CHAPTER 5: SETPOINTS
5.2 PRODUCT SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-27
5.2.6.3 Demand function measurements and states
Demand values are available at
Actual > Metering > Primary Values > Demand
.
Table 5-11: Demand measurements
*Note: The step depends on the selected “Primary Meter Units” in System Setup > General Settings (A_V; KA_KV)
Demand measurements for
current values
are as follows:
DEMAND I
X
This is the demanded value every minute or every integration period, depending on the
selected settings.
DEMAND I
X
MAX
Demanded maximeter; it stores the Maximum demand value until a demand reset is
issued.
DEMAND I
X
DATE
Date of the Maximum demand value
Being
X
the phase considered in each case.
Demand measurements for
power values
are as follows:
DEMAND
Y
This is the demanded value every minute or every integration period, depending on the
selected settings
DEMAND
Y
MAX
Demanded maximeter; it stores the Maximum demand value until a demand reset is
issued.
DEMAND
Y
DATE
Date of the Maximum demand value.
Name
Default Value
Step
DEMAND IA
0.000
KA
DEMAND IA MAX
0.000
KA
DEMAND IA DATE
01-Jan-2000 00:00:00.000
DEMAND IB
0.000
KA
DEMAND IB MAX
0.000
KA
DEMAND IB DATE
01-Jan-2000 00:00:00.000
DEMAND IC
0.000
KA
DEMAND IC MAX
0.000
KA
DEMAND IC DATE
01-Jan-2000 00:00:00.000
DEMAND IG
0.000
KA
DEMAND IG MAX
0.000
KA
DEMAND IG DATE
01-Jan-2000 00:00:00.000
DEMAND ISG
0.000
KA
DEMAND ISG MAX
0.000
KA
DEMAND ISG DATE
01-Jan-2000 00:00:00.000
DEMAND I2
0.000
KA
DEMAND I2 MAX
0.000
KA
DEMAND I2 DATE
01-Jan-2000 00:00:00.000
DEMAND W
0.000
MW
DEMAND W MAX
0.000
MW
DEMAND W DATE
01-Jan-2000 00:00:00.000
DEMAND VAR PWR
0.000
MVAr
DEMAND VAR MAX
0.000
MVAr
DEMAND VAR DATE
01-Jan-2000 00:00:00.000
DEMAND VA PWR
0.000
MVA
DEMAND VA MAX
0.000
MVA
DEMAND VA DATE
01-Jan-2000 00:00:00.000
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...