CHAPTER 6: ACTUAL VALUES
STATUS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
6-9
6
PORT 1…3 PTP STATE
is the present state of the port’s PTP clock. The PTP clock state is:
•
Disabled
is the port’s function setting is Disabled
•
No Signal
if enabled but no signal from an active master has been found and selected
•
Calibrating
if an active master has been selected but lock is not at present established
•
Synch’d (No Pdelay)
if the port is synchronized, but the peer delay mechanism is non-operational
•
Synchronized
if synchronized
PTP - IRIG-B DELTA
is the time difference, measured in nanoseconds, between the fractional seconds portion of the time
being received via PTP and that being received via IRIG-B. A positive value indicates that PTP time is fast compared to IRIG-
B time.
6.3.16 Direct inputs
ACTUAL VALUES
STATUS
DIRECT INPUTS
The
AVERAGE MSG RETURN TIME
is the time taken for direct output messages to return to the sender in a direct input/output
ring configuration (this value is not applicable for non-ring configurations). This is a rolling average calculated for the last
ten messages. There are two return times for dual-channel communications modules.
The
UNRETURNED MSG COUNT
values (one per communications channel) count the direct output messages that do not
make the trip around the communications ring. The
CRC FAIL COUNT
values (one per communications channel) count the
direct output messages that have been received but fail the CRC check. High values for either of these counts can indicate
on a problem with wiring, the communication channel, or one or more relays. The
UNRETURNED MSG COUNT
and
CRC FAIL
COUNT
values can be cleared using the
CLEAR DIRECT I/O COUNTERS
command.
The
DIRECT INPUT 1
to
DIRECT INPUT (32)
values represent the state of each direct input.
6.3.17 Direct devices status
ACTUAL VALUES
STATUS
DIRECT DEVICES STATUS
DIRECT INPUTS
AVERATE MSG RETURN
TIME CH1: 0 ms
UNRETURNED MSG
COUNT CH1: 0
CRC FAIL COUNT
CH1: 0
AVERAGE MSG RETURN
TIME CH2: 0 ms
UNRETURNED MSG
COUNT CH2: 0
CRC FAIL COUNT
CH2: 0
DIRECT INPUT 1:
On
DIRECT INPUT 32:
On
DIRECT DEVICES
STATUS
DIRECT DEVICE 1
STATUS: Offline
Range: Offline, Online
DIRECT DEVICE 16
STATUS: Offline
Range: Offline, Online
Содержание F35
Страница 12: ...1 4 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FOR FURTHER ASSISTANCE CHAPTER 1 INTRODUCTION 1 ...
Страница 202: ...4 88 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXLOGIC DESIGN USING ENGINEER CHAPTER 4 INTERFACES 4 ...
Страница 562: ...6 30 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL PRODUCT INFORMATION CHAPTER 6 ACTUAL VALUES 6 ...
Страница 576: ...7 14 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL TARGETS CHAPTER 7 COMMANDS AND TARGETS 7 ...
Страница 650: ...A 38 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL FLEXANALOG ITEMS APPENDIX A FLEXANALOG OPERANDS A ...
Страница 658: ...C 6 F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL COMMAND LINE INTERFACE APPENDIX C COMMAND LINE INTERFACE C ...
Страница 666: ...iv F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL ABBREVIATIONS ...
Страница 682: ...xvi F35 MULTIPLE FEEDER PROTECTION SYSTEM INSTRUCTION MANUAL INDEX ...