10-12
F650 DIGITAL BAY CONTROLLER
GEK-106310-AF
10.11 INSTANTANEOUS OVERCURRENT (50PH, 50PL, 50N, 50G, 50SG)
CHAPTER 10: COMMISSIONING
10.11 Instantaneous overcurrent (50PH, 50PL, 50N, 50G, 50SG)
Set the relay to trip for the protection element being tested. Configure any of the outputs to be enabled only by the
protection element being tested.
Apply 0.9 times the Pickup current and check that the relay does not trip.
Gradually increase the current value and verify that the relay operates between 1 and 1.1 times the set pickup current.
The relay must trip by instantaneous in a time frame of 10 to 55 ms. All the relay trip contacts must operate, as well as the
contact set as 50.
Remove current and apply it again suddenly to a value of 4 times the pickup current. The relay should trip instantaneously
in a time frame of 10 to 45 ms.
Test one point for each phase and group of the protection element.
Note (*): Only available for Enhanced models
50 ELEMENTS TEST PARAMETERS
Element Settings (50PH, 50PL, 50G and 50SG)
Setting
Value
Units
Function
Enabled
Input
RMS
NA
Pickup Level
3
A
Delay time
0
Seconds
Test Execution
Configure one output for 50 Trip
Apply times I pickup
Element Trip
Tripping times (ms)
0.9 x Pickup
NO
NA
1.1 x Pickup
YES
10-55
4 x Pickup
YES
10-45
Elements
Phase
Group
50PH and 50PL
IA
0
IB
0
IC
0
50G
IG
0
50SG
(*)
ISG
0
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...