CHAPTER 5: SETPOINTS
5.9 RELAY CONFIGURATION
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-167
5.9.8 Switchgear
This menu is used for defining the SWITCHGEAR elements to be controlled by the relay. A switchgear element can be a
breaker, a line selector switch, a grounding selector switch, a busbar selector switch, etc. It is possible to define up to 16
switchgear elements. The settings are as follows:
•
Select
checkbox: enables or disables the control of a new switchgear element
•
Contacts
setting: allows selecting which type of contact is used for monitoring the status (open/closed) of the
element. The selection can be:
52a
(contact type A, showing the same status as the represented element),
52b
(opposite status to the represented element),
52a+52b
(both types of contacts are used),
NONE
(no status monitoring).
•
Opening Time
setting: defines the maximum opening time of an element. It is used for issuing an opening time failure
signal if the element opening is not produced within this time.
•
Closing Time
setting: defines the maximum closing time of an element. It is used for issuing a closing time failure
signal if the element closing is not produced within this time.
•
Contact A
checkbox: allows selecting which operand or combination of operands activate the type A contact status.
Usually it is an input contact wired to type A contact of the element (Breaker/selector switch). This column and the
next two columns are only active if the selected contact type in the Contacts column is
52a
or
52a+52b
.
•
OR
checkbox: selects a group of operands instead of a single one. The relay performs and OR of the signals, and its
output produces operation.
•
NOT
checkbox inverts the status of the signal selected in column
Contact A
.
•
Contact B
checkbox: allows selecting which operand or combination of operands activates the type B contact status.
Usually it is an input contact wired to type B contact of the element (Breaker/selector switch). This column and the
next two columns are only active if the selected contact type in the Contacts column is
52b
or
52a+52b
.
•
OR
checkbox selects a group of operands instead of a single one. The relay performs OR of the signals, and its output
produces operation.
•
NOT
checkbox inverts the status of the signal selected in column
Contact B
.
•
Open text
setting: allows associating a text to the control event associated with the element opening.
•
Close text
setting: allows associating a text to the control event associated with the element closing.
•
Error 00 text
setting: in case of using double contact for the switchgear element status (
52a+52b
), this setting allows
to associate a text to the Error00 internal status, this means, when both contacts are inactive during a period longer
than the associated with the opening or closing Operation, depending on which Operation is being performed.
•
Error 11 text
setting: in case of using double contact for the switchgear element status (
52a+52b
), this setting allows to
associate a text to the Error11 internal status, this means, when both contacts are active during a period longer than
the associated with the opening or closing Operation, depending on which Operation is being performed.
•
ALARM
setting: enables the issue of an alarm in the event of a close, open, 00-type, 11-type error. If it is configured as
an alarm.
•
Opening init
setting: this setting selects which operand or combination of operands indicate the initiation of an
opening operation, in order to allow the follow up of the operation and generate the corresponding alarms if the
operation is not successful. The operation bit signal used to launch the opening init must be configured in the
operations tab inside relay configuration.
•
Closing init
setting: this setting selects which operand or combination of operands indicate the initiation of a closing
operation, in order to allow the follow up of the operation and generate the corresponding alarms if the operation is
not successful. The operation bit signal used to launch the closing init must be configured in the operations tab inside
relay configuration.
•
Block Open
: allow selecting which operand or combination of operands activates the opening blocks for the
switchgears (XSWI$ST$BlkOpn and XSWI$ST$BlkCls) for operating in 61850.
•
Block Close settings
: allow selecting which operand or combination of operands activates the closing blocks for the
switchgears (XSWI$ST$BlkOpn and XSWI$ST$BlkCls) for operating in 61850.
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...