CHAPTER 5: SETPOINTS
5.2 PRODUCT SETUP
GEK-106310-AF
F650 DIGITAL BAY CONTROLLER
5-19
5.2.4 Oscillography settings
Oscillography records contain waveforms captured at the sampling rate as well as other relay data at the point of trigger.
This trigger can be configured with a programmable logic operand.
Oscillography records are stored in COMTRADE ASCII - IEEE C37.111-1999 standard format.
The oscillography module is in charge of storing the instantaneous values of the 9 analog signals and the 16
programmable digital signals at
Setpoint > Relay Configuration > Oscillography
in fault conditions (OSCILLO TRIGGER
signal activation).
All oscillography records store all analog signals (fixed) plus 16 digital signals (programmable). The order of storage in the
case of analog signals is as follows:
Analog 1
IA channel.
Analog 2
IB channel.
Analog 3
IC channel.
Analog 4
IG channel.
Analog 5
ISG channel.
Analog 6
VA or VAB channel, depending on the selected configuration (Wye or Delta, at “
Setpoint>System Setup >
General Settings > Serial VT Connection
”).
Analog 7
VB or VBC channel, depending on the selected configuration (Wye or Delta, at “
Setpoint>System Setup >
General settings > Phase VT Connection
”).
Analog 8
VC or VCA channel, depending on the selected configuration (Wye or Delta, at “
Setpoint>System Setup >
General settings>Phase VT Connection
”).
Analog 9
VN or VX channel, depending on the selected configuration (zero sequence measured, or busbar voltage, at
“
Setpoint>System Setup>General settings>Auxiliary Voltage
”).
The 16 digital channels and the oscillography trigger signal are programmable using the EnerVista 650 Setup software at
Setpoint > Relay configuration > Oscillography
. Each digital channel can be associated with a single status or to a logic
status. In this last case, the logic must be configured using the PLC Editor tool, at
Setpoint > Logic Configuration
inside
EnerVista 650 Setup. The oscillography trigger signal can be a single status or a configured logic. The relay’s default
configuration associates the oscillography trigger to Virtual Output 83, which corresponds to the logic associated with the
general trip of protection elements.
5.2.4.1 Oscillography settings
Function Permission (Function):
Enabling this setting allows to create an oscillography record when the “
TRIGGER
OSCILLO
” signal is activated.
Trigger Position:
This setting defines the prefault data (in percentage) stored every time a new oscillo is
produced.
Samples/Cycle:
This setting defines the number of samples per cycle stored in each oscillography
record.
Setpoint > Product Setup > Oscillography
Setting Description
Name
Default Value
Step
Range
Function Permission
Function
ENABLED
N/A
[DISABLED – ENABLED]
Prefault
Trigger Position
30
1%
[5 : 95]
Samples per cycle
Samples/Cycle
64
N/A
[4 – 8 – 16 –32 – 64]
Maximum number of oscillos
Max. Number Osc.
4
1 oscillo
[1 : 20]
Automatic oscillography overwrite
Automatic Overwrite
DISABLED
N/A
[DISABLED – ENABLED]
Snapshot Event generation
Snapshot Events
ENABLED
N/A
[DISABLED – ENABLED]
Содержание F650
Страница 68: ...2 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 2 6 EXTERNAL CONNECTIONS CHAPTER 2 PRODUCT DESCRIPTION ...
Страница 406: ...6 58 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 6 5 RECORDS CHAPTER 6 ACTUAL VALUES ...
Страница 660: ...7 254 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 7 3 IEC 61850 CONFIGURATOR CHAPTER 7 IEC 61850 PROTOCOL ...
Страница 734: ...12 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF 12 4 RELAY CONFIGURATION CHAPTER 12 FREQUENTLY ASKED QUESTIONS ...
Страница 772: ...A 32 F650 DIGITAL BAY CONTROLLER GEK 106310 AF A 1 OPERANDS F650 MODEL FX GX APPENDIX A LOGIC OPERANDS ...
Страница 950: ...c 24 F650 DIGITAL BAY CONTROLLER GEK 106310 AF C 8 ANALOG INPUTS APPENDIX C DNP 3 0 PROTOCOL FOR F650 ...
Страница 994: ...H 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 995: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 3 ...
Страница 996: ...H 4 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 998: ...H 6 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 999: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 7 ...
Страница 1002: ...H 10 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1003: ...APPENDIX H FACTORY DEFAULT LOGIC GEK 106310 AF F650 DIGITAL BAY CONTROLLER h 11 ...
Страница 1004: ...H 12 F650 DIGITAL BAY CONTROLLER GEK 106310 AF APPENDIX H FACTORY DEFAULT LOGIC ...
Страница 1044: ...I 40 F650 DIGITAL BAY CONTROLLER GEK 106310 AF I 2 FACTORY DEFAULT CONFIGURATION APPENDIX I FACTORY DEFAULT CONFIGURATION ...
Страница 1046: ...J 2 F650 DIGITAL BAY CONTROLLER GEK 106310 AF J 1 GE MULTILIN WARRANTY APPENDIX J MISCELLANEOUS ...