2 32 Gbps 16 Gbps Fibre Channel Number Item Description 1 Fibre Channel connectors Connect to Fibre Channel cables 2 STATUS LED Green Front end module is in power on state Red Front end module can be removed safely 8 Gbps 16 Gbps or 32 Gbps Fibre Channel 4 port board LEDs and...

Страница 23: ... 32 Gbps Fibre Channel ports left to right Port 1 Port 2 Port 3 Port 4 CHB 1A 1A 3A 5A 7A CHB 1B 1B 3B 5B 7B CHB 1C 1C 3C 5C 7C CHB 1D 1D 3D 5D 7D CHB 1E 1E 3E 5E 7E CHB 1F 1F 3F 5F 7F CHB 1G 1G 3G 5G 7G CHB 1H 1H 3H 5H 7H CHB 2A 2A 4A 6A 8A CHB 2B 2B 4B 6B 8B CHB 2C 2C 4C 6C 8C CHB 2D 2D 4D 6D 8D CHB 2E 2E 4E 6E 8E CHB 2F 2F 4F 6F 8F CHB 2G 2G 4G 6G 8G 8 Gbps 16 Gbps or 32 Gbps Fibre Channel 4 po...

Страница 24: ...end module is in the power on state Red Front end module can be removed safely 2 PORT LED Red Small form factor pluggable can be removed Blue Normal link status at 16 Gbps Green Normal link status at 4 Gbps or 8 Gbps 3 Fibre Channel connectors Connect to Fibre Channel cables 16 Gbps Fibre Channel 2 port board LEDs and connectors Chapter 2 System controller Hitachi Virtual Storage Platform F700 Har...

Страница 25: ...CHB 1G 1G 3G CHB 1H 1H 3H CHB 2A 2A 4A CHB 2B 2B 4B CHB 2C 2C 4C CHB 2D 2D 4D CHB 2E 2E 4E CHB 2F 2F 4F CHB 2G 2G 4G CHB 2H 2H 4H Back end module LEDs and connectors The back end module LEDs display the operating status of the module Back end module LEDs and connectors Chapter 2 System controller Hitachi Virtual Storage Platform F700 Hardware Reference Guide 25 ...

Страница 26: ...ack end module can be removed safely 2 PORT LED Blue Link status is normal 3 PATH 0 connector Connect to a drive tray 4 PATH 1 connector Connects to a drive tray Back end module LEDs and connectors Chapter 2 System controller Hitachi Virtual Storage Platform F700 Hardware Reference Guide 26 ...

Страница 27: ...e across all host connection ports conventional hard disk drives HDD are not included or configurable with all flash arrays Small form factor drive tray DBS The following describes the physical specifications of the small form factor drive tray Name Model name Height Number of drive slots Drive type DBS DW F800 DBSC 2U 88 2 mm 24 2 5 inch SFF SFF with front panel bezel Number Item Description 1 PO...

Страница 28: ...ezel Number Item Description 1 POWER READY and LOCATE LEDs Green Drive tray is powered on Green Drive tray is operational Amber Indicates the location of the chassis Can be turned on or turned off by the maintenance utility 2 ALM LED Red Drive stopped due to a failure and can be replaced 3 ACT LED Green Normal operation SFF front panel without bezel Chapter 3 Drive trays Hitachi Virtual Storage Pl...

Страница 29: ... Description 1 ENC N A 2 POWER LED Green ENC is in the power on state 3 Locate LED Amber Indicates the location of the chassis Can be turned on or turned off by the maintenance utility 4 ALARM LED Red ENC can be replaced 5 PATH IN LED Blue IN side port is linked up 6 PATH IN connector Connects to a controller or drive tray SFF rear panel Chapter 3 Drive trays Hitachi Virtual Storage Platform F700 ...

Страница 30: ...it can be replaced 14 RDY LED Green Normal operation AC power supply unit LEDs and connectors Both SFF and LFF drive trays are equipped with AC power supply units The AC power supply units include LEDs to display its operating status Number Item Description 1 RDY LED Green Normal operation 2 ACI IN LED Green AC input is operating normally 3 ALM LED Red Power supply unit can be replaced AC power su...

Страница 31: ...ont panel bezel Number Item Description 1 POWER LED Green Drive tray is powered on 2 READY LED Green Drive tray is operational 3 Locate LED Amber Indicates the location of the chassis Can be turned on or turned off by the maintenance utility 4 Lock Locks and unlocks the front panel bezel by using the supplied key Flash module drive tray DBF Chapter 3 Drive trays Hitachi Virtual Storage Platform F7...

Страница 32: ...ks for about two to five minutes until the startup processing is complete ALM LED Red Drive stopped due to a failure and can be replaced Note ACT indicator is only printed on some types of FMDs 3 POWER READY and LOCATE LEDs Green Drive tray is powered on Green Drive tray is operational FMD front panel without bezel Chapter 3 Drive trays Hitachi Virtual Storage Platform F700 Hardware Reference Guid...

Страница 33: ...Slots are organized the following way 9 10 11 6 7 8 3 4 5 0 1 2 FMD rear panel Number Item Description 1 ENC N A 2 POWER LED Green ENC is in the power on state 3 Locate LED Amber Indicates the location of the chassis Can be turned on or turned off by the maintenance utility FMD rear panel Chapter 3 Drive trays Hitachi Virtual Storage Platform F700 Hardware Reference Guide 33 ...

Страница 34: ...tor Connects to a drive tray 9 Console This port is reserved 10 Receptacle Connects to the power cable provided with the storage system 11 Three LEDS top to bottom RDY LED AC IN LED ALM REPLACE LED Green Power supply unit is operating normally Green Power supply unit is operating normally Red Power supply unit can be replaced FMD rear panel Chapter 3 Drive trays Hitachi Virtual Storage Platform F7...

Страница 35: ... Hypervisor support for Gx00 Fx00 report at https support hitachivantara com en_us interoperability html Service Processor Windows 10 Enterprise hardware specifications The following table lists the hardware specifications for the service processor Windows 10 Enterprise provided by Hitachi Vantara Item Specification Dimensions Height 1 7 inches 43 mm Width 17 2 inches 437 mm Depth 9 8 inches 249 m...

Страница 36: ... the controllers and the IP network are configured as a bridge The SVP can be addressed using the default IP address 192 168 0 15 In the unlikely event you cannot connect to the SVP using the default IP address use the following emergency login http default SVP IP address dev storage model number system serial number emergency do For example Storage system model number Storage system serial number...

Страница 37: ...s equipped with LEDs a reset button and a power button Table 3 SVP Windows 10 Enterprise front panel Item Description 1 LED Left to Right N A LAN card 2 LAN card 1 Hard drive System standby power 2 Reset button 3 Power button SVP rear panel The only ports used at the rear panel of the physical SVP are the power socket and the four LAN ports The following ports connect to your IP network the manage...

Страница 38: ... network has BPDU enabled to prevent loops connect the user LAN port on controllers 1 and 2 to an Ethernet switch that is also connected to the LAN1 port on the SVP Note After the Initial Startup Wizard is complete the SVP can be used in non bridge mode In this mode the cables can be removed from SVP ports LAN3 and LAN4 and attached to switches For more information contact customer support SVP rea...

Страница 39: ...blinking status 2 Release the main switch and the POWER LED returns to solid green after blinking for approximately three seconds The power off process begins The process takes approximately 18 minutes or longer depending on the amount of data that needs to be written The POWER LED is solid green during the powering off process The POWER LED changes from green to amber when the process is complete...

Страница 40: ...ms of the contract Note The battery protects the data in the cache memory in an emergency such as a sudden power failure In these cases follow the normal power down procedure If not the battery might reach its lifespan earlier than expected and become unusable within three years When replacing the battery follow the given procedure for disposing a used battery Replacement period The battery lifeti...

Страница 41: ...VSP F700 parts list The VSP F700 includes the following standard and optional components Table 5 CBL controller components Model number Part description Quantity DW850 CBL 4U chassis 1 Power supply unit 2 LAN board LAN UPS 2 Backup module BKM 8 Front bezel 4U 1 Binder 1 SAS cable label 2 DW F800 RRCB Rail kit 1 DW F800 BAT Battery 6 Appendix A Storage system parts list Hitachi Virtual Storage Plat...

Страница 42: ... F800 4HF32R Front end 32 16 Gbps 4port FC 2 12 DW F800 1HP8 PCIe channel board 2 DW F800 PC1F PCIe cable 1 5m 2 DW F800 BS12G Disk board 0 4 DW F800 BS12GE Encryption disk board 0 4 DW F800 1PS16 SFP for 16 Gbps Shortwave 0 48 DW F800 1PL16 SFP for 16 Gbps Longwave 0 48 DW F800 1PL32 SFP for 32 Gbps Longwave 0 48 DW F800 BAT Battery 0 6 Note 1 A DIMM of a particular capacity cannot be mixed with ...

Страница 43: ...2FN 3 5 TB MLC 12 Gbps flash module drive 0 12 DKC F810I 7R0FP 7 TB MLC TLC 12 Gbps flash module drive 0 12 DKC F810I 14RFP 14 TB MLC TLC 12 Gbps flash module drive 0 12 Table 9 DBS drive tray components Model number Part description Quantity DW F800 DBSC 2U chassis 1 ENC 2 AC Power supply unit 2 Front bezel 2U 1 DW F800 RRDB Rail kit 1 VSP F700 parts list Appendix A Storage system parts list Hita...

Страница 44: ...y HDW2 F850 SVP P Service processor Windows 10 Enterprise 1 Drive tray and drive configuration The following table lists the supported maximum installable drive trays and data drives for the VSP F700 storage system Controller chassis Number of mountable drive trays Maximum number of mountable drives Drive trays Maximum Solid state drive Flash module drive FMD CBL DBS 36 864 N A DBF 36 N A 432 Data...

Страница 45: ...r 15 A A F6516 P620 Power cable for PDU 1 A F6516 P630 Power cable for PDU 1 Table 13 SAS cables Model number Specification DW F800 SCQ1 1 m SAS cable including omega clip 2 DW F800 SCQ1F 1 5 m SAS cable including omega clips 2 DW F800 SCQ3 3 m SAS cable including omega clips 2 DW F800 SCQ5 5 m SAS cable including omega clips 2 DW F800 SCQ10A 10 m SAS optical cable DW F800 SCQ30A 30 m SAS optical ...

Страница 46: ...LC optical cable for optical A 6515 HM10L 10 m LC LC optical cable for optical A 6515 HM20L 20 m LC LC optical cable for optical A 6515 HM30L 30 m LC LC optical cable for optical A 6515 HM50L 50 m LC LC optical cable for optical A 6515 HM100L 100 m LC LC optical cable for optical A 6515 HM200L 200 m LC LC optical cable for optical A 6515 HM300L 300 m LC LC optical cable for optical A 6515 JM5L 5 m...

Страница 47: ...number Specification A 6515 JM300L 300 m LC LC optical cable for optical Data and power cable model list Appendix A Storage system parts list Hitachi Virtual Storage Platform F700 Hardware Reference Guide 47 ...

Страница 48: ...IA unit 2 4U Heat output W 338 W Power consumption VA 363 VA Air flow m3 min 3 6 0 m3 min Notes 1 The start up time might be longer in proportion to the number of drive trays connected With a maximum configuration 1 controller chassis and 19 drive trays start up time is approximately 8 minutes 2 Can be mounted on the RKU rack For the mounting special rails for the rack and decoration panels are re...

Страница 49: ...DBS 2 2 m3 min Notes 1 The start up time might be longer in proportion to the number of drive trays connected With a maximum configuration 1 controller chassis and 19 drive trays start up time is approximately 8 minutes 2 Can be mounted on the RKU rack For the mounting special rails for the rack and decoration panels are required separately depending on the number of the mounted storage systems 3 ...

Страница 50: ... trays the maximum mountable quantity unit may vary 2 Available as spare or data disks Host interface Item Specification Interface type 16 32 Gbps FC Optical 10 Gbps iSCSI Optical 10 Gbps iSCSI Copper Data transfer speed Max speed for transfer to host 400 Mbps FC 800 Mbps FC 1600 Mbps FC 3200 Mbps FC 1000 Mbps iSCSI Optical 1000 Mbps iSCSI Copper Number of ports 16 32 Gbps FC Optical 64 10 Gbps iS...

Страница 51: ...P 14D 2P Maximum number of parity groups 288 Maximum volume size 3 TB when using the LDEVs of other Storage Systems 4TB Maximum volumes host groups and iSCSI targets 2048 Maximum volumes parity groups 2048 Note 1 A storage system configured with RAID6 RAID 5 or RAID 1 provides redundancy and enhances data reliability However there is still a possibility of losing data caused by unforeseeable hardw...

Страница 52: ...nvolatile memory Non volatile data in the cache memory is protected against sudden power failure The backup operation writes data into a cache even if a power interruption occurs and transferred to the cache flash memory Insulation performance Item Specification Insulation withstand voltage AC 1 500 V 100mA 1min Insulation resistance DC 500 V 10 MΩ or more Electrical specifications The electrical ...

Страница 53: ...or the two power units Therefore plan the power supply facility so that the current carrying capacity for one power unit can provide the total capacity for two power units 3 This table shows the power requirement 100 V or 200 V for the maximum configuration The actual required power might exceed the value shown in the table when the tolerance is included Environmental specifications The environmen...

Страница 54: ...erating 8 to 80 Non operating 8 to 90 Transport storage 5 to 95 Maximum wet bulb temperature C 29 C non condensing Vibration State FMD tray Operating m s2 2 5 or less 5 to 300Hz Within 5 seconds resonance point 10 Hz or less Non operating m s2 5 0 or less at 5 Hz to 300 Hz no damage to product 9 8 1 0 G Ensure own safety with fall prevention Within 5 seconds resonance point 10 Hz or less Transport...

Страница 55: ...10 C to 40 C Non operating m 60 to 12 000 Note 1 Meets the highest allowable temperature conditions and complies with ASHRAE American Society of Heating Refrigerating and Air Conditioning Engineers 2011 Thermal Guidelines Class A3 The maximum value of the ambient temperature and the altitude is from 40ºC at an altitude of 950m 3000 feet to 28ºC at an altitude of 3050m 1000 feet The allowable ambie...

Страница 56: ...is 23ºC 2ºC Device installation position The Controller Chassis is at the bottom of the rack and the Drive Box is at a height of 1 5m in the rack Measurement position 1m away from the front rear left or right side of the storage system and 1 5m high at four points Measurement value Energy average value of the four points front rear left and right The recommendation is to install the storage system...

Страница 57: ... operating status State Controller FMD tray Opera ting 60 dB Environmental temperature 32 C or less 1 60 dB Environmental temperature 32 C or less 1 2 3 Non opera ting 55 dB Environmental temperature 32 C or less 1 2 3 55 dB Notes 1 The internal temperature of the system controls the rotating speed of the fan module Therefore this standard value might be exceeded if the maximum load continues unde...

Страница 58: ...tachi does not test storage systems and data drives includes HDDs SSDs and FMDs for compatibility with fire suppression systems and pneumatic sirens Hitachi also does not provide recommendations or claim compatibility with any fire suppression systems and pneumatic sirens The customer is responsible to follow their local or national regulations To prevent unnecessary I O error or damages to the ha...

Страница 59: ... IEC International Electrotechnical Commission standards IEC 61584 5 Ed1 and IEC60297 Part5 scenic test at the maximum acceleration rate of 9 8m s2 1 0G equivalent to NEBS Network Equipment Building System Level3 Shared memory Using Hitachi software products the number of pairs migration plans and pool capacities and virtual volumes depend on the amount of capacity of shared memory installed on th...

Страница 60: ... and virtual volumes Table 15 Usable capacity of pools virtual volumes Shared memory function VSP F700 Base 1 6 PiB Extension1 4 4 PiB Extension2 8 05 PiB Extension3 12 5 PiB Note When decreasing shared memory function delete all DP DT active flash TI and dedupe and compression pools The following table lists the corresponding amount of shared memory function to shared memory capacity Table 16 Sha...

Страница 61: ...red for shared memory function Shared Memory Function VSP F700 Base 128 GiB Extension1 128 GiB Extension2 256 GiB Extension3 256 GiB Shared memory Appendix B System specifications Hitachi Virtual Storage Platform F700 Hardware Reference Guide 61 ...

Страница 62: ...i Command Suite or Hitachi Storage Advisor Allow communication to the storage system from the SVP TCP IP port assignments When you install your storage system default ports must be opened to allow for incoming and outgoing requests Review the following ports before you install the storage system to avoid conflicts between the TCP IP port assignments used by the storage system and those used by oth...

Страница 63: ...rt that Device Manager Storage Navigator uses refer to the Device Manager Storage Navigator online help 5989 Used by SMI S 10995 TCP Device Manager Storage Navigator and Hitachi suite components 23015 Used for Web browser communications 23016 Used for Web browser communications via SSL 28355 TCP Device Manager Storage Navigator Secure 31001 Used for communication by Hitachi Command Control Interfa...

Страница 64: ...ssLoade r RMI 51099 No RMIClassLoade rHttps RMI SSL 5443 No RMIIFRegist RMI 1099 No PreRMIServer RMI 51100 513551 No Automatic allocation 88 02 0x xx 00 or later DKCManPrivate RMI 11099 N A 88 02 0x xx 00 or later SMI S SLP SLP 427 Yes only if SMI S is not used SMIS_CIMOM SMI S 5989 62441 Yes only if SMI S is not used 88 02 0x xx 00 or later Automatic allocation 88 02 0x xx 00 or later CommonJetty...

Страница 65: ...ts available for host connections vary based on the controller model Fibre Channel SFP adapters are used to connect to your Fibre Channel switch and hosts iSCSI ports come in optical and copper RJ 45 interfaces and are used to connect to your Ethernet switch and hosts Each controller also has A SAS port for connection to an external drive tray An RJ 45 10 100 1000 bps user LAN port for performing ...

Страница 66: ...on the same network segment as the SVP and storage system Note The SVP running Windows 10 operating system does not provide a way to disable Spanning Tree Protocol STP If your network has BPDU enabled to prevent loops connect the user LAN port on controllers 1 and 2 to an Ethernet switch instead of connecting them to SVP LAN 3 and LAN 4 ports Virtual SVP connectivity requires all of the following ...

Страница 67: ...red for storage system installation vary according to the specific storage system and network configuration Fibre Channel and iSCSI cables are used to connect the controllers to a switch or host Serial attached SCSI SAS cables are used to connect drive trays to controllers and other drive trays Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 67 ...

Страница 68: ...ect the iSCSI 10 Gb RJ 45 ports on each controller to a host computer direct connection or to several host computers via an Ethernet switch SAS SAS optical Connects the controller to a drive tray or a drive tray to another drive tray Two SAS cables are provided with each drive tray Ethernet RJ 45 Four shielded Category 5e or 6a Ethernet cables are required for connecting the SVP to the controllers...

Страница 69: ...orts Fiber Channel connections to hosts For details about configuring FC host connections see the Provisioning Guide Note Due to high speed serial data transfer via Fibre Channel use high quality FC cables that comply with the Fibre Channel PH standard The following figure shows FC direct connection and FC connection through a switch Fibre Channel cables Appendix D Data and power cables Hitachi Vi...

Страница 70: ...Gbps 984 25 ft 300 m 1640 4 ft 500 m 3280 8 ft 10 km 4 Gbps 493 ft 150 m 1246 72 ft 380 m 1312 3 ft 400 m 8 Gbps 164 04 ft 50 m 493 ft 150 m 623 36 ft 190 m 16 Gbps 114 8 ft 35 m 328 08 ft 100 m 410 1 ft 125 m 32 Gbps 65 62 ft 20 m 229 7 ft 70 m 328 08 ft 100 m Fibre Channel cables Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 70 ...

Страница 71: ...lent to DXLC 2P PC xxM GC50 125 2SR OMx 50 125 μm 62 5 125 μm Multimode Wavelength 850 nm LC connector LC connector LC LC cable longwave DXLC 2PS SPC xxM SMC 10 125 2SR 9 125 μm Singlemode Wavelength 1300 nm The following figure shows the connector used for optical interfaces Fibre Channel cables Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 71 ...

Страница 72: ...ions to hosts For details about configuring iSCSI host connections see the Provisioning Guide Cable specifications for iSCSI optical interface Cable type Interface Cable mode name Nominal Cable Connector One side Other side LC LC cable Optical Equivalent to DXLC 2P PC xxM GC50 125 2SR OMx 50 125 mm Multimode Wavelength 850 nm LC connector LC connector iSCSI cables Appendix D Data and power cables ...

Страница 73: ...tor that connects the storage system optical iSCSI ports LC connector type Connector type LC duplex receptacle connector Interval 6 25 mm flat type two rows Cable specifications for 10 Gbps iSCSI copper interface iSCSI cables Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 73 ...

Страница 74: ...bps 1000BASE T STP use an STP cable that suppresses radio noise RJ 45 Category 6a LAN cable 50 m 10 Gbps 10GBASE T STP use an STP cable that suppresses radio noise RJ 45 The following figure shows a 10 Gbps iSCSI cable iSCSI cables Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 74 ...

Страница 75: ... RFC 1231 MIB II RFC 1757 RMON RFC 1901 SNMPv2 iSCSI specifications Item Specification Comments iSCSI target function Supported N A iSCSI target function Supported TrueCopy only iSCSI ports 2 per interface board VSP Fx00 models Maximum 24 per iSCSI system Connection methods Direct and switch connections Host connections 255 maximum per iSCSI port With Linux software initiator the maximum number de...

Страница 76: ...k aggregation Not supported N A Tagged VLAN Supported N A IPv4 Supported N A IPv6 Supported Note the following precautions When iSCSI Port IPv6 is set to Enabled if the IPv6 global address is set to automatic the address is determined by acquiring a prefix from an IPv6 router If the IPv6 router does not exist in the network the address cannot be determined As a result an iSCSI connection might be ...

Страница 77: ...e network equipment preventing the storage system from communicating through the new port number iSCSI name Both iqn3 and eui4 types are supported The unique iqn value is automatically set when a target is made iSCSI name is configurable Error recovery level 0 zero Error recovery by retrying from host Does not support Level 1 and Level 2 Header digest Supported Detects header error or data error w...

Страница 78: ...1 HiCommand Dynamic Link Manager Pass switching is achieved Not supported on Windows Vista and Windows 7 operating systems 2 IP Security Authentication and encryption of IP packets The storage system does not support IPsec 3 iqn iSCSI Qualified Name The iqn consists of a type identifier iqn a date of domain acquisition a domain name and a character string given by the individual who acquired the d...

Страница 79: ...ended bend radius The following table provides general guidelines for minimum bend radius values but you should consult the recommendation of your cable manufacturer Cable type Minimum bend radius values Fibre Channel 40 mm 1 73 inch iSCSI optical 40 mm 1 73 inch Category 5 Ethernet Four times the outside diameter of the cable SAS 40 mm 1 73 inch Managing cables Appendix D Data and power cables Hi...

Страница 80: ...e cables over time Therefore do not allow cables to sag through gaps in your supports Place drop points in your supports that permit cables to reach racks without bending or pulling Unintentional unplugging or unseating of a power cable can have a serious impact on the operation of an enterprise storage system Unlike data cables power connectors do not have built in retention mechanisms to prevent...

Страница 81: ...vides a variety of power cables that facilitate using storage systems around the world Hitachi power cables meet the safety standards for the country for which they are intended Power cable assemblies For information about racks and power distribution units PDUs refer to the Hitachi Universal V2 Rack Reference Guide Hitachi power cables consist of three parts Plug Male connector for insertion into...

Страница 82: ...00 240 10 16 CEI 23 50 Italy 200 240 10 16 CEI 23 50 7 Argentina 200 240 10 15 IRAM 2073 Australia 200 240 10 15 AS 3112 China 200 240 10 16 GB 1002 New Zealand 200 240 10 15 AS 3112 8 Denmark 200 240 10 DK 2 5 Israel 200 240 10 16 SI 32 94 Europe 200 240 CEE 7 7 105 India 200 240 6 16 IS 1293 South Africa 200 240 10 16 SABS 164 11 Switzerland 200 240 10 SEV 1011 126 International 200 240 20 IEC 3...

Страница 83: ...erland for a true 16 A application 7 4 wire three phase and earth Physical variations connector size and color indicate amperage rating 8 5 wire three phase earth and neutral Physical variations connector size and color indicate amperage rating AC connections The following table shows and describes the types of AC connections on your storage system Description Receptacle Input rating Reference sta...

Страница 84: ...ut rating Reference standards BS 1363 200V 240V 5 BS 1365 3 IEC 83 AS 3112 200V 240V 6 AS C112 Cable and connector AC connections Appendix D Data and power cables Hitachi Virtual Storage Platform F700 Hardware Reference Guide 84 ...

Страница 85: ...t any given time the voltage across the hot and neutral conductors can be anywhere between its peak maximum and zero Electrical conductors must be large to meet high amperage requirements Three phase power uses three cycles that are 120 degrees out of phase which never allows the voltage to drop to zero The more consistent voltage derived from the three hot conductors results in smoother current f...

Страница 86: ...wable current load on each PDU before plugging the device into the PDU Balance the electrical current load between available PDUs Americas single phase PDU 1P30A 8C13 3C19UL P The following figure and table describes the specifications of the PDU Figure 1 Americas PDU for the Hitachi Universal V2 Rack Single phase PDU 1P30A 8C13 3C19UL P Part Number Region Phase Description 1P30A 8C13 3C19U L P Am...

Страница 87: ...iption 1P30A 15C13 3C19 UL P Americas Single 208V 30A 24A rated 60Hz 15 IEC C13 3 IEC C19 sockets NEMA L6 30P input power plug 4 5 m 14 76 feet cable Americas three phase PDU 3P30A 8C13 3C19UL P The following figure and table describes the specifications of the PDU Americas single phase PDU 1P30A 15C13 3C19UL P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Stora...

Страница 88: ...ted 60Hz 8 IEC C13 3 IEC C19 sockets NEMA L15 30P input power plug 4 5 m 14 76 feet cable Americas three phase PDU 3P30A 15C13 3C19UL P The following figure and table describes the specifications of the PDU Americas three phase PDU 3P30A 15C13 3C19UL P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 88 ...

Страница 89: ...ated 60Hz 15 IEC C13 3 IEC C19 sockets NEMA L15 30P input power plug 4 5 m 14 76 feet cable Americas three phase PDU 3P30A 24C13 6C19UL P The following figure and table describes the specifications of the PDU Americas three phase PDU 3P30A 24C13 6C19UL P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 89 ...

Страница 90: ...60Hz 24 IEC C13 6 IEC C19 sockets NEMA L15 30P input power plug 4 5 m 14 76 feet cable APAC and EMEA single phase PDU 1P32A 9C13 3C19CE P The following figure and table describes the specifications of the PDU APAC and EMEA single phase PDU 1P32A 9C13 3C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 90 ...

Страница 91: ...Hz 9 IEC C13 3 IEC C19 sockets IEC309 Blue 2P E input power plug 4 5 m 14 76 feet cable APAC and EMEA single phase PDU 1P32A 18C13 3C19CE P The following figure and table describes the specifications of the PDU APAC and EMEA single phase PDU 1P32A 18C13 3C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 91 ...

Страница 92: ... 60Hz 18 IEC C13 3 IEC C19 sockets IEC309 Blue 2P E input power plug 4 5 m 14 76 feet cable APAC and EMEA three phase PDU 3P16A 9C13 3C19CE P The following figure and table describes the specifications of the PDU APAC and EMEA three phase PDU 3P16A 9C13 3C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 92 ...

Страница 93: ...0Hz 9 IEC C13 3 IEC C19 sockets IEC309 Red 3P N E input power plug 4 5 m 14 76 feet cable APAC and EMEA three phase PDU 3P16A 15C13 3C19CE P The following figure and table describes the specifications of the PDU APAC and EMEA three phase PDU 3P16A 15C13 3C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 93 ...

Страница 94: ...60Hz 15 IEC C13 3 IEC C19 sockets IEC309 Red 3P N E input power plug 4 5 m 14 76 feet cable APAC and EMEA three phase PDU 3P32A 24C13 6C19CE P The following figure and table describes the specifications of the PDU APAC and EMEA three phase PDU 3P32A 24C13 6C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 94 ...

Страница 95: ...32A 24C13 6C19 CE P APAC and EMEA Three 400V max 3x 32A 50Hz 60Hz 24 IEC C13 6 IEC C19 sockets IEC309 Red 3P N E input power plug 4 5 m 14 76 feet cable APAC and EMEA three phase PDU 3P32A 24C13 6C19CE P Appendix E Power distribution units for Hitachi Universal V2 Rack Hitachi Virtual Storage Platform F700 Hardware Reference Guide 95 ...

Страница 96: ...acles must face toward the back not toward each other The area behind the storage system and between the vertical 19 inch mounting posts must be free of PDUs and cable loops Hitachi Universal V2 Rack rail kits Use rail kits to mount the Hitachi Virtual Storage Platform family storage system in a Hitachi Universal V2 Rack The following tables list the rail kit information for the specified storage ...

Страница 97: ...V2 Rack Storage system Front door Rear door Side panels VSP Fx00 models Optional must be ordered separately A3BF DR Included with rack Not included with rack must be ordered separately A quantity of two must be ordered per rack A3BF Z PAN 1200 Hitachi Universal V2 Rack accessories Appendix F Non Hitachi racks Hitachi Virtual Storage Platform F700 Hardware Reference Guide 97 ...

Страница 98: ... mark Explanation Do not disassemble the equipment Be careful when handling heavy equipment Use caution when handling electrostatic sensitive equipment and microcircuitry Avoid placing any non essential objects or equipment onto the storage system Use caution when handling the equipment Use caution when handling equipment with movable parts Use caution when handling equipment with hot surfaces Use...

Страница 99: ...Small form factor drive tray Small form factor drive tray Appendix G Warning labels on the storage system Hitachi Virtual Storage Platform F700 Hardware Reference Guide 99 ...

Страница 100: ...Flash module drive tray Flash module drive tray Appendix G Warning labels on the storage system Hitachi Virtual Storage Platform F700 Hardware Reference Guide 100 ...

Страница 101: ...CBL controller Battery CBL controller Appendix G Warning labels on the storage system Hitachi Virtual Storage Platform F700 Hardware Reference Guide 101 ...

Страница 102: ...product Recycling A nickel metal hydride battery is used in the Cache Backup Battery A nickel metal hydride battery is a resource that can be recycled When you want to replace the Cache Backup Battery call the service personnel They will dispose of it for you This nickel metal hydride battery which is designated as recycling product by a recycling promotion low must be recycled The mark posted on ...

Страница 103: ... Regulatory compliance This equipment has been tested and certified for compliance with the following standards Appendix I Regulatory compliance Hitachi Virtual Storage Platform F700 Hardware Reference Guide 103 ...

Страница 104: ...ic emission certifications EN55022 2010 CE marking EU EN55024 2010 EN61000 3 2 2006 A1 A2 EN61000 3 3 2013 Safety certifications UL and CSA 60950 1 2007 cTuVus United States of America and Canada EN60950 1 2006 A1 1 A1 A12 A2 TUV Germany IEC60950 1 2005 A 1 A2 N A All CB countries IEC60950 1 2005 A 1 A2 S_Mark Argentina TP TC 004 2011 EAC Russia CNS 14336 1 BSMI Taiwan EN60950 1 2006 A1 1 A1 A12 A...

Страница 105: ...y cause harmful interference in which case the user will be required to correct the interference at his own expense Testing was done with shielded cables Therefore in order to comply with the FCC regulations you must use shielded cables with your installation If trouble occurs in another configuration a user might be requested to take appropriate preventative measures RKU CBL flash module drive tr...

Страница 106: ...ara Corporate Headquarters 2845 Lafayette Street Santa Clara CA 95050 2639 USA HitachiVantara com community HitachiVantara com Contact Information USA 1 800 446 0744 Global 1 858 5474526 HitachiVantara com contact ...